Again,  hazard is  Group A/Class IV.
I hedge because the client is trying to downgrade to Class III.
The fact is that the average commodity by weight is 60% PE, and
  now they are out looking for some water-soaked wood pallets
  to change the weight % category.

Further to this client, they are in cold country, where it freezes in
winter.
They don't want to heat their 300k sq. ft warehouse...so the dry-systems.

I begged them to go with FM approved ceiling-only large
orifice sprinklers.  I have given them the reasons, including that the owner
will be able to re-lease the building easier than if there were in-racks
left
behind in their warehouse, when this client leaves in 5 years time.

Best I can do, is admit my mistakes, document the uptakes, and
learn from the forum.   Thank you all for your wisdom.  My vote is in:
FM rocks.

scot deal
excelsior fire


>