Scot,

I responded to the specific question (and assumed everyone understood the 30% 
increase would be applied to the roof/ceiling).  However, I would not recommend 
a dry system in-rack if you can avoid it.  Quell, preaction, other might be 
better if possible.  Also, an engineered solution where you calculate the 
delivery time to the in-rack sprinklers might be part of the solution.  No one 
has asked what the hazard is, the specifics, or why the dry system...

Scott 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of å... ....
Sent: Thursday, May 31, 2012 1:43 PM
To: [email protected]
Subject: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in 
open racks

I know in-racks are very effective,
if they are not turned off because
a forklift operator broke a sprinkler
(as a colleague rightly pointed out).

If a mitigation is warranted,
I would rather see that mitigation shorten the required water deliver time, 
than try to place catch up with more sprinklers.

scot deal
excelsior fire