[PSES] Test lab for testing power equipment at high altitude

2012-06-13 Thread Jim Eichner
Hi everyone:  We are investigating the availability of a facility in which 
we can qualify some higher power (500-1000kW) inverters for operation at 
altitudes above their 2000m design value - the higher the better but at 
least 3000m, preferably 4000m or 5000m.   We would consider labs that are 
located at high elevation, or labs that have altitude chambers large 
enough for an approx. 9'W x 2'D x 7'H product..  Investigation of the 
effects on thermal performance is the main focus, so we need to be able to 
run the products at full output, which requires high power AC to be 
available (I won't go into details on that - there are many options).

Does anyone know of such a lab?

Thanks in advance for your help.

Regards,

Jim
_
 


Jim Eichner  |   Schneider Electric Solar Business  |   Compliance 
Engineering Manager 
Phone: +1-604-422-2546  |   Mobile: +1-604-418-8472 
Email: jim.eich...@schneider-electric.com  |   Site: 
www.schneider-electric.com  |   Address: 3700 Gilmore Way, Burnaby, BC, 
V5G 4M1, Canada 

*** Please consider the environment before printing this e-mail 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

[PSES] Vacation

2011-12-02 Thread Jim Eichner
SET EMC-PSTC NOMAIL
_
 


Jim Eichner  |   Schneider Electric   |  Renewable Energies Business  |   
CANADA  |   Compliance Engineering Manager 
Phone: +1-604-422-2546 ext. 62546  |   Mobile: +1-604-418-8472 
Email: jim.eich...@schneider-electric.com  |   Site: 
www.schneider-electric.com/renewable-energies  |   Address: 3700 Gilmore 
Way, Burnaby, B.C., V5G 4M1 

*** Please consider the environment before printing this e-mail 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: Cigarette socket in vehicles

2009-01-22 Thread Jim Eichner
Exactly.  Products designed to SAE standards and OEM standards will be
hardened against all sorts of things, including 24V applied to 12V products,
reverse DC polarity, alternator load-dump transients, etc.  Products generally
available to consumers will generally not be designed to those requirements as
it adds significant cost.

 

The general answer to the sine wave vs square wave question is that the square
wave (the inverter industry calls it “modified sine wave”) is generally
compatible with most loads.  There are a few types of loads that get a bit
hotter due to the steep rising edges of the waveform, and years ago there used
to be some types of transformerless battery chargers (for portable tools,
phones, and the like) that would actually fail, but we haven’t seen anything
like that in a long long time. 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.

e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Doug Smith
Sent: Monday, January 19, 2009 12:40 PM
To: Price, Edward
Cc: emc-p...@ieee.org
Subject: Re: Cigarette socket in vehicles

 

Hi Ed and the group,

In addition to the 12/14 Volt question there are a few other points to
consider.

1) pretty big fast transients from loads like the starter motor

2) load dump conditions (battery becomes disconnected when engine is running)
where the alternator drives the voltage way above the normal ~14 Volts for a
time. This is more common that you might think, these days caused by lead-free
battery clamps failing. (Lead free battery clamps strikes me as a very bad
idea and does not accomplish anything compared to the battery itself and the
real source of lead from cars, the wheel weights flinging off wheels.) I have
observed first hand one of these clamps failing during use and immediately
replaced both clamps with nice lead ones.

Automotive electronics are designed to withstand load dump conditions but your
electronics may not be.

Doug

Price, Edward wrote: 

 

 

 





From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
rk...@chrysler.com
Sent: Monday, January 19, 2009 6:37 AM
To: Scott Xe
Cc: emc-p...@ieee.org
Subject: Re: Cigarette socket in vehicles


Hello Scott, 

In the case of 12V accessories to plug in normally they have a regulator
installed to prevent the overvoltage. 

Thank you. 

Rob Kado
EMC Engineer - Module Laboratory Operations
Chrysler 
 

 

Initial assumptions can be deceiving. I recently bought a Magellan GPS. It
operates on 5 VDC, and came equipped with an external cigarette socket
adapter. I assumed the cheapest, that there was a little resistor inside the
adapter, or just possibly a cheap linear regulator. On taking the adapter
apart (yes, I tend to do things like that), I was quite surprised to find a
little 2 custom IC switching converter, with input inductors, filter
capacitors and a hefty input overvoltage clamp.

 

The input voltage range was not specified, but it seems likely to be capable
of 24 VDC operation.

