Scot, I responded to the specific question (and assumed everyone understood the 30% increase would be applied to the roof/ceiling). However, I would not recommend a dry system in-rack if you can avoid it. Quell, preaction, other might be better if possible. Also, an engineered solution where you calculate the delivery time to the in-rack sprinklers might be part of the solution. No one has asked what the hazard is, the specifics, or why the dry system...
Scott -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of å... .... Sent: Thursday, May 31, 2012 1:43 PM To: [email protected] Subject: dry-pipe with in-rack/ceiling protection of Class IV to > 25 ft in open racks I know in-racks are very effective, if they are not turned off because a forklift operator broke a sprinkler (as a colleague rightly pointed out). If a mitigation is warranted, I would rather see that mitigation shorten the required water deliver time, than try to place catch up with more sprinklers. scot deal excelsior fire -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120601/dcf6e098/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum