The actual square footage at 0.01 for the A/D calc and the 20x20 for
the listed residential head calc, and then the greater of the two for
the actual demand.

On Sat, Oct 30, 2010 at 8:08 AM, Carrol Glimstad
<[email protected]> wrote:
> Ok,
>
> I get that it's either the listed flow (20x20) or the .10 over the spacing
> area... But what I want to know is what do I use for the "spacing area"?  Do I
> use the 20 x20 because my heads are 10 feet off of walls  (s x l) or can I use
> the square footage of the room (16 x16) at 256 sq. ft.?  And yup, this is the
> head that drives the calc, the other three heads queue up to this one at even
> smaller head spacings.
>
> Thanks!
> Carrol
>
>
>
>
>
> ________________________________
> From: Sprinkler Academy - C Bilbo <[email protected]>
> To: FORUM <[email protected]>
> Sent: Fri, October 29, 2010 6:46:06 PM
> Subject: RE: Residential "Room Design Method"?
>
>
> Ok.... to back-up Ron....
>
> While the "Most Remote Area" is fine once you understand what it is that we
> intend.....
>
> The "Most Demanding Area" is the most accurate description, but....
>
> NFPA 13 refers to the "hydraulically most demanding area", the "design area",
> the "remote area", "most remote sprinkler"
>
> It's worth pointing out what we mean, but once we understand..... let's drop 
> the
> semantics.
>
>
> As for residential demand and calculatons:
>
> Sprinklers should flow:
> a.  .10gpm/sq ft over the spacing area (small room rule can help here) OR,
> b.  The listed flow for the residential sprinkler (if it is more
> demanding.....as opposed to remote) OR,
> c.  Whatever the manufacturer says.
>
> d.  Whichever is greater.
>
> Did I mention that you should listen to Ron? (choose D.)
>
> Sincerely,
>
> Some guy named Cecil
> (not known for being politically correct... just ask the Patriots' 
> Cheerleaders)
>
>> Date: Fri, 29 Oct 2010 17:27:20 -0700
>> Subject: Re: Residential "Room Design Method"?
>> From: [email protected]
>> To: [email protected]
>>
>> Design area(s) guys. Remote implies furthest from riser and we all
>> know that that is not always correct. Unfortunately the kids don't
>> know that and they get the wrong idea into their impressionable little
>> heads when we say remote. Trust me. I have to fight this all the time.
>> No matter how often I try to tell them the right stuff and then they
>> hear remote somewhere and all my good work is for naught. Cecil can
>> probably get my back on this.
>>
>> On Fri, Oct 29, 2010 at 5:17 PM, A.P.Silva <[email protected]> wrote:
>> > Would "hydraulically most remote" be more politically correct?
>> >
>> > Tony
>> >
>> > -----Original Message-----
>> > From: [email protected]
>> > [mailto:[email protected]] On Behalf Of Ron Greenman
>> > Sent: October 29, 2010 6:02 PM
>> > To: [email protected]
>> > Subject: Re: Residential "Room Design Method"?
>> >
>> > Jamie,
>> >
>> > Might I suggest changing your habit of saying "remote" area with the more
>> > proper and less confusing term "design" area. Remote more properly refers 
>> > to
>> > the furthest distance from a DPV for the inspector's test connection. Back
>> > in the olden days, when most sprinklers went into manufacturing and
>> > warehousing facilities, big, open buildings with tree systems and typically
>> > uniform branch lines, the "remote" area and the "design" area typically 
>> > were
>> > the same, but that doesn't always hold true these days. Additionally, until
>> > you're sure there is only one then "design area(s)" is even more apropos.
>> > Don't get me wrong. I do the  same thing on occasion. Old habits are hard 
>> > to
>> > break, but I try to be cognitive of the fact that every time I use "remote"
>> > I'm inferring something I really don't mean.
>> >
>> > On Fri, Oct 29, 2010 at 4:46 PM, Jamie.seidl <[email protected]> wrote:
>> >> You need to calculate the most hydraulically remote 4 heads.  This is
>> > typically a loaded branch line that supplies a bedroom on the end of the
>> > line. For instance (20x20 * (400 sqft) @ .10 gpm = 40 gpm). This end head
>> > pressure will act on the rest of the heads on the BL, closets, bathroom,
>> > hallway so your total demand on a BL can be upwards of 160 gpm, depending 
>> > on
>> > configuration of the unit.  Keep in mind, you can mix K factors in
>> > residential occupancies to balance the hydraulics and minimize over
>> > discharge.
>> >>
>> >> Jamie
>> >> Sent from my iPhone
>> >>
>> >> On Oct 29, 2010, at 7:24 PM, Carrol Glimstad <[email protected]>
>> > wrote:
>> >>
>> >>> I'm designing a residential project using res. heads (LFII) and
>> >>> designing to full NFPA 13.  When I calc my four heads using the
>> >>> "design area", I am wondering if I can use the room design method to
>> >>> determine my sprinkler demand?  For instance, I have a room that
>> >>> measures 16' X 16', (256 sq. ft.) but the head is actually located 10
>> >>> feet off of the 2 adjacent far walls.  If using the flow rates from
>> >>> the chart I know that I need to flow 20 gpm from that head based on my
>> > maximum 20' x 20' spacing.  But If I'm using the .10 over the "design area"
>> >>> can I just use the demand of 25.6 gpm for that head (16' x 16' sq.
>> >>> ft.) versus the 40 gpm based on 20' x 20'?  I understand then I would
>> >>> then base my system requirements on the more demanding of the two
>> >>> methods.  I can flow all four heads at a 20 gpm no problem, but the 40
>> > gpm from just one head.....ouch!
>> >>> I haven't done residential in a looooong time, so thought I'd check
>> >>> for the heck of it and I'm pretty sure I'll find instead that I'm full of
>> > it!
>> >>> Thanks in advance!
>> >>>
>> >>> Carrol Glimstad
>> >>>
>> >>>
>> >>>
>> >>> _______________________________________________
>> >>> Sprinklerforum mailing list
>> >>> [email protected]
>> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>>
>> >>> For Technical Assistance, send an email to: [email protected]
>> >>>
>> >>> To Unsubscribe, send an email
>> >>> to:[email protected]
>> >>> (Put the word unsubscribe in the subject field)
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >>
>> >
>> >
>> >
>> > --
>> > Ron Greenman
>> > Instructor
>> > Fire Protection Engineering Technology
>> > Bates Technical College
>> > 1101 So. Yakima Ave.
>> > Tacoma, WA 98405
>> >
>> > [email protected]
>> >
>> > http://www.bates.ctc.edu/fireprotection/
>> >
>> > 253.680.7346
>> > 253.576.9700 (cell)
>> >
>> > Member:
>> > AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>> >
>> > They are happy men whose natures sort with their vocations. -Francis Bacon,
>> > essayist, philosopher, and statesman (1561-1626)
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>> >
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>> >
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>>
>> [email protected]
>>
>> http://www.bates.ctc.edu/fireprotection/
>>
>> 253.680.7346
>> 253.576.9700 (cell)
>>
>> Member:
>> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>>
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to