If you get surprised when you are thinking logically, then are you really
thinking logically?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
On Mon, Jul 6, 2015 at 5:59 PM, [email protected]
<[email protected]> wrote:
But Aristotle was usually wrong. What I've found is that when I think
logically about how things ought to work from my observation physics
usually has a surprise of some sort in store for me. And I think I'd want
to block that spray pattern if the goal is to cool the column. I want most
of the water on the column, not somewhere behind it. But there I go with
logic again. Damned good thing neither I nor Aristotle write code books.

On Mon, Jul 6, 2015 at 2:54 PM, Kenneth Berman <[email protected]>
wrote:

> After careful review of the cited sections, all three instruct me to direct
> to the side of column. this can only be interpreted as horizontal, for a
> horizontal sidewall, or vertically toward the column, for a vertical
> sidewall. If protection of the piping and head is required (from forklift
> operators).then other measures should be taken. Perhaps a "head guard",
> they stop anything. With respect to Aristotle, logically the upward
> horizontal sidewall works best. I hate to obstruct the sidewall within a
> few inches. If memory serves, the only exception to installing other than
> listing is pendants in the upright position, under a wharf or dock.
>
> On Mon, Jul 6, 2015 at 4:29 PM, Parsley Consulting <
> [email protected]> wrote:
>
> > Ken,
> >
> > based on what I read in the sections I noted earlier I understand the
> > intent of NFPA 13 is to have the spray from the sidewall sprinkler,
> > horizontal or vertical, directed to one side of the column. If the spray
> > is directed up, how does that conform to what NFPA requires? Are you
> > suggesting the wording in NFPA 13 is incorrect, or that it's just being
> > incorrectly applied if the spray is directed horizontally, rather than
> > vertically?
> >
> > *Ken Wagoner, SET
> > *Parsley Consulting***
> > *350 West 9th Avenue, Suite 206
> > *Escondido, California 92025
> > *****Phone 760-745-6181*
> > Visit our website <http://www.parsleyconsulting.com/> ***
> > On 07/06/2015 2:09 PM, Kenneth Berman wrote:
> >
> >> What cools a fifty foot column above fifteen feet? Codes don't say
> install
> >> horizontal, vertical, up, down. In Tennessee gravity pulls the water
> down.
> >> I'm cooling twenty nine feet of column to prevent collapse.
> >>
> >> On Mon, Jul 6, 2015 at 3:55 PM, John Denhardt <
> >> [email protected]>
> >> wrote:
> >>
> >> Agree - I never seen one pointed up.
> >>>
> >>> John
> >>>
> >>> -----Original Message-----
> >>> From: Sprinklerforum [mailto:
> >>> [email protected]] On Behalf Of Travis
> >>> Mack,
> >>> SET
> >>> Sent: Monday, July 06, 2015 5:00 PM
> >>> To: [email protected]
> >>> Subject: Re: Column Protection
> >>>
> >>> Where does it say the sidewall is pointed up? I have only seen these
> >>> installed in the horizontal position for this application.
> >>>
> >>> Any steel columns shall be protected by 1-hour fireproofing or a
> >>> sidewall sprinkler directed to one side of the column at the top or at > >>> the 15 ft (4.6 m) level, whichever is lower. Flow from these sprinklers > >>> shall be permitted to be omitted from the sprinkler system demand for
> >>> hydraulic calculations.
> >>>
> >>>
> >>> Travis Mack, SET
> >>> MFP Design, LLC
> >>> 2508 E Lodgepole Drive
> >>> Gilbert, AZ 85298
> >>> 480-505-9271
> >>> fax: 866-430-6107
> >>> email:[email protected]
> >>>
> >>> http://www.mfpdesign.com
> >>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> >>> Send large files to us via: https://www.hightail.com/u/MFPDesign
> >>>
> >>> On 7/6/2015 1:57 PM, Kenneth Berman wrote:
> >>>
> >>>> You're all missing an important point, the horizontal sidewall is
> >>>> pointed
> >>>> upwards. A vertical sidewall, upwards, is incorrect. The horizontal
> >>>> sidewall cools the column from fifteen feet upwards, and the water
> >>>>
> >>> returned
> >>>
> >>>> by gravity cools the column below fifteen feet.
