Local requirement.
John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
From: Steve Leyton
Sent: Tuesday, July 30, 2024 4:30 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Dock System / Stand pipe
Why are the standpipe systems
While the building is a midrise, the stand pipe systems are automatic.
John Irwin via mobile device.
Fire Sprinkler Division
Solomon Plumbing
727-282-9243
Typed on tiny keys just for you. Please forgive spelling errors, typographical
transgressions, and grammatical gaffs
Ok understood. I mean that’s an argument for me doing what I want to do with
the stand pipe system.
John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
From: Steve Leyton
Sent: Tuesday, July 30, 2024 4:16 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject
Probably not doing that. =) Florida Building Code and Florida Fire Prevention
Code are as far as I dig.
John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
From: Steve Leyton
Sent: Tuesday, July 30, 2024 4:08 PM
To: Discussion list on issues relating to automatic fire sprinklers
Todd, this was my initial thought as well.
John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
From: Fpdcdesign
Sent: Tuesday, July 30, 2024 4:01 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Dock System / Stand pipe
Far am I to
nd pipe system? Is there any reason in NFPA 13 or 14 that I
can't extend my stand pipe system out horizontally?
John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
www.solomonplumbing.net
Cell: 727-282-9243
Office: 248-486-1600 (Corporate)
"The bitterness of poor quality remains
This is the answer I was looking for. We will contact the city for their
pumping ability.
Thank you
John Irwin
Branch Manager - Florida West Coast
Quick Response Fire Protection
Cell: 727-282-9243
"The bitterness of poor quality remains long after the sweetness of low price
is forg
) arranged so that
all zones can be maintained in full service with any one pump out of service.
(2) An auxiliary means that is capable of providing the full fire protection
demand and that is acceptable to the authority having jurisdiction.
John Irwin<https://www.linkedin.com/in/johnrir
te cochere. And parking is
temporary.
John Irwin
Director Of Construction
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
transgressions and grammatical gaffs.
From: Scott Futrell
Sent: T
orating too many "what if" scenarios. I was going to respond
what if a truck full of fireworks parks here? Should we protect for extra
hazard then?
Anyone have anything to help me convince him he's wrong? Should I pursue an
interpretation from AFSA or NFPA?
Thank you
John Irwin<htt
Victory!
Now if I can just stop a certain AHJ from making me put 200 psi on existing
piping...
John Irwin
Director Of Construction
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
transgressions and grammatical gaffs
Seems like your client has to choose between gearing up for a fight or writing
a little check.
John Irwin
Director of Construction
Quick Response Fire Protection
Cell: 727-282-9243
jir...@quickresponsefl.com
“The bitterness of poor quality remains long after the sweetness of low price
is forgott
I'd like that. The last time I went a couple rounds with her we did have a few
AFSA interpretations but none exactly fit the 'identical' situation so she
wasn't satisfied.
John Irwin
Director Of Construction
Quick Response Fire Protection
727-282-9243
Typed on tiny keys,
psi on these old systems.
At this very moment I have 2 guys still on a job making repairs after a failed
hydro this morning.
John Irwin
Director Of Construction
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
trans
And if some random person breaks a sprinkler inside the mail room, who's
responsible for the repair? This is my issue with having sprinklers outside the
fee simple unit.
John Irwin
Director of Construction
Quick Response Fire Protection
Cell: 727-282-9243
"The bitterness of po
e ROOFs of these rooms. Is this a factor?
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." - Benjamin Franklin
___
Sprinklerforum mailing
I have done a lot of these in many jurisdictions and never protected the
lockers. I have not been asked about it yet.
I do protect the 4x4 or 5x5 lockers that are full height.
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness o
Cecil,
I received several responses outside the user group and that section was
pointed out to me. And it was noted in my response to the AHJ.
Thank you
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling
pediatric office. Tell me
who’s responsible for that if it blows apart at 200 psi.
John Irwin
Quick Response Fire Protection
“The bitterness of poor quality remains long after the sweetness of low price
is forgotten.” – Benjamin Franklin
From: tfscolorado
Sent: Wednesday, August 19, 2020 1:02 PM
To
I included this reference in my response. From 4 different editions of 13. As
well as a half dozen informal interpretations from AFSA and explanatory
comments from the handbook.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you
Nobody has an informal code interpretation on this? I don't believe we're all
just putting 200 psi on other people's pipe. Anything saved from AFSA, NFSA or
NFPA would be great. Thanks
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long
Does anyone have a release of liability form for when the owner does decide to
have us pressure test the system rather than argue with the local Marshall.