 

Ed Price

ed.pr...@cubic.com blocked::mailto:ed.pr...@cubic.com  WB6WSN

NARTE Certified EMC Engineer

Electromagnetic Compatibility Lab

Cubic Defense Applications

San Diego, CA  USA

858-505-2780

Military  Avionics EMC Is Our Specialty

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 





-- 

___  _   Doug Smith
 \  / )  P.O. Box 1457
  =  Los Gatos, CA 95031-1457
   _ / \ / \ _   TEL/FAX: 408-356-4186/358-3799
 /  /\  \ ] /  /\  \ Mobile:  408-858-4528
|  q-( )  |  o  |Email:   d...@dsmith.org
 \ _ /]\ _ / Website: http://www.dsmith.org


-

This message is from the IEEE Product Safety

RE: Sanity check on AC motors for boat use

2009-01-08 Thread Jim Eichner
Last time I checked, the Recreational Craft Directive and EMC Directive do not 
help much re this question.  There is the EN 60945 standard which includes 
sections on EMC for marine navigation and radio systems, and I've seen some 
non-navigation equipment approved to that standard, but it sounds like your 
equipment is out of scope of that standard.  That means you're left with the 
normal non-marine EMC regime.

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Doug Kramer
Sent: Thursday, January 08, 2009 8:19 AM
To: emc-p...@ieee.org
Subject: RE: Sanity check on AC motors for boat use

Good point, however these will be on recreational craft in most cases.  I'm 
told US, Canada, Australia and then EU are the markets.
-Doug


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of 
john.merr...@us.schneider-electric.com
Sent: Thursday, January 08, 2009 10:16 AM
To: Doug Kramer
Cc: emc-p...@ieee.org
Subject: Re: Sanity check on AC motors for boat use

Depends upon what is meant by a Boat

A Recreational Vessel or a Commercial Vessel?

I would think the later needs to conform to requirements of the International 
Association of
Class Societies E10 standard. Or more particularly perhaps to the standards of 
the actual Class
Society (Lloyds Register, American Bureau of Shipping, etc.) who is approving 
the design and
construction of the vessel.

YMMV

John Merrill
Square D Automation








  Doug Kramer 

  dkramer@nceelabsTo:   emc-p...@ieee.org

  .comcc:  

  Sent by: Subject:  Sanity check on AC 
motors for boat use 
  emc-p...@ieee.org 





  01/08/2009 10:48  

  AM







In reviewing standards as applicable to DC powered (battery) motors for use on 
boats, as I’m
seeing it that applicable EMC directive standards to apply would be EN55012 and 
EN55014-2.
EN55014-1 excludes devices used exclusively in vehicles.  Another route to go 
would be in
looking at EN61000-6 series for immunity.  I think the emissions requirement is 
very straight
forward.  A long I/O or control line in addition to the DC power cables causes 
a pause for
thought, but is easily tested and addressed in EN55014-2.

Thoughts?

Thanks,

Doug Kramer
Lab Manager
NCEE Labs
Product Compliance Solutions
Phone: 402.472.5880
Toll Free: 1.888.567.6860
Fax: 402.472.5881
Email: dkra...@nceelabs.com
www.nceelabs.com

CONFIDENTIALITY NOTICE:  This e-mail message, including any attachments, is for 
the sole use of
the intended recipient(s) and may contain confidential and privileged 
information.  Any
unauthorized review, use, disclosure or distribution is prohibited.  If you are 
not the
intended recipient, please contact the sender by reply e-mail and destroy all 
copies of the
original message.

P Please consider the environment before printing this e-mail.





This email has been scanned for SPAM content and Viruses by the MessageL
abs Email Security System.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To
post a message

RE: IEC 60950-1 section 4.7.3.2 regarding openings in fire enclosures

2009-01-08 Thread Jim Eichner
If an opening fully complies with 4.6.1 or 4.6.2 then it doesn't need to be 
filled with anything, and there's no reason for a V-1 requirement.

I believe the '950 authors meant to address openings that would not comply with 
4.6.1 or 4.6.2 if the component involved was not installed in the hole.  Since 
they say components and have the note NOTE Examples of these components are 
fuseholders, switches, pilot lights, connectors and appliance inlets, I guess 
they figured that they didn't need to put any size limits in.  However what if 
the component in question is a 4 diameter panel-mounted instrument?  Or a 
blanking plate covering an unused 2 knockout.  Or...

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.



From: Bolintineanu, Constantin [mailto:cbolintine...@tycoint.com] 
Sent: Thursday, January 08, 2009 6:01 AM
To: Jim Eichner
Subject: RE: IEC 60950-1 section 4.7.3.2 regarding openings in fire enclosures

Hi Jim,

Your question is a very USEFUL one, I did not know who may clarify it?!?

