At the outlet of the hose connection, or in other words, at the beginning of the hose. Be sure to include the hose valve in the hydraulics!
Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: A.P.Silva [mailto:[email protected]] Sent: Tuesday, July 12, 2011 1:11 AM To: [email protected] Subject: NFPA 14 Standpipe systems shall be one of the following: (1) Hydraulically designed to provide the required waterflow rate at a minimum residual pressure of 100 psi (6.9 bar) at the outlet of the hydraulically most remote 21/2-in. (63.5-mm) hose connection and 65 psi (4.5 bar) at the outlet of the hydraulically most remote 11/2-in. (38.1-mm) hose station. 65 psi is required at the end of the 100 foot long 1 1/2" hose or at the beginning? I would say at the beginning as that would be the outlet of the hose stations. But would like other opinions. Thanks, Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)