My apologies for re-visiting this subject but I have been off of here for a 
while. 

This was a general question. Not associated with one building type or room 
size. It was brought to my attention by the sales person that the fire marshals 
are making the contractors put in sprinklers with the gas systems based on the 
following code;

NFPA 13 2007
4.1 Level of Protection. A building, where protected by an
automatic sprinkler system installation, shall be provided with
sprinklers in all areas except where specific sections of this
standard permit the omission of sprinklers.

An argument could be based on the following, but it still does not specifically 
allow the omission of "water based sprinklers" 

NFPA 13 2007
1.5 Equivalency. Nothing in this standard is intended to prevent
the use of systems, methods, or devices of equivalent or
superior quality, strength, fire resistance, effectiveness, durability,
and safety over those prescribed by this standard. Technical
documentation shall be submitted to the authority having
jurisdiction to demonstrate equivalency. The system,
method, or device shall be approved for the intended purpose
by the authority having jurisdiction.
1.6 New Technology.
1.6.1 Nothing in this standard shall be intended to restrict
Nothing in this standard shall be intended to restrict
new technologies or alternate arrangements, provided the
level of safety prescribed by this standard is not lowered.


The  Novec 1230 systems from Viking are basically designed for a single room. I 
have multiple projects around the country that I can use this system on, small 
computer rooms around 12'x12'.  The higher temp sprinkler in the room would act 
as a backup to the system, but that defeats the purpose of the gas system to 
eliminate the chance of a sprinkler accidentally going off in a room, I know 
that the odds are very slim, but tell that to building owners who see them 
going off all the time in the movies. I guess what it will come down to is a 
ruling from each individual fire Marshall. 

Thanks for the help!

Aaron Johnson
Northwest Consulting, Inc.






-----Original Message-----
From: [email protected]
To: [email protected]
Sent: Thu, Feb 11, 2010 7:25 am
Subject: RE: Gas systems replacing sprinklers


Didn't we just visit this question or is my e-mail system doing something funky?
Aaron, the consensus from the last time we discussed this was that the building 
ode is what governs whether you can make the substitution or not along with 
pproval by the AHJ.  NFPA has no preference.  
You need to know if the architect took some of the allowances for area 
increases 
r egress or other things that were based on the building being fully 
prinklered before attempting to omit sprinklers from any area. 

raig L. Prahl, CET   
ire Protection Specialist
echanical Department
H2MHILL
ockwood Greene
500 International Drive
O Box 491, Spartanburg, SC  29304-0491
irect - 864.599.4102
ax - 864.599.8439
[email protected]
ttp://www.ch2m.com 

----Original Message-----
rom: [email protected] 
[mailto:[email protected]] 
n Behalf Of Michael J. Ricks
ent: Thursday, February 11, 2010 9:38 AM
o: [email protected]
ubject: Gas systems replacing sprinklers
Does anyone know if NFPA specifically states that a gas fire suppression system 
an replace a fire sprinkler in a room, or rooms? I scanned and searched and the 
nly section it addresses that issue is in marine systems 25.1.5, partial 
ystems. Section 1.5 possibly covers it but convincing a fire marshal of that 
ould be a bit tough. Thanks.

aron Johnson
orthwest Consulting, Inc. 

 
Aaron:
 
NFPA 13 2002 edition A.8.1.1 states:  "This standard contemplates full 
sprinkler 
rotection for all areas..Other NFPA standard that mandate sprinkler 
nstallation might not require sprinklers in certain areas.  The requirements of 
his standard should be used insofar as they are applicable.
he AHJ should be consulted in each case.  A building is considered sprinklered 
hroughout when protected in accordance with the requirements of this standard."
 
It seems to me that you need to request a modification based on alternative 
aterials and methods (see IFC 104.8 and 104.9).  In short, you will need to 
how the AHJ why there are practical difficulties involved in providing 
prinklers in the area in question and show him that the proposed system 
rovides an equivalent level of protection.  If I were presenting it I would be 
eady to offer a minimum design area to 3000 sq. ft. and maybe a rated enclosure 
round the unsprinklered area.  I think most AHJ's would go for that.
 
 
Michael Ricks
Katco Fire Sprinkler Design
P.O. Box 607
555 South 100 East
Salem, UT   84653
801-423-3096  Cell:  801-380-4651
[email protected]
 
 
_______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)
______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to