Yes. That comes straight from FM. If you have an FM job, you will be held to that requirement.
Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Jun 1, 2017, at 6:31 AM, Damien Shannon <[email protected]> wrote: > > That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it > specified in project specs? Can you use seamless pipe to bypass the issue? > > Damien Shannon. > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Brian Harris > Sent: 01 June 2017 06:59 > To: [email protected] > Subject: Review Comments > > Just got back some review comments for a project we’re doing and one in > particular stuck out; > “Orient longitudinal pipe weld seam toward building roof; at least 45 degrees > in relationship to the floor (for reference, the weld line points to the > floor at 0 degrees) to mitigate pipe weld seam corrosion.” > > Could you imagine the headache that would cause at the fab shop? > > Brian Harris, CET > BVS Systems Inc. > Design Manager > bvssystemsinc.com > Phone: 704.896.9989 > Fax: 704.896.1935 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org