John Irwin
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
ion.
Does anyone have a code interpretation from AFSA, NFSA or NFPA on this? Her
stance is that the code says "such as relocated drops" and I may have added a
few drops.
I am sure we have all come across this right?
John Irwin
Quick Response Fire Protection
"The bitterness of
these? I realize
they are not required but are they permitted to remain?
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
No.
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." - Benjamin Franklin
From: Sprinklerforum On Behalf
Of John Drucker via Sprinklerforum
Sent: Friday, May 29, 2020 8:42 AM
To: spri
If you work in Florida you should know that the AHJ doesn’t have the final say.
The code does. And while I agree that I would like to see sprinklers there, I
need to know if they are required as this is a BID situation.
John Irwin
Quick Response Fire Protection
“The bitterness of poor
he parking spaces are not
separated. To sprinkle or not to sprinkle?
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
www.quickresponsefl.com
Office: 844-9QUICKFL
Cell: 727-282-9243
Main Office: 20545 Independence Blvd. Unit G Groveland, Florida 34736
West Coast: 15201 Roos
board (along with sprinklers below
the ACT) should be good. If the fiberboard burns, I'd rather have sprinklers
above it than below ...
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." - Ben
Where you live does the AHJ have the authority to write his own fire code? In
Florida we would say "that's great that you want that, but no."
13D is two sprinklers. Do you even have 4 sprinklers in a single compartment?
This kind of thing makes me crazy.
John Irwin
West Coast
We have chapter 23 in NFPA 13 that gives us our checklist of what needs to be
included in our shop drawings.
Is there are similar check list for fire alarms? I don't see anything in NFPA 72
John Irwin
___
Sprinklerforum mailing list
Sprinkler
Thank you. We spend a ton of time in the NFPA codes so I'm very familiar with
jumping back to the definition section as your statement certainly applies to
the books I use daily as well.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys,
nyone have a fire alarm design class like AFSA and NFSA do for
sprinklers?
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Not in Florida.
Florida Fire Prevention Code > Local AHJ
It's a wonderful thing to have a state fire code that the local dum dums can't
walk all over.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please for
mercantile occupancy. Thoughts and opinions are welcome ...
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Thanks everyone.
Sprinklers it is.
John Irwin
Quick Response Fire Protection
“The bitterness of poor quality remains long after the sweetness of low price
is forgotten.” – Benjamin Franklin
From: Sprinklerforum On Behalf
Of Fpdcdesign
Sent: Tuesday, July 2, 2019 8:47 AM
To
They don't have an
insurance requirement that they are protected. They are all 48" wide.
What say ye?
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Our current opinion in the office is that because if these openings (six of
them), the ACT no longer meets the definition of a ceiling in NFPA 13. Thus the
deck now becomes a ceiling and the ACT becomes an obstruction.
[cid:image001.jpg@01D51AB7.D1292690]
John Irwin
Quick Response Fire
ng, ground Description
automatically generated][A large room Description automatically generated]
John Irwin
West Coast Branch Manager
www.quickresponsefl.com
Office: 844-9QUICKFL
Cell: 727-282-9243
Main Office: 20545 Independence Blvd. Unit G Groveland, Fl. 34736
West Coast: 4500 140th Avenue N
belief that
this should be acceptable?
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
from research, and from your
comments on this topic, and will present it to the owner as this is what I
think is “required” and this is what we should “probably do”.
John Irwin
Quick Response Fire Protection
“The bitterness of poor quality remains long after the sweetness of low price
is
it’s “severely
obstructed by occupancy, not structural conditions”.
[cid:image003.jpg@01D4B888.4F25FE20]
[cid:image005.png@01D4B888.4F25FE20]
[cid:image010.png@01D4B888.4F25FE20]
John Irwin
Quick Response Fire Protection
“The bitterness of poor quality remains long after the sweetness of low
ectly address this situation.
What say you?
John Irwin
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." - Benjamin Franklin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firespr
That makes sense,
Thanks Matt.
