Don't get me wrong; I don't necessarily believe that freezing is something to 
be taken lightly; I'm just parsing the sentence in NFPA 13.  And you're right; 
there's a revision bar in my 2007 edition next to 8.16.4.1.3.

I'm not so naïve to think that this wasn't interpreted that way by most AHJ's 
in the past when the code technically didn't require heat from 32.1dF to 
39.9dF.  It looks like the committee cleaned this up, finally.

Thanks!



Eric J. Shelton, PE
Senior Fire Protection Engineer
Associate

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
 
v: (804) 521.7105 f: (804) 217.8520
http://www.haengineers.com


 Do you really need to print this e-mail?



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, November 12, 2009 4:39 PM
To: [email protected]
Subject: Re: Gulf Coast

Methinks Eric has an older version because It used to be what he says
but now its what David says.

On Thu, Nov 12, 2009 at 1:26 PM, Autry, David <[email protected]> wrote:
> "Where does it say 40dF?"
>
> NFPA 13 (2002, Edition) 8.15.3.1.1
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
> ** Note new email address: [email protected]
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Eric Shelton
> Sent: Thursday, November 12, 2009 3:19 PM
> To: [email protected]
> Subject: RE: Gulf Coast
>
> Where does it say 40dF?  My copy of 13 says that were piping is subject to 
> freezing it shall be heated to 40dF.
>
>
> Eric J. Shelton, PE
> Senior Fire Protection Engineer
> Associate
>
> Hankins and Anderson
> Consulting Engineers
> 4880 Sadler Road Suite 300
> Glen Allen, VA 23060
>
> v: (804) 521.7105 f: (804) 217.8520
> http://www.haengineers.com
>
>
>  Do you really need to print this e-mail?
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Cliff Whitfield
> Sent: Thursday, November 12, 2009 4:05 PM
> To: [email protected]
> Subject: RE: Gulf Coast
>
> Chris,
>
> Believe me, I live here (in the panhandle of Florida), it gets cold here at
> times.  I can remember plenty of times growing up that it got in the teens.
>
> Besides, I believe 13 says "reliably maintained at or above 40° F " so it
> doesn't really matter how long or how low it gets.  I would not think of
> designing a system around here and not have freeze protection if it were not
> in a conditioned space.
>
> Cliff Whitfield, SET
> President
> Fire Design, Inc.
>
> [email protected]
> www.fire-design.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Thursday, November 12, 2009 1:20 PM
> To: [email protected]
> Subject: Gulf Coast
>
> Note I'm a little north of the Gulf Coast if this question sounds a little
> odd.  Would you be looking at a dry system in an unheated warehouse within
> say 5 miles of the northern Gulf Coast?  Seriously I know it can get cool by
> our standards down there but it ain't cold.   But for how long?  Even a day
> or 2 in the mid 20's would that cause a freeze up problem in a 100,000
> sq.ft. plus building?  Just wondering what the norm is for dealing with cool
> weather.  I know I've been in the Tampa and Orlando area and seen plenty of
> exterior wet risers not to mention the double checks off the UG.  My
> question is a little more LA specific.
>
>
>
> Chris Cahill, P.E.
>
> Fire Protection Engineer
>
> Sentry Fire Protection, Inc.
>
>
>
> 763-658-4483
>
> 763-658-4921 fax
>
>
>
> Email: [email protected]
>
>
>
> Mail: P.O. Box 69
>
>        Waverly, MN 55390
>
>
>
> Location: 4439 Hwy 12 SW
>
>              Waverly, MN 55390
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to