And that's the point. By the way, the values for fixture counts in 13R are identical to those in the plumbing code and probably (there's the getting ready to step in the poop word) come directly from the plumbing code. Could I get the civil to CALC a more rationale projected domestic demand for the complex? Sure, if there is one or if someone will pay him to do it. Otherwise I have nothing to use but the fixture count method (schedule) which is over-kill and really for (I'll venture probably again) single buildings off a loop which NFPA 13R directs me to incorporate into my fire sprinkler calculations. Funny though is that I only have to add gpm and not any pressure drop. Bet 54 units (or was it buildings) worth of folks with normal domestic usage will have a substantial effect on residual pressure on a dead end main no matter how big.
On Wed, Dec 2, 2009 at 1:57 PM, Ben Young <[email protected]> wrote: > My understanding is that the reason we don't account for sprinkler systems > in additional buildings is because most (if not all) NFPA codes work under > the assumption that there will be only one fire in one building. I can > understand that from a statistical standpoint, but as far as plumbing > demands go, if you have a fire in an apartment complex, people in other > buildings aren't going to stop showering or washing their dishes. > > Eric, I responded to your comment to expand on your last statement, not to > disagree with you. I agree about the separate connection dilemma in 13R vs > 13 systems, and wonder why this has never been addressed by the code > committees before. > > On Wed, Dec 2, 2009 at 4:48 PM, Eric Tysinger <[email protected]> wrote: > >> That makes a lot more sense if the plumbing values for the specific project >> for domestic demand aren't as great as what 13R tells us to use, but in a >> code driven industry, do we follow the code of 13R or use the possibly less >> demanding plumbing values. >> >> Also, looking at the previous posts, one is to assume that no matter what, >> the domestic demand needs to be accounted for. So why does NFPA 13R say it >> is only required to be accounted for on shared connections? If those >> connections are separate at the 8" main in front of the building, as shown >> in figure A.6.5.3(b)is it not a shared connection? Why is it not an issue >> with NFPA 13 systems? Lets say we have a client who typically uses large >> volumes of water, (restaurants, laundry mat facilities and many others that >> exist), we have to account for 100 or 250 for hose allowance, when the >> actual water usage may be much greater. If 13R systems where that concerned >> with additional water usage (domestic) why isn't there a hose allowance. 13R >> has been around through several code cycles where the knowledge of multiple >> multi-family buildings on the same site were being built. Why hasn't 13R >> addressed this issue more clearly, why haven't they addressed the issue of >> multiple buildings needin >> g to be accounted for. We don't account for the sprinkler systems in the >> addition buildings. One is led to think that we need only be concerned with >> the building at hand. >> >> -----Original Message----- >> From: [email protected] [mailto: >> [email protected]] On Behalf Of Steve Leyton >> Sent: Wednesday, December 02, 2009 4:22 PM >> To: [email protected] >> Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition >> (Handbook) >> >> Good points, but theoretical. I don't have to run the numbers to know that >> adding 250 GPM to even a very long run of 8" won't add 1 PSI to the demand. >> As Eric pointed out, if we use the tabled values from 13R, we could get a >> ridiculous concurrent flow allowance from multiple buildings. 13R is NOT >> the plumbing code; I guess what I was trying to say (very inefficiently, I >> must admit) is that if we have a serious and vested interest in PLUMBING, we >> should use the PLUMBING CODE. Or the plumbing engineer, which is WAY more >> convenient and gives us another (separate) responsible charge party to point >> fingers at and to sue later when the recriminations start. >> >> Steve Leyton >> Protection Design & Consulting >> San Diego, CA >> >> >> >> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)