In my engineering judgement the decision shall be considered in conjunction 
with the Clause 4.6. Openings in enclosures;

My personal interpretation was (and still is until somebody else will provide a 
rationale OR as you specified a CTL decision will be available - I did not find 
anything related to it-but it does not mean that there is nothing...), that 
they are talking about the OPENINGS that fully meet 4.6.1 and /or 
4.6.2ONLY; 

OTHER OPENINGS are (as per 4.6 not allowed EXCEPT if Method 2 of 4.7.1 is used 
and complies with it) exempted and can not filled with anything worst than 
5VB (e.g.: stationary equipment)...

Respectfully yours,
Constantin

Constantin Bolintineanu P.Eng.
TYCO SAFETY PRODUCTS CANADA
3301 LANGSTAFF Road, L4K 4L2
CONCORD, ONTARIO, CANADA
e-mail: cbolintine...@tycoint.com
Tel: 905 760 3000 ext 2568
Fax: 905 760 3020


Before printing this e-mail think if it is necessary



DISCLAIMER: This e-mail message may contain privileged or confidential 
information. If you are not the intended recipient, you may not disclose, use, 
disseminate, distribute, copy or rely upon this message or attachment in any 
way. If you received this e-mail message in error, please return the message 
and its attachments to the sender, and then please delete from your system 
without copying or forwarding it or call TSPC at 905 760 3000 extension 2568 so 
that the sender's address records can be corrected.

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Jim Eichner
Sent: Wednesday, January 07, 2009 3:08 PM
To: emc-p...@ieee.org
Subject: IEC 60950-1 section 4.7.3.2 regarding openings in fire enclosures

IEC 60950-1 section 4.7.3.2 contains the following paragraph:

Materials for components that fill an opening in a FIRE ENCLOSURE, and that are 
intended to be mounted in this opening shall:
− be of V-1 CLASS MATERIAL; or
− pass the tests of Clause A.2; or
− comply with the flammability requirements of the relevant IEC component 
standard.

Seems ok to require most of the fire enclosure to be 5V with small sections of 
V1 allowed, but the above has no size restriction, which seems odd to me.  Does 
anyone know if this is the subject of a CTL decision or any other 
“official” interpretation?  

I’ve seen UL and CSA standards with similar easements but there’s a 
dimensional cap (for example openings no more than 1” (25.4mm) in any 
dimension).

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules

IEC 60950-1 section 4.7.3.2 regarding openings in fire enclosures

2009-01-07 Thread Jim Eichner
IEC 60950-1 section 4.7.3.2 contains the following paragraph:

Materials for components that fill an opening in a FIRE ENCLOSURE, and that are 
intended to be
mounted in this opening shall:
− be of V-1 CLASS MATERIAL; or
− pass the tests of Clause A.2; or
− comply with the flammability requirements of the relevant IEC component 
standard.

Seems ok to require most of the fire enclosure to be 5V with small sections of 
V1 allowed, but the above has no size restriction, which seems odd to me.  Does 
anyone know if this is the subject of a CTL decision or any other 
“official” interpretation?  

I’ve seen UL and CSA standards with similar easements but there’s a 
dimensional cap (for example openings no more than 1” (25.4mm) in any 
dimension).

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com




RE: Common-mode emissions from SMPS

2008-12-10 Thread Jim Eichner
SMPS without PFC front ends can cause high common-mode and differential
mode conducted emissions, and significant radiated emissions due to
common-mode cable currents.  PFC is not a necessary element to this
problem, although it does introduce additional challenges.  The basic
mechanism that was described - dV/dt coupling into parasitic (and/or
intentional) capacitances - is valid, but so is it's corollary - dI/dt
coupling into loops.  This dI/dt is often left out of SMPS EMI
discussions, but I've seen it be the more predominant source and a hard
one to mitigate, especially where the source is not the grid but a low
voltage DC source from which you demand and hard-switch high currents
(ie high dI/dt).

Another piece of the SMPS EMI puzzle that I focus on is the rather nice
radiated emissions generator set up when you take a device switching in
the 10's or 100's of kHz and put a set of cables on each end of it =
dipole antenna with an RF source in the middle.  

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Fred
Townsend
Sent: Wednesday, December 10, 2008 3:20 PM
To: John Woodgate
Cc: emc-p...@ieee.org
Subject: Re: Common-mode emissions from SMPS

First you seem to condemn all SMPS to common mode emissions. Far from 
true. Most switching power supplies (at least the smaller ones) rectify 
the line and then use higher frequency DC to DC converters. It saves 
iron and with modern fast components you don't lose much in efficiency 
due to using higher frequencies (20 to 500KHz). The converter 
frequencies don't propagate much because they have to go through the big

rectifier filer first.

