Damien- I didn't realize that was in the FM sheets but luckily this is not an FM project. There was no mention of it in the specs or on the contract drawings.
Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:[email protected]] On Behalf Of Damien Shannon Sent: Thursday, June 01, 2017 9:32 AM To: [email protected] Subject: RE: Review Comments That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it specified in project specs? Can you use seamless pipe to bypass the issue? Damien Shannon. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: 01 June 2017 06:59 To: [email protected]<mailto:[email protected]> Subject: Review Comments Just got back some review comments for a project we're doing and one in particular stuck out; "Orient longitudinal pipe weld seam toward building roof; at least 45 degrees in relationship to the floor (for reference, the weld line points to the floor at 0 degrees) to mitigate pipe weld seam corrosion." Could you imagine the headache that would cause at the fab shop? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935