I agree with Brad on this one. The code says that it is acceptable as long as 
"each unprotected ceiling pocket is separated from any adjacent unprotected 
pocket by a minimum 10 feet horizontal distance" 13 2007 8.6.7.2 (4)

It seems like a protected ceiling pocket would not get in the way of this 
requirement.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Pielow, Robert
Sent: Thursday, April 22, 2010 11:09 AM
To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com
Subject: RE: skylights vs. ceiling pockets

Creative thinking Brad, but I think all three would need sprinklers.  I do not 
think a sprinklered pocket within 10 feet is the same as no pocket within 10 
feet.

Robert J. Pielow, P.E.
Fire Protection & Life Safety



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad
Sent: Thursday, April 22, 2010 11:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: skylights vs. ceiling pockets

And by the way-- say you have 3 skylights, 3' square, at 9' c-c, those
skylights would need to be sprinklered, right? Wrong-- only the middle one
needs a head, bcoz now the other 2 are separated by at least 10' from any
other unprotected ceiling pocket! (2010 clarifies)

-----Original Message-----
From: Pielow, Robert [mailto:robert.pie...@hdrinc.com] 
Sent: Thursday, April 22, 2010 10:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: skylights vs. ceiling pockets

I do not believe NFPA 13 requires a sprinkler in either a pocket or skylight
that meet the prescribed limitations on size and dimension.  The recesses
are required to be separated by at least 10 feet so any delay caused by the
height of the pocket would not have an impact.  The sprinkler handbook
provides a good description of this condition.  It references skylights or
"similar pockets".

Robert J. Pielow, P.E.


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R
Sent: Thursday, April 22, 2010 10:38 AM
To: sprinklerforum@firesprinkler.org
Subject: skylights vs. ceiling pockets

Am I understanding the standard correctly in that a ceiling pocket that
would otherwise require sprinklers may no longer require sprinklers if I
were to install a skylight in the pocket, regardless of depth etc.?  

If the answer is yes, any logical reasons one could offer would be helpful. 

Thanks,

Rich Richardson
Seattle Fire Department
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to