The problem occurs when we add power factor correction (PFC). Instead of

straight rectification the AC current is taken out of the line in 
chunks. This produces lots of harmonics. Symmetry tends to cancel out 
the even harmonics but the odd ones propagate, particularly along the 
neutral in three phase systems. Since 3 phase neutrals are not expected 
to carry much current they are sometimes built smaller than the line 
circuits. It's all the perfect formula for emissions. Lack of symmetry 
and the UNCOMMON mode means they are very hard to filter.

So it's not the SMPS and it's not common mode, it's the PFC. No good 
deed goes unpunished.

Fred Townsend
DC to Light



John Woodgate wrote:

 SMPS seem to be very good at producing common-mode emissions on all 
 the cables attached to them and the products they power. Would someone

 please give me a simple explanation of how these common-mode emissions

 are generated?

 I don't get involved with the internals of SMPS, and I've been given 
 some explanations that are both contradictory and, taken one at a 
 time, not terribly credible.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com




FW: When UL component recognition is not enough.

2008-12-10 Thread Jim Eichner
This is a subset of a bigger problem: the meaningless nature of the UR
mark.  Since UL allows itself to issue this mark with less than full
evaluation or testing to the standard, or with less than full
compliance, anybody using a UR part needs to take that approval with a
bucket (not a grain) of salt.  Then to further frustrate attempts by
component users do things right, UL does not publish the Conditions of
Acceptability, and you have to go to the part mfr to try to get them to
show the list with you.  

It's an appalling situation where an accredited certification body can
do less than a complete job, the mfr gets to use their mark anyway, and
the public is not given access to the information as to what areas are
lacking from the approval.  

Having said all that, in some cases nothing is lacking, it's simply a
properly and fully approved component.  I have no problem with that.

And yes, I realize we are free to walk away from any part mfr that won't
give us the Conditions of Acceptability.

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Kunde,
Brian
Sent: Wednesday, December 10, 2008 6:26 AM
To: ieee
Subject: RE: When UL component recognition is not enough.

The Company has the right to accept or not any component for any
reason even though in this case the reason they give seems unreasonable.
I expect there are other reasons they do not want to use this component
and they are just using this as the excuse.

If the Company is trying to get NRTL approval on their product and their
non-UL NRTL has a problem with this component, then their NRTL needs to
contact UL and get things straitened out.  I have seen competing NRTLs
nit-pick over such things in the past and I think it shows a lack of
professionalism.  If they do not get resolve, I would contact OSHA and
complain. 

The Components Manufacturer will have to decide if they are willing to
lose such business over something so small. I think it would be a very
simple paperwork process to re-list and document their components under
the new standard with UL.  In most cases, UL would not require
additional evaluation or testing. The two standards are very similar. 

The Other Brian

 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Robert
Johnson
Sent: Tuesday, December 09, 2008 4:20 PM
To: ieee
Subject: When UL component recognition is not enough.

I have a complaint about a certification process where agencies are 
providing approvals of little value. There are products for sale which 
have been reviewed (for example) to UL 1950, and are currently being 
manufactured and UL recognized. UL 1950 is a withdrawn standard, 
replaced by UL 60950. I have no problem with that since UL has conducted

an IEC Sector Review Process which assures the product has no safety 
shortcomings with regard to the current standards. For standard changes 
affecting safety, a requirement effective date - RED is established and 
applied to the product.

However a company wishing to use this product has a problem with the 
component recognition since it is to a withdrawn standard as is stated 
in the Certification Directory. The company using the component must 
either have the component manufacturer resubmit, or have the component 
reassessed as part of the end product evaluation.

The result is, the component recognition is of no value to the new 
customer even though UL has gone through the work of assuring the 
component has no shortcomings with regard to the current standard. 
Apparently UL is reserving the step of updating the paperwork as an 
income source.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

LECO Corporation Notice:  This communication may contain confidential
information intended for the named recipient(s) only. If you received
this by mistake, please destroy

RE: EMI Receiver

2008-12-02 Thread Jim Eichner
Indeed, however while I too may be losing the will to live, I still have
the will to search out a new spectrum analyzer (note I learn from my
experiences and have dropped the term-that-shall-remain-unspoken from
this posting).

So dare I repeat my question and that of Tim's original posting:  does
anyone care to sing the praises of any particular make/model for
pre-compliance radiated and conducted emissions testing?

