30% more sprinkler water required due to the fire being 30% bigger due to
time delay?

-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]] 
Sent: Thursday, May 31, 2012 1:19 PM
To: [email protected]
Subject: Re: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft
in open racks

Scott,
     I think Scot Deal raised an interesting question.  He's correct in 
the increase in area of 30%, per 12.5.1, but the question remains, if we 
have in-rack sprinklers, do we increase the number of them flowing in a 
dry system calculation?  If so, why?  If not, why not?  The table Scot 
referenced doesn't allow the use of CMDA sprinklers without in-racks as 
well, so what do we do about the number flowing in the calc?

     Anyone have input on the answer?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 5/31/2012 10:13 AM, Scott A Futrell wrote:
> Scot,
>
> I don't see anything that sends you back to 11.2.3.2.5 to increase the
in-rack design requirement by 30%.  11.2.3.2.5 is an area of sprinkler
operation increase, not a number of design sprinklers increase.
Intuitively, yes.  Prescriptive, no.
>
> Scott Futrell
>   
> (763) 425-1001 x 12 Office
> (612) 759-5556 Cell
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of å... ....
> Sent: Thursday, May 31, 2012 11:50 AM
> To: [email protected]
> Subject: dry-pipe with in-rack/ceiling protection of Class IV to>  25 ft
in open racks
>
> 2010 NFPA 13
>
> When one uses dry-pipe with combination in-rack/ceiling sprinklers to
protect Class IV to greater than 25 ft per Table 16.3.1.1, the 30% increase
applies to both in-rack and overhead sprinklers, yes?
>
> scot deal
> excelsior fire
> -------------- next part --------------
> An HTML attachment was scrubbed...
>
URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120601/1810b32c/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to