Gaseous extinguishing systems in carousels is tricky business.  We tried
this on one unit due to the dollar value of parts involved.  These things
are not very air tight.  Doing a door fan test is fun.  We had to cut a
circular hole in the top to fit the fan to and then patch with a sheet
metal cover plate.  25 tubes of caulk and weatherstripping on the
parts-picking door to get it to pass the fan test.

It can be done but is not a routine job.  CO2 may be easier to meet the
conditions but the temperature change from a discharge may not be
well-handled by the parts being stored.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]


                                                                                
                                       
  From:       Todd Williams <[email protected]>                                     
                                        
                                                                                
                                       
  To:         [email protected]                                  
                                       
                                                                                
                                       
  Date:       02/26/2010 10:58 AM                                               
                                       
                                                                                
                                       
  Subject:    Re: Carousel Storage Units                                        
                                       
                                                                                
                                       
  Sent by:    [email protected]                          
                                       
                                                                                
                                       





I don't know of anything in 13 that addresses this. I believe that
this type of storage, on a much larger scale, is used in Europe.
(Perhaps some of out brethren from across the pond could help out.)
Without doing a lot of research, my guess would be to put a couple of
concealed heads at the top and use a CO2 or dry chem extinguishing
system. A lot of potential  obstructions for water, but a gas system
might not be a bad solution. Of course, some could consider it
furniture and say it doesn't need sprinklers.


At 11:23 AM 2/26/2010, you wrote:
>I've been searching NFPA 13 for info on protection of these type of
>storage units.   They are typically fully enclosed, have rows of
>plastic bins which are linked together by a drive mechanism, often
>computer indexed to an operator can enter a part number and the rows
>of bins rotate until the appropriate row is at the operator opening
>for access.  They can be of any size, we're looking at about 10-15
>feet wide, about 5-10 ft deep and about 20 ft tall.  The parts in
>the plastic bins are supposed to be mostly non-combustible (they
>used the term mostly and that's all they'll share).
>
>http://www.kardexremstar.com/content/products/vertical/
>
>I can't find anything in 13, so either the Standard doesn't address
>these or I'm using the wrong term.
>
>I do know there is an FM Data Sheet on them but we are directed not
>to follow FM data.  This is a foreign client who insists that if
>it's not in the Building or Fire code they are not going to do it
>regardless of who says to do what.  I can't argue with that but I do
>need to make sure the situation has been addressed.
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to