At some point, the requirement for the flexible coupling kicks in.  Have always 
understood 9.3.2.3 (1) - 2010 edition, previous ones numbered differently - to 
include the main system riser, so the flange or adaptive fitting would have to 
be configured to allow a flex coupling at no more than 24" above the floor.

SL




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Tuesday, July 12, 2011 7:17 AM
To: [email protected]
Subject: RE: Transition from Outside to Inside

Bill - I'm going to go on a limb a bit and suggest there is no maximum height. 

There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the transition 
piece (23.1.6.1.1). It is implied that underground pipe is only underground. An 
aggressive AHJ or EOR may argue that the flange must be located at the floor 
level - so no underground pipe is above-ground and vice versa. I would suggest 
that it really only matters when dealing with plastic underground transitioning 
to above-ground pipe. No plastic pipe should be allowed above ground, so the 
transition should start below grade. I always spec' ductile iron into the 
building. This meets the intent of 23.1.6.1.1 as a transition.  We normally 
shoot for the transition to the above-ground pipe to occur at 6 to 12 inches 
above the floor, but there is nothing in 13 that mandates any particular height.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
[email protected] 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Tuesday, July 12, 2011 8:07 AM
To: [email protected]
Subject: Transition from Outside to Inside

Something I thought I could find but couldn't.  What is the maximum height for 
the floor flange to transition from the below ground pipe to the above ground 
pipe?  (NFPA 13-2010, 6.3 & 23.1.6.1.1)  Ductile and plastic are not listed in 
the Table 6.3.1.1.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to