Ken,

based on what I read in the sections I noted earlier I understand the intent of NFPA 13 is to have the spray from the sidewall sprinkler, horizontal or vertical, directed to one side of the column. If the spray is directed up, how does that conform to what NFPA requires? Are you suggesting the wording in NFPA 13 is incorrect, or that it's just being incorrectly applied if the spray is directed horizontally, rather than vertically?

*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/06/2015 2:09 PM, Kenneth Berman wrote:
What cools a fifty foot column above fifteen feet? Codes don't say install
horizontal, vertical, up, down. In Tennessee gravity pulls the water down.
I'm cooling twenty nine feet of column to prevent collapse.

On Mon, Jul 6, 2015 at 3:55 PM, John Denhardt <[email protected]>
wrote:

Agree - I never seen one pointed up.

John

-----Original Message-----
From: Sprinklerforum [mailto:
[email protected]] On Behalf Of Travis Mack,
SET
Sent: Monday, July 06, 2015 5:00 PM
To: [email protected]
Subject: Re: Column Protection

Where does it say the sidewall is pointed up?  I have only seen these
installed in the horizontal position for this application.

Any steel columns shall be protected by 1-hour fireproofing or a
sidewall sprinkler directed to one side of the column at the top or at
the 15 ft (4.6 m) level, whichever is lower. Flow from these sprinklers
shall be permitted to be omitted from the sprinkler system demand for
hydraulic calculations.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 7/6/2015 1:57 PM, Kenneth Berman wrote:
You're all missing an important point, the horizontal sidewall is pointed
upwards. A vertical sidewall, upwards, is incorrect. The horizontal
sidewall cools the column from fifteen feet upwards, and the water
returned
by gravity cools the column below fifteen feet.

On Mon, Jul 6, 2015 at 2:50 PM, Parsley Consulting <
[email protected]> wrote:

Rocci,
      I'd echo Travis and Mark's comments. When all else fails, point to
12.12.2.2.4.1, 16.1.4.1, 17.1.4.1, or 18.2.1 (whichever is appropriate)
and
ask him, politely of course, how he's reaching the conclusion that the
sidewall sprinkler must be vertical.
      In short, ask him to "prove it."
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***


On 07/06/2015 11:20 AM, Rocci Cetani 3 wrote:

I have a FM questioning the use of horizontal sidewall sprinklers (he
thinks
it should be a vertical sidewall) with no heat collectors @ 15'
AFF...NFPA
13 2013   17.1.4.1  only states a sidewall sprinkler pointed in the
direction of the column @ 15' AFF.  Any suggestions?



Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

C- (408) 595-3906


[email protected]

www.norcalfire.com <http://www.norcalfire.com/>


CONFIDENTIALITY NOTICE: This message and any document accompanying it
may
contain confidential information

belonging to the sender. The information is intended only for the use
of
individual or entity named above. If you are not the intended
recipient,
or
the employee or agent responsible to deliver this message to the
intended
recipient, you are hereby notified that any disclosure, copying or
taking
of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the
documents.

_______________________________________________
Sprinklerforum mailing list
[email protected]


http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]


http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org