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Julian
Jones
Sent: Monday, December 01, 2008 8:49 AM
To: Untitled
Subject: RE: EMI Receiver

Can we please drop this topic now..I am beginning to lose
the will to live. 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Price,
Edward
Sent: 01 December 2008 16:53
To: Untitled
Subject: RE: EMI Receiver

 -Original Message-
 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ken 
 Javor
 Sent: Monday, December 01, 2008 8:47 AM
 To: Untitled
 Subject: Re: EMI Receiver
 
 This may be one of those usage differences that occur on opposite 
 sides of the Pond. After all, what we in the USA call a billion, you 
 call a milliard, and what you mean by a billion is what we call one 
 trillion.
  
 Ken Javor



So USA 2 billion is a UK billiard?


Ed Price
ed.pr...@cubic.com WB6WSN
NARTE Certified EMC Engineer  Technician Electromagnetic Compatibility
Lab Cubic Defense Applications San Diego, CA  USA 858-505-2780 (Voice)
858-505-1583 (FAX)
Military  Avionics EMC Is Our Specialty

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com




RE: EMI Receiver

2008-12-02 Thread Jim Eichner
As we often test immature prototypes with high emissions, I am quite
concerned about out-of-band emissions-related effects, and consider a
real preselector to be a mandatory part of any system we switch over
to.  The manufacturers may be able to tell me that they solve the same
problem a different way, but I know what my starting position is.  In
fact we currently use 3 protective elements:  a 100kHz high-pass filter,
a transient limiter, and a pre-selector (moving from the EUT end of the
chain towards the SA) and have found we need all three.  Amazing the
spectrum you get when a really large 50kHz switching fundamental slams
into the transient limiter.

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: John McAuley [mailto:john.mcau...@cei.ie] 
Sent: Tuesday, December 02, 2008 9:46 AM
To: Jim Eichner; emc-p...@ieee.org
Subject: RE: EMI Receiver

I notice Rohde and Schwarz have a new low cost ESL receiver. Unlike
previous pre compliance receivers it appears to be compliant to CISPR
16
even for the 1 Hz QP prf. However, it has no pre selection. I note the
recent comments about modern receivers having less sophisticated pre
selection. This one has none. Probably uses clever digital filters to
perform bandwidth, QP and Average functions based on a basic spectrum
analyzer front end. 

I presume that this instrument can be used for full compliance testing,
however, one needs to be very careful about the accuracy of the
measurement.
By careful use of input attenuation and observing the results, a
traditional
skill used by users of spectrum analysers may help?

BR

John McAuley



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Jim
Eichner
Sent: 02 December 2008 08:03
To: emc-p...@ieee.org
Subject: RE: EMI Receiver

Indeed, however while I too may be losing the will to live, I still have
the will to search out a new spectrum analyzer (note I learn from my
experiences and have dropped the term-that-shall-remain-unspoken from
this posting).

So dare I repeat my question and that of Tim's original posting:  does
anyone care to sing the praises of any particular make/model for
pre-compliance radiated and conducted emissions testing?

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Julian
Jones
Sent: Monday, December 01, 2008 8:49 AM
To: Untitled
Subject: RE: EMI Receiver

Can we please drop this topic now..I am beginning to lose
the will to live. 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Price,
Edward
Sent: 01 December 2008 16:53
To: Untitled
Subject: RE: EMI Receiver

 -Original Message-
 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ken 
 Javor
 Sent: Monday, December 01, 2008 8:47 AM
 To: Untitled
 Subject: Re: EMI Receiver
 
 This may be one of those usage differences that occur on opposite 
 sides of the Pond. After all, what we in the USA call a billion, you 
 call a milliard, and what you mean by a billion is what we call one 
 trillion.
  
 Ken Javor



So USA 2 billion is a UK billiard?


Ed Price
ed.pr...@cubic.com WB6WSN
NARTE Certified EMC Engineer  Technician Electromagnetic Compatibility
Lab Cubic Defense Applications San Diego, CA  USA 858-505-2780 (Voice)
858-505-1583 (FAX)
Military  Avionics EMC Is Our Specialty

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from

RE: EMI Receivers

2008-11-28 Thread Jim Eichner
Many posts have addressed the calibration part of this question, but not the
make and model part.  We have an aging HP rack that we are considering
relegating to spare status by purchasing a new or nearly new spectrum analyzer
or EMC receiver (I think the line there is blurring a bit these days but we
want/need a preselector if that affects the semantics at all).  I don’t
think we need 18GHz for our applications, so if you have a favourite that tops
out at a lower frequency please include it.  I don’t want to hijack Tim’s
originally 18GHz enquiry though.

