You need to look at 8.6.5.2.2 for suspended or floor mounted obstructions.  
This is assuming you're in an LH space.  

Also look at 8.6.5.3. 

8.6.5.3.1 Continuous or noncontinuous obstructions that interrupt the water 
discharge in a
horizontal plane more than 18 in. (457 mm) below the sprinkler deflector in a 
manner to
limit the distribution from reaching the protected hazard shall comply with 
8.6.5.3.

Handbook Commentary:
Once the sprinkler spray pattern has developed, small obstructions have a 
limited impact on
sprinkler performance. However, larger obstructions located 18 in. (457 mm) or 
more below
the sprinkler deflector, which are addressed in 8.6.5.3.1, prevent the 
sprinkler discharge
from reaching combustibles located below them. This information identifies when 
additional
upright or pendent sprinklers are required to compensate for these types of 
obstructions.


But all in all, they will disrupt the discharge pattern of the sprinkler and 
instead of a conical spray pattern, you will just have water running down the 
panels.  

If they could space them out to 6-8 ft then possibly you could arrange the 
sprinkler layout to accommodate the baffles.  As they are proposing now, there 
will be an issue.





Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Thursday, October 29, 2009 3:55 PM
To: [email protected]
Subject: Sound Baffles

We are reviewing a proposal to install sound baffles suspended from the roof, 
and evaluating obstructions to sprinkler discharge.   The baffles are 2 ft. 
deep panels hung vertically every ft.  The top of the baffle is just over 18 
ins. From the sprinkler heads so NFPA 13 would indicate that there is no 
obstruction problem because they do not exceed the 4 ft. obstruction trigger 
for obstruction more than 18 in. below the heads. 

However, the panels are every foot and it sure seems like a significant 
obstruction, but the installation does not violate NFPA 13 for obstructions.

Has anyone ever dealt with this issue and offer any insight.

Thanks,

Rich Richardson
Seattle Fire Department



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to