Scott,
I think Scot Deal raised an interesting question. He's correct in the increase in area of 30%, per 12.5.1, but the question remains, if we have in-rack sprinklers, do we increase the number of them flowing in a dry system calculation? If so, why? If not, why not? The table Scot referenced doesn't allow the use of CMDA sprinklers without in-racks as well, so what do we do about the number flowing in the calc?

    Anyone have input on the answer?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 5/31/2012 10:13 AM, Scott A Futrell wrote:
Scot,

I don't see anything that sends you back to 11.2.3.2.5 to increase the in-rack 
design requirement by 30%.  11.2.3.2.5 is an area of sprinkler operation 
increase, not a number of design sprinklers increase.   Intuitively, yes.  
Prescriptive, no.

Scott Futrell
(763) 425-1001 x 12 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of å... ....
Sent: Thursday, May 31, 2012 11:50 AM
To: [email protected]
Subject: dry-pipe with in-rack/ceiling protection of Class IV to>  25 ft in 
open racks

2010 NFPA 13

When one uses dry-pipe with combination in-rack/ceiling sprinklers to protect 
Class IV to greater than 25 ft per Table 16.3.1.1, the 30% increase applies to 
both in-rack and overhead sprinklers, yes?

scot deal
excelsior fire
-------------- next part --------------
An HTML attachment was scrubbed...
URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120601/1810b32c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to