I agree with Mark. Some folks (including the TC at the ROP meeting) seem to think it is acceptable based on 13:A.10.6.5 showing part of the underground pipe extending above the floor. They seem to have ignored that the Figure is ductile so doesn't address plastic and seem to have forgotten that the listing for underground plastic pipe applies to it being underground. As soon as it is exposed (whether in a trench or as a transition piece above the floor) it has to be acceptable as an above ground pipe. Needless to say, this issue will be addressed again at the ROC meeting.

Roland

On Jul 12, 2011, at 7:16 AM, Mark Sornsin wrote:

Bill - I'm going to go on a limb a bit and suggest there is no maximum height.

There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the transition piece (23.1.6.1.1). It is implied that underground pipe is only underground. An aggressive AHJ or EOR may argue that the flange must be located at the floor level - so no underground pipe is above-ground and vice versa. I would suggest that it really only matters when dealing with plastic underground transitioning to above- ground pipe. No plastic pipe should be allowed above ground, so the transition should start below grade. I always spec' ductile iron into the building. This meets the intent of 23.1.6.1.1 as a transition. We normally shoot for the transition to the above- ground pipe to occur at 6 to 12 inches above the floor, but there is nothing in 13 that mandates any particular height.

Mark A. Sornsin, PE| Fire Protection Engineer
Ulteig Engineers, Inc.| Fargo, ND
[email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to