We can use the sprinkler nozzle pressure, but as a means to the end of
estimating how high the sprinkler will project water:

1. use the nozzle pressure with K-factor to get flow = Q,
2. with Q, divide by  sprinkler orifice area (A) to get velocity.   This is
the max possible velocity as deflector will slow 90% of the spray.
3.  from velocity, use Bernoullis at v2= 0 m/s velocity, to predict the
height water will rise
4.  note, once the water is outside the sprinkler, the pressure is
essentially ambient, so P1 ~ P2 in Bernoulli's equation.
5.  solve for z, maximum height the water will rise from vertically
oriented sprinkler.

This seems like a lot of energy and discussion for a relatively minor
sprinkler design point.
I mean, if we have gotten to the point of a fire where a column sprinkler
is to save the structure, perhaps we earlier missed some more important
fire protectioin design-issues, at least more important than sidewall
horiztonal or sidewall down/up.

Do you think sometimes we put more energy into debating the simple points,
because they are simpler to think about,
and we spend less time debating the not-so-clear subject material, because
we don't want to spend the mental energy, even though that is the effort
that would yield the-most-design value for the time?



Scot Deal
Excelsior Fire/Risk Engineering