Gaseous extinguishing systems in carousels is tricky business. We tried this on one unit due to the dollar value of parts involved. These things are not very air tight. Doing a door fan test is fun. We had to cut a circular hole in the top to fit the fan to and then patch with a sheet metal cover plate. 25 tubes of caulk and weatherstripping on the parts-picking door to get it to pass the fan test.
It can be done but is not a routine job. CO2 may be easier to meet the conditions but the temperature change from a discharge may not be well-handled by the parts being stored. John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | [email protected] From: Todd Williams <[email protected]> To: [email protected] Date: 02/26/2010 10:58 AM Subject: Re: Carousel Storage Units Sent by: [email protected] I don't know of anything in 13 that addresses this. I believe that this type of storage, on a much larger scale, is used in Europe. (Perhaps some of out brethren from across the pond could help out.) Without doing a lot of research, my guess would be to put a couple of concealed heads at the top and use a CO2 or dry chem extinguishing system. A lot of potential obstructions for water, but a gas system might not be a bad solution. Of course, some could consider it furniture and say it doesn't need sprinklers. At 11:23 AM 2/26/2010, you wrote: >I've been searching NFPA 13 for info on protection of these type of >storage units. They are typically fully enclosed, have rows of >plastic bins which are linked together by a drive mechanism, often >computer indexed to an operator can enter a part number and the rows >of bins rotate until the appropriate row is at the operator opening >for access. They can be of any size, we're looking at about 10-15 >feet wide, about 5-10 ft deep and about 20 ft tall. The parts in >the plastic bins are supposed to be mostly non-combustible (they >used the term mostly and that's all they'll share). > >http://www.kardexremstar.com/content/products/vertical/ > >I can't find anything in 13, so either the Standard doesn't address >these or I'm using the wrong term. > >I do know there is an FM Data Sheet on them but we are directed not >to follow FM data. This is a foreign client who insists that if >it's not in the Building or Fire code they are not going to do it >regardless of who says to do what. I can't argue with that but I do >need to make sure the situation has been addressed. > > >Craig L. Prahl, CET >Fire Protection Specialist >Mechanical Department >CH2MHILL >Lockwood Greene >1500 International Drive >PO Box 491, Spartanburg, SC 29304-0491 >Direct - 864.599.4102 >Fax - 864.599.8439 >[email protected] >http://www.ch2m.com > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)