 

Thanks, 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of emcp...@aol.com
Sent: Thursday, November 20, 2008 11:39 AM
To: emc-p...@ieee.org
Subject: EMI Receivers

 

Hello,

 

I'm looking to purchase an EMI receiver for use in a 5 meter chamber. Does
anyone recommend a certain model? I would want one that has at least a
frequency range from 150kHz to 18GHz so one unit can be used for radiated and
conducted emission measurements.

 

I'm looking for a unit that can be calibrated by a local accredited
calibration lab. I believe all RS receivers need to be sent to them for
calibration, which there would be risk and time involved in shipping.

 

Thanks,

Tim Pierce







One site has it all. Your email accounts, your social networks, and the things
you love. Try the new AOL.com http://p
.atwola.com/promoclk/10075x12129629
9x1200825291/aol?redir=http://www.aol.c
m/?optin=new-dp%26icid=aolcom40vanity%26ncid=emlcntaolcom0001  today!

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




RE: What's the deal with Wire Nuts?

2008-11-20 Thread Jim Eichner
Flexible cord is not to be used where a permanent wiring system is required,
except under certain exceptions.  The concern is that flexible cord is not as
robust as wiring in conduit or wiring in walls, and over the long-term
exposure that permanent installation implies, a flexible cord could become
damaged and hazardous.

 

Canada: CEC part 1 2006 rule 4-010

 

US: NEC 2008 rule 400.7

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Haynes, Tim
(SELEX GALILEO, UK)
Sent: Thursday, November 20, 2008 1:03 AM
To: Don Gies; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

 

Don, Hi.

 

In your response to Brian you said...

 

  However, written into the body of the IEC 60950-1 and EN 60950-1 (and other
national derivative standards) is a wiring method for permanent connection to
the mains not acceptable in the US and Canada – the use of a non-detachable
power supply cord for permanent connection. 

 

Can you please supply to me the reference that prohibits that wiring method in
US and Canada? 

 

Regards

Tim

 



Tim Haynes A1N10

Electromagnetic Engineering Specialist

SELEX Sensors and Airborne Systems 

300 Capability Green

Luton LU1 3PG

( Tel  : +44 (0)1582 886239

7 Fax : +44 (0)1582 795863 

) Mob: +44 (0)7703 559 310 

* E-mail : tim.hay...@selexgalileo.com

P Please consider the environment before printing this email. 

 

There are 10 types of people in the world-those who understand binary and
those who don't. J. Paxman

 

SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England  Wales. Company no. 02426132

This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




RE: Functional Safety and the LVD

2008-10-28 Thread Jim Eichner
What if the safety function of the product was related to electrical safety? 
Again I’ll go to my RCD example.  Suppose you have a product that contains
multiple subsystems, one of which is an RCD circuit that keeps the overall
product/system safe under fault conditions.  Is that RCD not providing a
safety function and could it not be considered a requirement to evaluate it to
61508?  Certainly UL has gone this route in their interpretation of the
applicability of UL1998 and UL991, which makes me question how certain we can
be that 61508 won’t start to be used for these sorts of product evaluations
too.

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Amund Westin
Sent: Monday, October 27, 2008 9:07 AM
To: emc-p...@ieee.org
Subject: RE: Functional Safety and the LVD

 

If a standard shall be listed under LVD, it must be electrical safety related.
I can’t  see that 61508 should be LVD listed, since it deals with HW / SW
functional safety. 

So you can sell a functional safety related product, CE mark it and not make
any references to LVD. An example is a flame detector driven by 24VDC. But as
an end user in offshore / marine market, it would have been a requirement that
the flame detector was tested and verified according to 61508.

 

Regards

Amund Westin

Oslo, Norway

 

Fra: emc-p...@ieee.org [mailto:emc-p...@ieee.org] På vegne av Jim Eichner
Sendt: 27. oktober 2008 16:14
Til: emc-p...@ieee.org
Emne: RE: Functional Safety and the LVD

 

Those systems are covered, but there’s nothing that excludes products. Take
for example an RCD device.  Clearly its function is safety-related.  Why
wouldn’t the 61508 series be relevant?

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/  


Any opinions expressed are those of my invisible friend. 


Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

 

 

 

From: David Clement [mailto:david.clem...@verizon.net] 
Sent: Saturday, October 25, 2008 2:12 PM
To: Jim Eichner; emc-p...@ieee.org
Subject: Re: Functional Safety and the LVD

 

61508 deals with electrical, electronic and program devices and systems that
provide safety such as rail road signaling, safety shut down systems in power
plants, machinery interlocks. It has several in depth sections on software
that is used in systems that provide functional safety. 

