2007/11.3.1

see
11.3.1.1
and
11/.3.1.2

On Sat, Oct 30, 2010 at 9:04 AM,  <[email protected]> wrote:
> Carrol,
> I was always taught in sprinkler systems hydraulics,you MUST use the actual
> head spacing (in your case 20'x20') to determine the maximum end head
> pressure.I have heard of others who have used the averaging method but
> haven't found anyone to give me the actual code section to back this up.
> If this is a situation where only one area is driving the 20x20 condition,it
> may be more feasable to just add a few heads to attain a lower end head
> condition that will work for the entire system.A few heads could save a lot
> of larger pipng,etc.
>
> Lamar Vaughn,SET
>
>
>
>
> On Sat, Oct 30, 2010 at 11:08 AM, Carrol Glimstad wrote:
>
>> Ok,
>> I get that it's either the listed flow (20x20) or the .10 over the spacing
>> area... But what I want to know is what do I use for the "spacing area"?  Do
>> I use the 20 x20 because my heads are 10 feet off of walls  (s x l) or can I
>> use the square footage of the room (16 x16) at 256 sq. ft.?  And yup, this
>> is the head that drives the calc, the other three heads queue up to this
>> one at even smaller head spacings.
>>
>> Thanks!
>> Carrol
>>
>>
>>
>>
>>
>> ________________________________
>> From: Sprinkler Academy - C Bilbo <[email protected]>
>> To: FORUM <[email protected]>
>> Sent: Fri, October 29, 2010 6:46:06 PM
>> Subject: RE: Residential "Room Design Method"?
>>
>>
>> Ok.... to back-up Ron....
>>
>> While the "Most Remote Area" is fine once you understand what it is that
>> we intend.....
>>
>> The "Most Demanding Area" is the most accurate description, but....
>>
>> NFPA 13 refers to the "hydraulically most demanding area", the "design
>> area", the "remote area", "most remote sprinkler"
>>
>> It's worth pointing out what we mean, but once we understand..... let's
>> drop the semantics.
>>
>> As for residential demand and calculatons:
>>
>> Sprinklers should flow:
>> a.  .10gpm/sq ft over the spacing area (small room rule can help here) OR,
>> b.  The listed flow for the residential sprinkler (if it is more
>> demanding.....as opposed to remote) OR,
>> c.  Whatever the manufacturer says.
>>
>> d.  Whichever is greater.
>>
>> Did I mention that you should listen to Ron? (choose D.)
>>
>> Sincerely,
>>
>> Some guy named Cecil
>> (not known for being politically correct... just ask the Patriots'
>> Cheerleaders)
>>
>>> Date: Fri, 29 Oct 2010 17:27:20 -0700
>>> Subject: Re: Residential "Room Design Method"?
>>> From: [email protected]
>>> To: [email protected]
>>>
>>> Design area(s) guys. Remote implies furthest from riser and we all
>>> know that that is not always correct. Unfortunately the kids don't
>>> know that and they get the wrong idea into their impressionable little
>>> heads when we say remote. Trust me. I have to fight this all the time.
>>> No matter how often I try to tell them the right stuff and then they
>>> hear remote somewhere and all my good work is for naught. Cecil can
>>> probably get my back on this.
>>>
>>> On Fri, Oct 29, 2010 at 5:17 PM, A.P.Silva <[email protected]> wrote:
>>>>
>>>> Would "hydraulically most remote" be more politically correct?
>>>>
>>>> Tony
>>>>
>>>> -----Original Message-----
>>>> From: [email protected]
>>>> [mailto:[email protected]] On Behalf Of Ron
>>>> Greenman
>>>> Sent: October 29, 2010 6:02 PM
>>>> To: [email protected]
>>>> Subject: Re: Residential "Room Design Method"?
>>>>
>>>> Jamie,
>>>>
>>>> Might I suggest changing your habit of saying "remote" area with the
>>>> more
>>>> proper and less confusing term "design" area. Remote more properly
>>>> refers to
>>>> the furthest distance from a DPV for the inspector's test connection.
