ABSOLUTELY.

What is funny is that Unobstructed with structural members less than 3 ft has a 
spacing limitation of 130SF.  That makes perfect sense for trusses with a 
cumulative negative impact on discharge but why should it be 130 sf for a 
ceiling with 2x4 stringers?  The reason is that after taking 3 cycles to 
FINALLY define an actual depth for unobstructed / obstructed, the issue of 
spacing has not been revisited - YET.  On my list for next cycle (that being 
2022 since we are in the middle of the 2019 cycle). 


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Nov 23, 2016, at 6:18 AM, Ed Kramer <[email protected]> wrote:
> 
> Roland,
>  
> If the structural members extended down below the insulation, but no further 
> than 4”, would you still consider it unobstructed?  More than 4” – obstructed?
>  
> Ed Kramer
> Bamford Fire Sprinkler
>  
>  