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." - Benjamin Franklin
From: Sprinklerforum On Behalf
Of Matt Grise
Sent: Tuesday, January 8, 2019 6:08 AM
To: spri
state. Does anyone
happen to have an old letter or verbiage from a set of plans that I can take a
look at? - Not my job, just trying to help a client out.
John Irwin
Branch Manager - West Coast
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CEL
es in dwelling unit.
After the first floor I go to all Res in Dwelling and Corridor.
I would do this on any floor with a mixed occupancy that doesnt have clear
seperation between hazards.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just fo
I like the premise, but the reference from the appendix only mentions Response
and not temperature. Also, we did make some changes to the system. A few low
offices and party rooms were added. I dont think this would fly in my situation.
John Irwin
West Coast Branch Manager
Quick Response Fire
because an AHJ doesn’t know what he’s talking
about. In this case, the AHJ is pretty knowledgeable and reasonable. So if I
can justify our opinion I think he would concede.
John Irwin
From: Sprinklerforum On Behalf
Of Joe Burtell
Sent: Thursday, January 3, 2019 5:02 PM
To: sprinklerforum
Exposed roof at about 25ft. 286 sprinklers are existing.
We have no information on the padding used for the park.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
transgressions and
tor, do I have to take alarm activation in to
consideration at all?
How would you proceed with this?
John Irwin
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CELL - 727-282-9243
___
Sprinklerforum maili
nklers all need to be changed?
Would there be any reason to call an assembly occupancy, ordinary hazard?
John Irwin
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
transgressions and grammatical gaffs.
___
Sprinklerfor
The bulk of the storage area is ceramic or porcelain tile, in wrapped boxes, on
wood slat pallets.
However there are “some” vinyl floor tiles (packaged the same way) and “some”
rolled rugs and carpet squares.
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Larry
I agree with this, except it calls for one level of in-racks.
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of cw bamford
Sent: Thursday, November 29, 2018 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Mixed rack storage
Calc seperate areas
I think I follow. And that makes sense.
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Mark Sornsin [FAR]
Sent: Wednesday, November 28, 2018 3:22 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: Mixed rack storage
John,
I assume the ceram
e to Group A, non-expanded
plastics. My question is this ... is it permissible for the client to storage
all their group A plastics on racks UNDER 12' and their ceramic floor tiles on
the racks OVER 12' and to then calculate the roof system for the lesser,
ceramic tile st
plate with all the correct
information without even performing a flow test. And I'd like to hear from some
more contractors on this.
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Steve Leyton
Sent: Wednesday, November 21, 2018 9:42 AM
To: spri
as originally designed?
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Now there’s a good question. I assumed ceramic or porcelain but obviously there
are a lot of other types.
RFI
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Fpdcdesign
Sent: Monday, November 5, 2018 4:10 PM
To: Sprinklerforum
Subject: Re: Storage Density
What
/3000 with high temperature sprinklers at
the roof.
NFPA 13 2016 edition.
Anyone disagree?
John Irwin
Branch Manager - West Coast
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CELL - 727-282-9243
___
Sprink
Wow. I didn't even consider an equalization manifold. Great response. I love
this group.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
transgressions and grammatical gaffs.
O
venting?
What standard am I using to design this contraption? Is it 1142 for a dry
hydrant?
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Matt Grise
Sent: Friday, November 2, 2018 8:07 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Always something new
artment from
imploding these tanks with their truck?
I'm looking forward to hearing your thoughts on this.
John Irwin
Branch Manager - West Coast
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CELL - 727-282-9243
Tyco’s technical department is usually pretty good at assisting working out the
use of the attic sprinklers.
John Irwin
Quick Response Fire Protection
From: Sprinklerforum On Behalf
Of Richard Mote
Sent: Friday, October 12, 2018 7:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject
is plan doesn't seem
to think I need sprinklers. I think I do.
What say you?
[cid:image003.png@01D46258.046A33A0]
John Irwin
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CELL - 727-282-9243
r with the
work, as required.
Michigan uses to have a test sprinkler contractors could take to seal plans.
Act 144 I think it was called. Florida needs that.
John Irwin
Quick Response Fire Protection
West Coast Branch Manager
CELL 727-282-9243
Typed on tiny keys, just for you. Please forgiv
If each area meets the criteria for a compartment, then I believe it's a
separate compartment and neither should require sprinklers.
