Travis,

I actually don't want to use CC heads because of the onerous draft stopping
requirements, so that's a negative.
Space is heated, so we're talking wet system here.


Benjamin Young

On Mon, Nov 21, 2016 at 3:10 PM, Travis Mack, SET <[email protected]>
wrote:

> I would say you have combustible framing members less than 3' on center so
> you are limited to 130 sq ft spacing.  If the space is less than 60" deep,
> you may want to consider something like the Tyco CC3 and get up to 16'
> spacing at 256 sq ft.  Also, the design area would be reduced.  You would
> have 1950 sq ft with SSU, assuming this is dry, or 1300 sq ft with CC3,
> again, assuming it is dry.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298480-505-9271
> fax: 866-430-6107email:[email protected]
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 11/21/2016 12:56 PM, Ben Young wrote:
>
> So I have a crawl space that was originally supposed to get drywall on the
> underside of the trusses, but now the owner wants sprinklers instead.
>
> This is inside an apartment building of type VB construction under the
> ground floor.  The crawl space is more than 36" deep, so it doesn't require
> CC heads.
>
> My question is how the heck do I treat the spacing for the heads I'm going
> to install?
>
> The structure is 14" deep TJIs that are stuffed with non-faced batt
> insulation that's held in place by furring strips.  My gut is telling me
> its not a smooth flat ceiling, but its also not exactly combustible
> obstructed either.
>
> At this point, I don't even know whether I should consider it obstructed
> or unobstructed.
>
>
> I'm leaning towards the insulation will act as a ceiling and I can go 1-12
> down from the bottom of the truss, and do 225 SQFT spacing, but can't find
> anything to assuage my fears in the code.
>
> This project was submitted under the 2010 edition of 13, but the AHJ now
> has adopted 2013, FYI.
>
> I looked through 8.15.1 but that doesn't really tell me HOW to space in
> these areas, just if I can omit or not... also didn't find too much of use
> in the AFSA informal interps.
>
> Any thoughts on this?
>
> Benjamin Young
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to