> >>>>
> >>>> On Mon, Jul 6, 2015 at 2:50 PM, Parsley Consulting <
> >>>> [email protected]> wrote:
> >>>>
> >>>> Rocci,
> >>>>> I'd echo Travis and Mark's comments. When all else fails, point
> >>>>> to
> >>>>> 12.12.2.2.4.1, 16.1.4.1, 17.1.4.1, or 18.2.1 (whichever is
> appropriate)
> >>>>>
> >>>> and
> >>>
> >>>> ask him, politely of course, how he's reaching the conclusion that the
> >>>>> sidewall sprinkler must be vertical.
> >>>>> In short, ask him to "prove it."
> >>>>> *Ken Wagoner, SET
> >>>>> *Parsley Consulting***
> >>>>> *350 West 9th Avenue, Suite 206
> >>>>> *Escondido, California 92025
> >>>>> *****Phone 760-745-6181*
> >>>>> Visit our website <http://www.parsleyconsulting.com/> ***
> >>>>>
> >>>>>
> >>>>> On 07/06/2015 11:20 AM, Rocci Cetani 3 wrote:
> >>>>>
> >>>>> I have a FM questioning the use of horizontal sidewall sprinklers
> (he
> >>>>>> thinks
> >>>>>> it should be a vertical sidewall) with no heat collectors @ 15'
> >>>>>>
> >>>>> AFF...NFPA
> >>>
> >>>> 13 2013 17.1.4.1 only states a sidewall sprinkler pointed in the
> >>>>>> direction of the column @ 15' AFF. Any suggestions?
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>> Rocci Cetani III, CET
> >>>>>>
> >>>>>> Lead Designer
> >>>>>>
> >>>>>> Water-Based Fire Protections Systems Layout, Nicet Level III
> >>>>>>
> >>>>>>
> >>>>>> Northern California Fire Protection Services Inc.
> >>>>>>
> >>>>>> 16840 Joleen Way Bldg. A
> >>>>>>
> >>>>>> Morgan Hill, CA 93037
> >>>>>>
> >>>>>> P-(408) 776-1580 EXT.111
> >>>>>>
> >>>>>> F-(408) 776-1590
> >>>>>>
> >>>>>> C- (408) 595-3906
> >>>>>>
> >>>>>>
> >>>>>> [email protected]
> >>>>>>
> >>>>>> www.norcalfire.com <http://www.norcalfire.com/>
> >>>>>>
> >>>>>>
> >>>>>> CONFIDENTIALITY NOTICE: This message and any document accompanying
> it
> >>>>>>
> >>>>> may
> >>>
> >>>> contain confidential information
> >>>>>>
> >>>>>> belonging to the sender. The information is intended only for the
> use
> >>>>>>
> >>>>> of
> >>>
> >>>> individual or entity named above. If you are not the intended
> >>>>>>
> >>>>> recipient,
> >>>
> >>>> or
> >>>>>> the employee or agent responsible to deliver this message to the
> >>>>>>
> >>>>> intended
> >>>
> >>>> recipient, you are hereby notified that any disclosure, copying or
> >>>>>>
> >>>>> taking
> >>>
> >>>> of
> >>>>>> any action in reliance on the contents of this information is
> strictly
> >>>>>> prohibited. If you have received this transmission in error, please
> >>>>>> immediately notify us by telephone to arrange for return of the
> >>>>>>
> >>>>> documents.
> >>>
> >>>>
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected]
> >>>>>>
> >>>>>>
> >>>>>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>>>
> >>>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>>
> >>>>>
> >>>>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>>
> >>>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>
> >>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to