Agreed! Robert J. Pielow, P.E. Fire Protection & Life Safety
-----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise Sent: Thursday, April 22, 2010 11:13 AM To: 'sprinklerforum@firesprinkler.org' Subject: RE: skylights vs. ceiling pockets I agree with Brad on this one. The code says that it is acceptable as long as "each unprotected ceiling pocket is separated from any adjacent unprotected pocket by a minimum 10 feet horizontal distance" 13 2007 8.6.7.2 (4) It seems like a protected ceiling pocket would not get in the way of this requirement. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Pielow, Robert Sent: Thursday, April 22, 2010 11:09 AM To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com Subject: RE: skylights vs. ceiling pockets Creative thinking Brad, but I think all three would need sprinklers. I do not think a sprinklered pocket within 10 feet is the same as no pocket within 10 feet. Robert J. Pielow, P.E. Fire Protection & Life Safety -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Sent: Thursday, April 22, 2010 11:05 AM To: sprinklerforum@firesprinkler.org Subject: RE: skylights vs. ceiling pockets And by the way-- say you have 3 skylights, 3' square, at 9' c-c, those skylights would need to be sprinklered, right? Wrong-- only the middle one needs a head, bcoz now the other 2 are separated by at least 10' from any other unprotected ceiling pocket! (2010 clarifies) -----Original Message----- From: Pielow, Robert [mailto:robert.pie...@hdrinc.com] Sent: Thursday, April 22, 2010 10:53 AM To: sprinklerforum@firesprinkler.org Subject: RE: skylights vs. ceiling pockets I do not believe NFPA 13 requires a sprinkler in either a pocket or skylight that meet the prescribed limitations on size and dimension. The recesses are required to be separated by at least 10 feet so any delay caused by the height of the pocket would not have an impact. The sprinkler handbook provides a good description of this condition. It references skylights or "similar pockets". Robert J. Pielow, P.E. -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R Sent: Thursday, April 22, 2010 10:38 AM To: sprinklerforum@firesprinkler.org Subject: skylights vs. ceiling pockets Am I understanding the standard correctly in that a ceiling pocket that would otherwise require sprinklers may no longer require sprinklers if I were to install a skylight in the pocket, regardless of depth etc.? If the answer is yes, any logical reasons one could offer would be helpful. Thanks, Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)