also funny is this could be a case where max deflector for unobstructed
exceeds that for obstructed:

 

if extends 4.5" below insulation-- obstructed = 10.5" max below insulation
due to 6" max below plane of obstructing member, vs 12" for unobstructed.

 

you gotta love this stuff

 

:) brad

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, November 23, 2016 10:14 AM
To: [email protected]
Subject: Re: Ceiling of trusses and insulation - Character set not allowed

 

ABSOLUTELY.

 

What is funny is that Unobstructed with structural members less than 3 ft
has a spacing limitation of 130SF.  That makes perfect sense for trusses
with a cumulative negative impact on discharge but why should it be 130 sf
for a ceiling with 2x4 stringers?  The reason is that after taking 3 cycles
to FINALLY define an actual depth for unobstructed / obstructed, the issue
of spacing has not been revisited - YET.  On my list for next cycle (that
being 2022 since we are in the middle of the 2019 cycle). 

 

 

Roland Huggins, PE - VP Engineering

American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

 

 

On Nov 23, 2016, at 6:18 AM, Ed Kramer <[email protected]> wrote:

 

Roland,

 

If the structural members extended down below the insulation, but no further
than 4", would you still consider it unobstructed?  More than 4" -
obstructed?

 

Ed Kramer

Bamford Fire Sprinkler

 

 