Are these suspended in such a way that they can swing back and forth 
in any air flow? Could a fire plume moving up through them have any 
unforeseen consequences?  Just thoughts from someone who over-thinks 
everything.




>Subject: RE: Sound Baffles
>
>Thanks for the thoughts.  The suspended obstruction table is met quite
>easily (though this is not Light hazard), meaning that water can get over
>the top of the obstruction, but it will just hit the next panel.
>
>The rules for obstructions greater than 18 in. speak to significant
>horizontal obstructions, which is not the case here. The horizontal element
>is only 2 ins. Max.
>
>I suppose this is no different than deep exposed beams where a head is
>placed in each beam pocket, none of which meet the beam rule.  There does
>not seem to be a basis to deny the proposal.
>
>Rich Richardson
>Seattle Fire Department
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Thursday, October 29, 2009 13:26
>To: [email protected]; Richardson, R
>Subject: RE: Sound Baffles
>
>Unfortunately that section deals with grid or egg-crate type ceilings where
>the ceiling panel is much thinner than the 24 inches of depth of the sound
>baffles.
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Hinson, Ryan
>Sent: Thursday, October 29, 2009 4:03 PM
>To: [email protected]
>Subject: RE: Sound Baffles
>
>I would refer to NFPA 13 (2007) section 8.15.13.  This refers to the
>obstruction of the vertical member to the developing spray pattern.  I would
>reduce the square footage per head to protect this area.
>
>Ryan Hinson
>Burns & McDonnell
>Direct: 952-656-6003 Ext 3662
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Richardson, R
>Sent: Thursday, October 29, 2009 2:55 PM
>To: [email protected]
>Subject: Sound Baffles
>
>We are reviewing a proposal to install sound baffles suspended from the
>roof, and evaluating obstructions to sprinkler discharge.   The baffles
>are 2 ft. deep panels hung vertically every ft.  The top of the baffle is
>just over 18 ins. From the sprinkler heads so NFPA 13 would indicate that
>there is no obstruction problem because they do not exceed the 4 ft.
>obstruction trigger for obstruction more than 18 in. below the heads.
>
>However, the panels are every foot and it sure seems like a significant
>obstruction, but the installation does not violate NFPA 13 for obstructions.
>
>Has anyone ever dealt with this issue and offer any insight.
>
>Thanks,
>
>Rich Richardson
>Seattle Fire Department
>

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to