FM adherence is not a requirement unless you’re directed by the OWNER to adhere 
to FM recommendations.  Just because FM publishes a Data Sheet doesn’t mean 
every portion will necessarily be followed.

The specifications should explicitly state what is to be followed and to what 
degree as this should have been agreed upon by the owner and their FM rep. and 
then communicated to the EOR and included in the engineering documents prior to 
bids.

Some owners will accept all insurer recommendations, others push back and take 
some and disregard other recommendations made by their insurer.  But that’s 
between the owner and insurer, not the contractor at the end of the line.

Any EOR worth his fee should be asking the owner at the beginning of the 
project who their insurer is and what unique requirements are expected for the 
project.  It’s irritating to get drawings that state something like “Follow FM 
Global guidelines”.  Follow what to what end?

FM’s recommendations are based on solid testing and verification of data but 
some of the recommendations do have an upcharge attached to them.  The engineer 
assigned to producing the fire protection package should be competent enough to 
understand the ramifications of insurer requirements/recommendations and 
incorporate those into the design package.  Don’t make the contractor do your 
work or have to guess.

This is an issue that gets overlooked a lot by engineers and not just FP 
engineers. All engineers on projects should understand how to work with the 
owner’s insurer since FM for example has data sheets on numerous other building 
systems other than just fire protection.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, June 01, 2017 10:00 AM
To: [email protected]
Subject: RE: Review Comments [EXTERNAL]

Luckily not an FM project.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Thursday, June 01, 2017 9:59 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Review Comments

Yes. That comes straight from FM. If you have an FM job, you will be held to 
that requirement.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jun 1, 2017, at 6:31 AM, Damien Shannon 
<[email protected]<mailto:[email protected]>> wrote:
That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it 
specified in project specs? Can you use seamless pipe to bypass the issue?

Damien Shannon.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: 01 June 2017 06:59
To: 
[email protected]<mailto:[email protected]>
Subject: Review Comments

Just got back some review comments for a project we’re doing and one in 
particular stuck out;
“Orient longitudinal pipe weld seam toward building roof; at least 45 degrees 
in relationship to the floor (for reference, the weld line points to the floor 
at 0 degrees) to mitigate pipe weld seam corrosion.”

Could you imagine the headache that would cause at the fab shop?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to