>>>> Back
>>>> in the olden days, when most sprinklers went into manufacturing and
>>>> warehousing facilities, big, open buildings with tree systems and
>>>> typically
>>>> uniform branch lines, the "remote" area and the "design" area typically
>>>> were
>>>> the same, but that doesn't always hold true these days. Additionally,
>>>> until
>>>> you're sure there is only one then "design area(s)" is even more
>>>> apropos.
>>>> Don't get me wrong. I do the  same thing on occasion. Old habits are
>>>> hard to
>>>> break, but I try to be cognitive of the fact that every time I use
>>>> "remote"
>>>> I'm inferring something I really don't mean.
>>>>
>>>> On Fri, Oct 29, 2010 at 4:46 PM, Jamie.seidl <[email protected]>
>>>> wrote:
>>>>>
>>>>> You need to calculate the most hydraulically remote 4 heads.  This is
>>>>
>>>> typically a loaded branch line that supplies a bedroom on the end of the
>>>> line. For instance (20x20 * (400 sqft) @ .10 gpm = 40 gpm). This end
>>>> head
>>>> pressure will act on the rest of the heads on the BL, closets, bathroom,
>>>> hallway so your total demand on a BL can be upwards of 160 gpm,
>>>> depending on
>>>> configuration of the unit.  Keep in mind, you can mix K factors in
>>>> residential occupancies to balance the hydraulics and minimize over
>>>> discharge.
>>>>>
>>>>> Jamie
>>>>> Sent from my iPhone
>>>>>
>>>>> On Oct 29, 2010, at 7:24 PM, Carrol Glimstad
>>>>> <[email protected]>
>>>>
>>>> wrote:
>>>>>
>>>>>> I'm designing a residential project using res. heads (LFII) and
>>>>>> designing to full NFPA 13.  When I calc my four heads using the
>>>>>> "design area", I am wondering if I can use the room design method to
>>>>>> determine my sprinkler demand?  For instance, I have a room that
>>>>>> measures 16' X 16', (256 sq. ft.) but the head is actually located 10
>>>>>> feet off of the 2 adjacent far walls.  If using the flow rates from
>>>>>> the chart I know that I need to flow 20 gpm from that head based on my
>>>>
>>>> maximum 20' x 20' spacing.  But If I'm using the .10 over the "design
>>>> area"
>>>>>>
>>>>>> can I just use the demand of 25.6 gpm for that head (16' x 16' sq.
>>>>>> ft.) versus the 40 gpm based on 20' x 20'?  I understand then I would
>>>>>> then base my system requirements on the more demanding of the two
>>>>>> methods.  I can flow all four heads at a 20 gpm no problem, but the 40
>>>>
>>>> gpm from just one head.....ouch!
>>>>>>
>>>>>> I haven't done residential in a looooong time, so thought I'd check
>>>>>> for the heck of it and I'm pretty sure I'll find instead that I'm full
>>>>>> of
>>>>
>>>> it!
>>>>>>
>>>>>> Thanks in advance!
>>>>>>
>>>>>> Carrol Glimstad
>>>>>>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>>
>>>>>> For Technical Assistance, send an email to: [email protected]
>>>>>>
>>>>>> To Unsubscribe, send an email
>>>>>> to:[email protected]
>>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to: [email protected]
>>>>>
>>>>> To Unsubscribe, send an email
>>>>> to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>
>>>>
>>>>
>>>> --
>>>> Ron Greenman
>>>> Instructor
>>>> Fire Protection Engineering Technology
>>>> Bates Technical College
>>>> 1101 So. Yakima Ave.
>>>> Tacoma, WA 98405
>>>>
>>>> [email protected]
>>>>
>>>> http://www.bates.ctc.edu/fireprotection/
>>>>
>>>> 253.680.7346
>>>> 253.576.9700 (cell)
>>>>
>>>> Member:
>>>> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>>>>
>>>> They are happy men whose natures sort with their vocations. -Francis
>>>> Bacon,
>>>> essayist, philosopher, and statesman (1561-1626)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>>
>>> [email protected]
>>>
>>> http://www.bates.ctc.edu/fireprotection/
>>>
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>>
>>> Member:
>>> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>>>
>>> They are happy men whose natures sort with their vocations. -Francis
>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>>                         _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>>
>>      _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to