Does anyone know if NFPA specifically states that a gas fire suppression
system can replace a fire sprinkler in a room, or rooms? I scanned and
searched and the only section it addresses that issue is in marine systems
25.1.5, partial systems. Section 1.5 possibly covers it but convincing a
fire marshal of that could be a bit tough. Thanks.
 
Aaron Johnson
Northwest Consulting, Inc. 
 

 

Aaron:

 

NFPA 13 2002 edition A.8.1.1 states:  "This standard contemplates full
sprinkler protection for all areas..Other NFPA standard that mandate
sprinkler installation might not require sprinklers in certain areas.  The
requirements of this standard should be used insofar as they are applicable.
The AHJ should be consulted in each case.  A building is considered
sprinklered throughout when protected in accordance with the requirements of
this standard."

 

It seems to me that you need to request a modification based on alternative
materials and methods (see IFC 104.8 and 104.9).  In short, you will need to
show the AHJ why there are practical difficulties involved in providing
sprinklers in the area in question and show him that the proposed system
provides an equivalent level of protection.  If I were presenting it I would
be ready to offer a minimum design area to 3000 sq. ft. and maybe a rated
enclosure around the unsprinklered area.  I think most AHJ's would go for
that.

 

 

Michael Ricks

Katco Fire Sprinkler Design

P.O. Box 607

555 South 100 East

Salem, UT   84653

801-423-3096  Cell:  801-380-4651

[email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to