John Irwin
Quick Response Fire Protection
West Coast Branch Manager
CELL 727-282-9243
Typed on tiny keys, just for you. Please forgive spelling e
Most sprinklers rating is to 175.
You're going to end up changing the sprinklers. Sounds like sooner rather than
later. And if we're talking about warehouse storage and you dont have a fire
pump I'd consider getting an evaluation done by a local FP contractor.
John Irwin
Quic
Is there a fire pump on the system? I mean you cant just pick a pressure to
dump water at because x pressure is required to operate the system.
You really just need to change the sprinklers. You got your money's worth out
of the old ones.
John Irwin
Quick Response Fire Protection
West
uld either
change them all or take a big sample and send them off to the lab. The former
is probably going to solve the issue.
John Irwin
Quick Response Fire Protection
West Coast Branch Manager
CELL 727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
tran
Are the sprinklers that actuate all in one area? Any chance there was a
previous heat incident that damaged a group of sprinklers?
John Irwin
Quick Response Fire Protection
West Coast Branch Manager
CELL 727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors
Just received the following from a friend in the industry...
El-o-matic el300 series heads ( fm approvals are explosion proof style; CSA
approvals look more normal) mounted on victauluc 300 series grooved butterfly's.
Find anyone that can sell the el-o-matic heads, and you're set. Our local gu
A company I worked for about 14 years ago used to use Victaulic. At least
the butterfly portion was Victaulic. And as I wasn't involved in the
purchasing I can't say with 100% certainty that they were listed.
John Irwin, C.E.T. - <mailto:jo...@cfcsystems.com> jo..
NFPA 88A 2015 edition: 9.2.4.1 –
Very helpful …
John Irwin
From: Sprinklerforum On Behalf
Of Travis Mack
Sent: Friday, July 13, 2018 11:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Robotic Parking
You are going to have to get the EOR that created your
This is 7 levels of cars stacked vertically. We are in the 2013 edition of NFPA
13.
John Irwin, C.E.T. – <mailto:jo...@cfcsystems.com> jo...@cfcsystems.com
Commercial Fire and Communications
Fire Sprinkler Specialist – NICET ID: 134153
Cell: 727-282-9243
From: Sprinklerfor
aware of. It's
pretty much 7 floors of this ..
The top floor doesn't show the center area protected. I'm wondering if it
needs to be .
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
Thanks everyone.
John Irwin
DynaFire Inc. – “*Same Day – Next Day*”
*From:* Sprinklerforum *On
Behalf Of *Steve Leyton
*Sent:* Thursday, May 17, 2018 11:36 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Misc Rack Storage
What Craig and Travis said. From a performance
We have a winner.
Thanks.
23.4.4.1.14 – uhg Is this even English?
John Irwin
DynaFire Inc. – “*Same Day – Next Day*”
*From:* Sprinklerforum *On
Behalf Of *MFP Design, LLC
*Sent:* Thursday, May 17, 2018 11:29 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Misc Rack
Regardless of the trailers, do I need to provide .6/2000 for the racks? If
so, do I need to do that for the entire 5,000 sqft area? Seems excessive.
John Irwin
DynaFire Inc. – “*Same Day – Next Day*”
*From:* Sprinklerforum *On
Behalf Of *Steve Leyton
*Sent:* Thursday, May 17, 2018 11
unit is 23-9.
The racks will contain a mix of group A plastic, emergency supplies in
plastic totes, with lids, on non-combustible pallets.
Do I really have to upgrade this entire space from OH II to .6/2000?
Do I tell them they should just not store over 12’?
John Irwin
Fire Sprinkler
’ bottles.
Propane Safe contains two tanks for forklift.
(1) – Do I have to be concerned about the propane in the “propane safe”?
(2) – What standard do I protect the Oxygen to? (NFPA 99 doesn’t seem to
fit this application)
John Irwin
Fire Sprinkler Specialist
DynaFire, Inc. – “*Same
Aww now you're going to make me pause Boss Baby and get my laptop.
I should also note that there are "engineered FPs" with this set but give no
direction on anything.. Florida engineering laws really need to change..
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Divisio
ding per NFPA 13, NFPA 13 still gives me the omission.
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please forgive brevity, typographical
errors, and grammatical gaffes.
On Apr 13, 2018, 7:37 PM, at 7:37 PM, Travis Mack wro
up of
coffee...
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please forgive brevity, typographical
errors, and grammatical gaffes.
On Apr 13, 2018, 6:42 PM, at 6:42 PM, Ed Kramer wrote:
>This is something we're seeing
setting 10 gallons of gas on
the court while they cut the grass..
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please forgive brevity, typographical
errors, and grammatical gaffes.
On Apr 13, 2018, 6:02 PM, at 6:02 PM, "
I was thinking about all the Porte Coches that I don't protect when looking at
this job. I've done Porte Cochres larger than this and not needed protection.
Personally I think idling cars present a higher risk of fire than a concrete
basketball court.
John Irwin
DynaFire Inc.
I'm not sure assuming the worst is the way to go. Additionally, 2/3 of the
covered area is concrete basketball court.
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please forgive brevity, typographical
errors, and gramma
I can appreciate your opinion, but I need a code reference. 😉
John Irwin
DynaFire Inc. – “*Same Day – Next Day*”
*From:* Sprinklerforum *On
Behalf Of *Steve Leyton
*Sent:* Friday, April 13, 2018 1:47 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Exterior Play Area
in that areas.
What say you?
John Irwin
Fire Sprinkler Specialist
DynaFire, Inc. – “*Same Day – Next Day*”
727-282-9243 – Cell
*“A customer is the most important visitor on our premises. He is not
dependent on us. We are dependent on him. He is not an interruption on our
work. He is
Combustible concealed space in a light hazard occupancy. Hatches or no
hatches ... Sprinklers yes.
John Irwin
DynaFire Inc. - "Same Day - Next Day"
-Original Message-
From: Sprinklerforum On
Behalf Of P & P Sprinklers Ltd
Sent: Thursday, March 29, 2018 9:48 AM
To:
I don't know if I would have the water to protect the attic in this place.
But I have made very clear what the difference between Residential
protection and NFPA 13 protection is.
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Mark.Phelps
Sent: M
And if I
can't come up with a solution for him I'll tell him so.
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Steve Leyton
Sent: Monday, March 19, 2018 10:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water stora
Are you suggesting I use the pool as my water supply?
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Mike Stossel
Sent: Monday, March 19, 2018 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage
I assume a house that
Yeah .. that's a concern I have as well.
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Matt Grise
Sent: Monday, March 19, 2018 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage
When I hear 'hurrican
Yep.
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Fpdcdesign
Sent: Monday, March 19, 2018 10:12 AM
To: Sprinklerforum
Subject: Re: Residential water storage
Is he aware that he is going to need a pump if he does not come off a
public supply
Nope. I offered that. They are adamant that they don't give up any floor
space.¯\_(ツ)_/¯
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum On
Behalf Of Travis Mack
Sent: Monday, March 19, 2018 9:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Reside
? Standard well
pump? Should I not even bother with a city supply if I am feeding off of a
tank? Obviously money doesn’t seem to be a consideration …
John Irwin
Fire Sprinkler Specialist
DynaFire, Inc.
727-282-9243 – Cell
*“A customer is the most important visitor on our premises. He is not
Great information. I really appreciate the time it must have taken to gather
this information. Thank you!
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Hinson, Ryan
Sent: Thursday, March 1, 2018 12:53
Thanks. That helps me get started.
Bouncing this mess back to the sales guy who sold it. ;)
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please forgive brevity, typographical
errors, and grammatical gaffes.
On Mar 1
properly.
Can someone provide direction on which path I even begin on. Where should I
look for proper spacing, calculation procedures. heck is there even a
requirement (I assume this will lead to knowing what’s being protected … )
Any leads are greatly appreciated.
John Irwin
Fire
Jeeze ... if it was a snake it would have bit me.
Tanks Pete.
John Irwin
DynaFire Inc.
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Pete Schwab
Sent: Monday, February 26, 2018 10:13 AM
To: sprinklerforum
are standard response.
Did we order the wrong sprinklers, or do we now have to change out the 90
standard response with new quick response?
I can’t find a code reference to specifically address this situation.
We are in 2013 CODE.
John Irwin
Fire Sprinkler Specialist
DynaFire, Inc.
727