I don't see it being called out as part of a product safety directive.

 

Dave Clement

 

 


From: Jim Eichner jim.eich...@xantrex.com
To: emc-p...@ieee.org
Sent: Friday, October 24, 2008 1:44:53 PM
Subject: Functional Safety and the LVD

A search of the latest list of standards under the LVD does not turn up
any hits on EN61508, yet it would seem natural for this standard to be
considered relevant under the LVD.  I'm not looking for the added work
that would imply, but I do need to know if it's coming.

Any thoughts or inside knowledge if this is coming our way?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas  emcp...@ptcnh.net
Mike Cantwell  mcantw...@ieee.org

For policy questions, send mail to:

Jim

RE: Functional Safety and the LVD

2008-10-28 Thread Jim Eichner
Ok but does that mean it won’t ever get published under the LVD?  Maybe the
only answer is “never say never”.

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: David Clement [mailto:david.clem...@verizon.net] 
Sent: Monday, October 27, 2008 4:03 PM
To: Jim Eichner; emc-p...@ieee.org
Subject: Re: Functional Safety and the LVD

 

61508 is not a product standard. It relates to systems that provide System
Safety where a portion of the system is electrical, electronic, or
programmable. 

System Safety as a discipline looks at the severity of hazards that are
present if something fails to perform as designed, the likely hood of  it
occurring, assessing if the risk is acceptable and if its not take mitigation
steps to reduce the risk. 61508 provides special considerations when the
mitigation is provided by Electrical, Electronic or Programmable. For example;
It has guidance on the software development rigor necessary for the different
Safety Integrity Levels.

An RCD device provides a safety function for sure but a single device is
explicitly not covered. Below is an excerpt from the standard scope.

does not cover E/E/PE systems where
– a single E/E/PE system is capable of providing the necessary risk
reduction,

 

Dave Clement

 

 


From: Jim Eichner jim.eich...@xantrex.com
To: emc-p...@ieee.org
Sent: Monday, October 27, 2008 11:14:06 AM
Subject: RE: Functional Safety and the LVD

Those systems are covered, but there’s nothing that excludes products. Take
for example an RCD device.  Clearly its function is safety-related.  Why
wouldn’t the 61508 series be relevant?

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/  


Any opinions expressed are those of my invisible friend. 


Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

 

 

 

From: David Clement [mailto:david.clem...@verizon.net] 
Sent: Saturday, October 25, 2008 2:12 PM
To: Jim Eichner; emc-p...@ieee.org
Subject: Re: Functional Safety and the LVD

 

61508 deals with electrical, electronic and program devices and systems that
provide safety such as rail road signaling, safety shut down systems in power
plants, machinery interlocks. It has several in depth sections on software
that is used in systems that provide functional safety. 

I don't see it being called out as part of a product safety directive.

 

Dave Clement

 

 


From: Jim Eichner jim.eich...@xantrex.com
To: emc-p...@ieee.org
Sent: Friday, October 24, 2008 1:44:53 PM
Subject: Functional Safety and the LVD

A search of the latest list of standards under the LVD does not turn up
any hits on EN61508, yet it would seem natural for this standard to be
considered relevant under the LVD.  I'm not looking for the added work
that would imply, but I do need to know if it's coming.

Any thoughts or inside knowledge if this is coming our way?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas  emcp...@ptcnh.net
Mike Cantwell  mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher:j.bac...@ieee.org
David Heald:  dhe...@gmail.com

All emc-pstc postings are archived

RE: Functional Safety and the LVD

2008-10-27 Thread Jim Eichner
Those systems are covered, but there’s nothing that excludes products. Take
for example an RCD device.  Clearly its function is safety-related.  Why
wouldn’t the 61508 series be relevant?

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/  


Any opinions expressed are those of my invisible friend. 


Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

 

 

 

From: David Clement [mailto:david.clem...@verizon.net] 
Sent: Saturday, October 25, 2008 2:12 PM
To: Jim Eichner; emc-p...@ieee.org
Subject: Re: Functional Safety and the LVD

 

61508 deals with electrical, electronic and program devices and systems that
provide safety such as rail road signaling, safety shut down systems in power
plants, machinery interlocks. It has several in depth sections on software
that is used in systems that provide functional safety. 

I don't see it being called out as part of a product safety directive.

