Scot, I don't see anything that sends you back to 11.2.3.2.5 to increase the in-rack design requirement by 30%. 11.2.3.2.5 is an area of sprinkler operation increase, not a number of design sprinklers increase. Intuitively, yes. Prescriptive, no.
Scott Futrell (763) 425-1001 x 12 Office (612) 759-5556 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of å... .... Sent: Thursday, May 31, 2012 11:50 AM To: [email protected] Subject: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in open racks 2010 NFPA 13 When one uses dry-pipe with combination in-rack/ceiling sprinklers to protect Class IV to greater than 25 ft per Table 16.3.1.1, the 30% increase applies to both in-rack and overhead sprinklers, yes? scot deal excelsior fire -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120601/1810b32c/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum