Thanks for the thoughts.  The suspended obstruction table is met quite easily 
(though this is not Light hazard), meaning that water can get over the top of 
the obstruction, but it will just hit the next panel.

The rules for obstructions greater than 18 in. speak to significant horizontal 
obstructions, which is not the case here. The horizontal element is only 2 ins. 
Max.

I suppose this is no different than deep exposed beams where a head is placed 
in each beam pocket, none of which meet the beam rule.  There does not seem to 
be a basis to deny the proposal.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, October 29, 2009 13:26
To: [email protected]; Richardson, R
Subject: RE: Sound Baffles

Unfortunately that section deals with grid or egg-crate type ceilings where the 
ceiling panel is much thinner than the 24 inches of depth of the sound baffles. 
 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Thursday, October 29, 2009 4:03 PM
To: [email protected]
Subject: RE: Sound Baffles

I would refer to NFPA 13 (2007) section 8.15.13.  This refers to the 
obstruction of the vertical member to the developing spray pattern.  I would 
reduce the square footage per head to protect this area.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Thursday, October 29, 2009 2:55 PM
To: [email protected]
Subject: Sound Baffles

We are reviewing a proposal to install sound baffles suspended from the
roof, and evaluating obstructions to sprinkler discharge.   The baffles
are 2 ft. deep panels hung vertically every ft.  The top of the baffle is just 
over 18 ins. From the sprinkler heads so NFPA 13 would indicate that there is 
no obstruction problem because they do not exceed the 4 ft. obstruction trigger 
for obstruction more than 18 in. below the heads. 

However, the panels are every foot and it sure seems like a significant 
obstruction, but the installation does not violate NFPA 13 for obstructions.

Has anyone ever dealt with this issue and offer any insight.

Thanks,

Rich Richardson
Seattle Fire Department



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

X-BeenThere: [email protected]
X-Mailman-Version: 2.1.9
Precedence: list
Reply-To: s
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to