That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it
specified in project specs? Can you use seamless pipe to bypass the issue?

 

Damien Shannon.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: 01 June 2017 06:59
To: [email protected]
Subject: Review Comments

 

Just got back some review comments for a project we're doing and one in
particular stuck out;

"Orient longitudinal pipe weld seam toward building roof; at least 45
degrees in relationship to the floor (for reference, the weld line points to
the floor at 0 degrees) to mitigate pipe weld seam corrosion."

 

Could you imagine the headache that would cause at the fab shop?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 