We have local ahjs that require dual feed for all most all systems however; you 
can only use the most remote feed in the calculations.  NFPA 13 requires the 
signage.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, October 27, 2011 4:17 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dual floor control assembies

There would have to be or a single flow would set off all WFSs since it would 
act as a big vertical grid.

Believe the dual connection is Marriott standard on high-rises, much to my 
chagrin.

Posting a sign at both sides that it's dual feed is something my insurance 
carrier would make me post- what if you got dragged into some bonehead that 
shut a side, opened the drain, let it flow while going to the head with ladder, 
and ASSUMED it was drained and pulled the head?
If you installed and didn't post signage, you're dragged into it and have some 
mud you could have avoided.
Even 1 5% culpability of a $1m claim in a highrise is $150k on your loss runs- 
for years.....and you could stick a zero on the end of that portion pretty 
easily if their lawyer convinced the unwashed jury that you'd done something 
unusual and mislead his poor unsuspecting bonehead.

I haven't done a dual feed I can recall since 80's there has to be a reason 
why. I recall when I did it (Stonybrook Manor), the code changed prohibiting 
like a year later.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Garth W. Warren
Sent: Thursday, October 27, 2011 3:00 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dual floor control assembies

I believe there is a requirement for check valves at each connection.

Garth

----- Original Message ----- 
From: "Ronl.Fletcher" <rfletc...@aerofire.com>
To: <sprinklerforum@firesprinkler.org>
Sent: Wednesday, October 26, 2011 1:13 PM
Subject: Dual floor control assembies


> Is anyone aware of a prohibition against having two floor control 
> assemblies  on each floor connected to two different standpipes and 
> calculating the loop to size the sprinkler main?
>
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to