If this isn't included in the specifications for the project, offer them a change order price for compliance. That should get their attention.
Mark at Aero 602 820-7894 Sent from my iPhone On Jun 1, 2017, at 5:59 AM, Brian Harris <[email protected]<mailto:[email protected]>> wrote: Just got back some review comments for a project we’re doing and one in particular stuck out; “Orient longitudinal pipe weld seam toward building roof; at least 45 degrees in relationship to the floor (for reference, the weld line points to the floor at 0 degrees) to mitigate pipe weld seam corrosion.” Could you imagine the headache that would cause at the fab shop? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org