100% agree, my last stop our only client was a major FM insured site, it 
took a lot of prodding but they started pushing back more and more as FMs 
requirements became more and more onerous to their pocketbook.  The real 
tipping point was the 4'-0" on center heads under non-flat obstructions 
over 4'.  I did find the requirement mentioned in FM datasheet 2-0 Revised 
in 2014 under 2.5.2.1 (we should always remember to cite "chapter and 
verse" as my last boss would say, I had to look it up).  Interestingly in 
my 6 years at said FM client, this NEVER came up even once.  Underwriters 
are underwriters, their enforcement power is limited to increasing policy 
costs, or revoking policies for non-compliance.  Owners need to be 
reminded/taught this and given their options form the contractor cost wise 
so they can see what if any cost impact the insurance requirement not 
being satisfied will create.



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   "Prahl, Craig/GVL" <[email protected]>
To:     "[email protected]" 
<[email protected]>
Date:   06/01/2017 10:26 AM
Subject:        RE: Review Comments
Sent by:        "Sprinklerforum" 
<[email protected]>



FM adherence is not a requirement unless you’re directed by the OWNER to 
adhere to FM recommendations.  Just because FM publishes a Data Sheet 
doesn’t mean every portion will necessarily be followed. 
 
The specifications should explicitly state what is to be followed and to 
what degree as this should have been agreed upon by the owner and their FM 
rep. and then communicated to the EOR and included in the engineering 
documents prior to bids.
 
Some owners will accept all insurer recommendations, others push back and 
take some and disregard other recommendations made by their insurer.  But 
that’s between the owner and insurer, not the contractor at the end of the 
line. 
 
Any EOR worth his fee should be asking the owner at the beginning of the 
project who their insurer is and what unique requirements are expected for 
the project.  It’s irritating to get drawings that state something like 
“Follow FM Global guidelines”.  Follow what to what end? 
 
FM’s recommendations are based on solid testing and verification of data 
but some of the recommendations do have an upcharge attached to them.  The 
engineer assigned to producing the fire protection package should be 
competent enough to understand the ramifications of insurer 
requirements/recommendations and incorporate those into the design 
package.  Don’t make the contractor do your work or have to guess. 
 
This is an issue that gets overlooked a lot by engineers and not just FP 
engineers. All engineers on projects should understand how to work with 
the owner’s insurer since FM for example has data sheets on numerous other 
building systems other than just fire protection.
 

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]

 
From: Sprinklerforum [
mailto:[email protected]] On Behalf Of Brian 
Harris
Sent: Thursday, June 01, 2017 10:00 AM
To: [email protected]
Subject: RE: Review Comments [EXTERNAL]
 
Luckily not an FM project.
 
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
 
From: Sprinklerforum [
mailto:[email protected]] On Behalf Of Travis 
Mack
Sent: Thursday, June 01, 2017 9:59 AM
To: [email protected]
Subject: Re: Review Comments
 
Yes. That comes straight from FM. If you have an FM job, you will be held 
to that requirement. 
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
 
Sent from my iPhone

On Jun 1, 2017, at 6:31 AM, Damien Shannon <[email protected]> wrote:
That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it 
specified in project specs? Can you use seamless pipe to bypass the issue?
 
Damien Shannon.
 
From: Sprinklerforum [
mailto:[email protected]] On Behalf Of Brian 
Harris
Sent: 01 June 2017 06:59
To: [email protected]
Subject: Review Comments
 
Just got back some review comments for a project we’re doing and one in 
particular stuck out;
“Orient longitudinal pipe weld seam toward building roof; at least 45 
degrees in relationship to the floor (for reference, the weld line points 
to the floor at 0 degrees) to mitigate pipe weld seam corrosion.”
 
Could you imagine the headache that would cause at the fab shop?
 
Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com
Phone: 704.896.9989
Fax: 704.896.1935
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=gcC7YInrqa8KtrGsHOm6RMAyxl8Ai7D3ntB2Qttaa5k&e=
 




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.