2006 IBC/IFC

901.2 Fire protection systems. Fire protection systems shall be
installed, repaired, operated and maintained in accordance with this
code and the International Fire Code. Any fire protection system for
which an exception or reduction to the provisions of this code has been
granted shall be considered to be a required system.

[F] 903.1.1 Alternative protection. Alternative automatic
fire-extinguishing systems complying with Section 904 shall be permitted
in lieu of automatic sprinkler protection
where recognized by the applicable standard and approved by the fire
code official.

TABLE 601
FIRE-RESISTANCE RATING REQUIREMENTS FOR BUILDING ELEMENTS (hours)
e. An approved automatic sprinkler system in accordance with Section
903.3.1.1 shall be allowed to be substituted for 1-hour
fire-resistance-rated construction, provided
such system is not otherwise required by other provisions of the code or
used for an allowable area increase in accordance with Section 506.3 or
an allowable
height increase in accordance with Section 504.2. The 1-hour
substitution for the fire resistance of exterior walls shall not be
permitted.

Hope that helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Michael
J. Ricks
Sent: Thursday, February 11, 2010 9:38 AM
To: [email protected]
Subject: Gas systems replacing sprinklers

Does anyone know if NFPA specifically states that a gas fire suppression
system can replace a fire sprinkler in a room, or rooms? I scanned and
searched and the only section it addresses that issue is in marine
systems 25.1.5, partial systems. Section 1.5 possibly covers it but
convincing a fire marshal of that could be a bit tough. Thanks.
 
Aaron Johnson
Northwest Consulting, Inc. 
 

 

Aaron:

 

NFPA 13 2002 edition A.8.1.1 states:  "This standard contemplates full
sprinkler protection for all areas..Other NFPA standard that mandate
sprinkler installation might not require sprinklers in certain areas.
The requirements of this standard should be used insofar as they are
applicable.
The AHJ should be consulted in each case.  A building is considered
sprinklered throughout when protected in accordance with the
requirements of this standard."

 

It seems to me that you need to request a modification based on
alternative materials and methods (see IFC 104.8 and 104.9).  In short,
you will need to show the AHJ why there are practical difficulties
involved in providing sprinklers in the area in question and show him
that the proposed system provides an equivalent level of protection.  If
I were presenting it I would be ready to offer a minimum design area to
3000 sq. ft. and maybe a rated enclosure around the unsprinklered area.
I think most AHJ's would go for that.

 

 

Michael Ricks

Katco Fire Sprinkler Design

P.O. Box 607

555 South 100 East

Salem, UT   84653

801-423-3096  Cell:  801-380-4651

[email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to