Matt,

I believe a product such as Allied's ABF coated pipe would meet the intent
as corrosion resistant therefore being an alternative to galvanized. Since
galvanized pipe is starting to fall out of favor, this will probably be
used more often to satisfy that particular code section.


Justin Reid

On Thu, Oct 27, 2011 at 4:56 PM, Matt Grise <m...@afpsprink.com> wrote:

> In the 2007/2010 edition of NFPA 13, section 8.3.4.3 allows k 4.2
> sprinkler heads to be used on dry systems where the piping is corrosion
> resistant or internally galvanized.
>
> Are there any options that people are aware of for corrosion resistance
> besides internally galvanized? (Copper being too expensive, and plastic not
> allowed for full 13 dry systems)
>
> Would a system that is charged with Nitrogen meet the intent?
>