I can't imagine that computer equipment in a 12x12 room can be so
costly as to justify a fire system that will not protect the building
if it fails on it's one shot or justifies the additional cost of
back-up equipment (i.e.: multiple additional bottles) to provide for a
second try just to mitigate against a myth about accidental discharge
being a common problem in 12 x 12 computer rooms. Heads that fail by
themselves usually leak rather than discharge and the clumsy
maintenance guy and his ladder can be mitigated against by using a
single (12 x 12 room) concealed head. Rather, put in the wet head,
spend the extra twenty bucks to make it concealed and use the
thousands saved for off-site records back-up (records being the actual
valuable item, not the hardware--that is unless you can now get a
thermo-nuclear powered, cryogenically cooled, Cray Super Computer in a
12 x12 room these days).

On Thu, Feb 11, 2010 at 9:20 AM,  <[email protected]> wrote:
>
> That does help. Thanks. 903.1.1 That states specifically that the "water 
> based sprinklers" can be eliminated if an approved alternative method( gas 
> system in this case) is used and approved by the AHJ. Some AHJ's really get 
> hung up on a specific section and will not see past a single paragraph no 
> matter what else you show them in the book.
>
> Thank you
>
> Aaron Johnson
> Northwest Consulting, Inc.
> formally in the Northwest now based in Palm Springs, CA
>
>
>
>
>
>
> -----Original Message-----
> From: John Drucker <[email protected]>
> To: [email protected]
> Sent: Thu, Feb 11, 2010 7:31 am
> Subject: RE: Gas systems replacing sprinklers
>
>
>  2006 IBC/IFC
> 901.2 Fire protection systems. Fire protection systems shall be
> nstalled, repaired, operated and maintained in accordance with this
> ode and the International Fire Code. Any fire protection system for
> hich an exception or reduction to the provisions of this code has been
> ranted shall be considered to be a required system.
> [F] 903.1.1 Alternative protection. Alternative automatic
> ire-extinguishing systems complying with Section 904 shall be permitted
> n lieu of automatic sprinkler protection
> here recognized by the applicable standard and approved by the fire
> ode official.
> TABLE 601
> IRE-RESISTANCE RATING REQUIREMENTS FOR BUILDING ELEMENTS (hours)
> . An approved automatic sprinkler system in accordance with Section
> 03.3.1.1 shall be allowed to be substituted for 1-hour
> ire-resistance-rated construction, provided
> uch system is not otherwise required by other provisions of the code or
> sed for an allowable area increase in accordance with Section 506.3 or
> n allowable
> eight increase in accordance with Section 504.2. The 1-hour
> ubstitution for the fire resistance of exterior walls shall not be
> ermitted.
> Hope that helps,
> John Drucker Jr CET
> ire Protection Subcode Official
> ire/Building/Electrical Inspector
> orough of Red Bank, NJ
> -----Original Message-----
> rom: [email protected]
> mailto:[email protected]] On Behalf Of Michael
> . Ricks
> ent: Thursday, February 11, 2010 9:38 AM
> o: [email protected]
> ubject: Gas systems replacing sprinklers
> Does anyone know if NFPA specifically states that a gas fire suppression
> ystem can replace a fire sprinkler in a room, or rooms? I scanned and
> earched and the only section it addresses that issue is in marine
> ystems 25.1.5, partial systems. Section 1.5 possibly covers it but
> onvincing a fire marshal of that could be a bit tough. Thanks.
>
> aron Johnson
> orthwest Consulting, Inc.
>
>
> Aaron:
>
> NFPA 13 2002 edition A.8.1.1 states:  "This standard contemplates full
> prinkler protection for all areas..Other NFPA standard that mandate
> prinkler installation might not require sprinklers in certain areas.
> he requirements of this standard should be used insofar as they are
> pplicable.
> he AHJ should be consulted in each case.  A building is considered
> prinklered throughout when protected in accordance with the
> equirements of this standard."
>
> It seems to me that you need to request a modification based on
> lternative materials and methods (see IFC 104.8 and 104.9).  In short,
> ou will need to show the AHJ why there are practical difficulties
> nvolved in providing sprinklers in the area in question and show him
> hat the proposed system provides an equivalent level of protection.  If
>  were presenting it I would be ready to offer a minimum design area to
> 000 sq. ft. and maybe a rated enclosure around the unsprinklered area.
>  think most AHJ's would go for that.
>
>
> Michael Ricks
> Katco Fire Sprinkler Design
> P.O. Box 607
> 555 South 100 East
> Salem, UT   84653
> 801-423-3096  Cell:  801-380-4651
> [email protected]
>
>
> _______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email
> o:[email protected]
> Put the word unsubscribe in the subject field)
>
> ONFIDENTIAL AND PROPRIETARY:
> his email message is intended only for the use of the individual or entity to
> hich it is addressed and may contain information that is privileged and
> onfidential, nor is it, unless specifically stated, intended to be relied upon
> y any person or persons other than the individual or entity named above and no
> arranties or representations are made or intended to persons or entities not
> amed above.  If the reader is not the intended recipient, you are hereby
> otified that any dissemination, distribution or copying of this communication
> s strictly prohibited.  If you have received this communication in error,
> lease notify us immediately by telephone, return this message to the address
> bove and delete all copies.  Thank you.
> _______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
InstrucRon Greenman, CET, FPE
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to