The applicable code section regarding the removal of non required fire 
protection system is not in NFPA 13 or the IBC.  It is in Section 901.6 of the 
IFC (2006)



901.6 Inspection, testing and maintenance. 

Fire detection, alarm and extinguishing systems shall be maintained in an 
operative condition at all times, and shall be replaced or repaired where 
defective. Nonrequired fire protection systems and equipment shall be 
inspected, tested and maintained or removed.



Some jurisdictions will apply "removed" to be fully removed.  Others may allow 
removal only of the parts that are visible.  There is no single, correct 
answer.  It depends upon how the AHJ wants to apply this IFC provision.


Robert J. Pielow, P.E.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, April 08, 2010 12:07 PM
To: [email protected]
Subject: RE: abandoned pipe

Three screened suction intakes off the bottom of the pool min 6' apart so
one person can't block all and have their intestines pulled out- it's
happened. 8" to keep the velocity down. Order fire pump with knowledge of
pool additives.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, April 08, 2010 12:26 PM
To: '[email protected]'
Subject: RE: abandoned pipe

Just curious: how do you keep children and pool toys out of the pump inlet?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, April 08, 2010 11:29 AM
To: [email protected]
Subject: RE: abandoned pipe

If applicable code didn't require, Ron faced what isn't all that unusual,
and reminds me of the two times we used swimming pools for pump suction-

We do a lot because it's the right thing to do. Lots of these things don't
cost a lot, sometimes, like a tank, they do. I don't like using a pool, but
I'm not donating a tank to the job cause I don't like what the owner wants
to do; nor am I necessarily walking away from a job because of this. Once
every 18 years I've used a pool for water supply, and they work.

Other things are a little hairier. We generally use a 2,000 GPM pump on ESFR
jobs. Its 10" not 8" so our costs go up, not insignificantly. But when the
tenant adds a conveyor and the design area goes from 12 to 14 heads, we
don't want to say you need a new pump. We explain this, but imagine we do
lose jobs over the difference. If you're selling the GC not the
developer/owner, it's a harder sell- or they just don't care/don't
understand. 

I know, bid 1500 and add alt for 2,000 is possible, etc.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Thursday, April 08, 2010 12:03 PM
To: [email protected]
Subject: RE: abandoned pipe

You beat me to it Dave.  I knew there was a 'false sense of security' clause
on 1 somewhere.
I always thought it only meant heads, devices, etc.
Tom


NFPA 1 (2003, Edition)
4.5.8.2
Existing life safety features obvious to the public, if not required by the
Code, shall be either maintained or removed. 

David Autry

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to