 

Dave Clement

 

 


From: Jim Eichner jim.eich...@xantrex.com
To: emc-p...@ieee.org
Sent: Friday, October 24, 2008 1:44:53 PM
Subject: Functional Safety and the LVD

A search of the latest list of standards under the LVD does not turn up
any hits on EN61508, yet it would seem natural for this standard to be
considered relevant under the LVD.  I'm not looking for the added work
that would imply, but I do need to know if it's coming.

Any thoughts or inside knowledge if this is coming our way?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas  emcp...@ptcnh.net
Mike Cantwell  mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher:j.bac...@ieee.org
David Heald:  dhe...@gmail.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 




Functional Safety and the LVD

2008-10-24 Thread Jim Eichner
A search of the latest list of standards under the LVD does not turn up
any hits on EN61508, yet it would seem natural for this standard to be
considered relevant under the LVD.  I'm not looking for the added work
that would imply, but I do need to know if it's coming.

Any thoughts or inside knowledge if this is coming our way?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:   dhe...@gmail.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





IEC60225-5 surge test impedance?

2008-10-07 Thread Jim Eichner
We are being asked to run this test and don't have the standard.  The voltage 
is 5kV and the energy is 0.5J but rather than do the calculus involved I 
thought I'd just ask for the specified source impedance.  

Thanks in advance


Jim Eichner
Sent from Blackberry Wireless

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





RE: IEC60225-5 surge test impedance?

2008-10-07 Thread Jim Eichner
Thanks Don.  Too bad our generator/CDN only has 2 or 12 ohms!

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: MacArthur, Don [mailto:don.macart...@gd-itronix.com] 
Sent: Tuesday, October 07, 2008 7:54 AM
To: Jim Eichner; emc-p...@ieee.org
Cc: Fred Kracke
Subject: RE: IEC60225-5 surge test impedance?

500 Ohms

 
Don MacArthur
Compliance Engineer
General Dynamics Itronix Corporation
12825 E. Mirabeau Parkway
Spokane Valley, WA 99216
ph: 509-742-1342
fax: 509-742-1672
 
email address:  don.macart...@gd-itronix.com
 
This email message is for the sole use of the intended recipients and
may contain GDC4S confidential or privileged information. Any
unauthorized review, use, disclosure or distribution is prohibited. If
you are not an intended recipient, please contact the sender by reply
email and destroy all copies of the original message.

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Jim
Eichner
Sent: Tuesday, October 07, 2008 7:41 AM
To: emc-p...@ieee.org
Cc: Fred Kracke; Jim Eichner
Subject: IEC60225-5 surge test impedance?

We are being asked to run this test and don't have the standard.  The
voltage is 5kV and the energy is 0.5J but rather than do the calculus
involved I thought I'd just ask for the specified source impedance.  

Thanks in advance


Jim Eichner
Sent from Blackberry Wireless

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





RE: EN 50178 scope

2008-09-05 Thread Jim Eichner
My understanding is that there will not be any more work on EN50178 /
IEC 62103 as TC22 has decided that it is not a very good standard and
other standards and standards development efforts have already moved
past it.  The intent of the scope was always vague, perhaps
intentionally so, but I can tell you it is in widespread use for motor
drives and solar inverters, and is likely being used for other power
conversion equipment without an obvious product standard, and for
non-power-conversion electronics equipment that is related to electrical
installations (for example current sensors).

For drives, EN 50178 / IEC 62103 has already been replaced by IEC
61800-5.

For solar inverters, EN 50178 / IEC 62103 will be replaced by IEC
62109-1 and -2 when they get published, assuming CENELEC adopts them and
they get published by reference in the OJ under the LVD, which is
certainly the intent of the IEC TC82 WG6 authors.  

For other power conversion products and other electronics currently
being done to EN 50178 / IEC 62103, there are other product standards
that can be used, but some products will naturally fit the scope of EN
50178 / IEC 62103 or will have no other home, so it will continue to be
used until it gets withdrawn.  In the long run, TC22 is developing IEC
62477 which will be a group safety standard for power conversion
equipment, and will have product standards published under it.  

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Thursday, September 04, 2008 11:48 AM
To: emc-p...@ieee.org
Subject: RE: EN 50178 scope

John,

Thanks much.

I note that there is no EN62103 on the Low Voltage Directive list
of harmonised standards, but that EN50178 is still listed.

Anyone care to comment if there will be a transition ?

luck,
Brian


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of
John
McAuley
Sent: Thursday, September 04, 2008 11:29 AM
To: 'Brian O'Connell'; emc-p...@ieee.org
Subject: RE: EN 50178 scope

Brian

It was transferred to IEC TC22 and published as IEC 62103. It is
available
for preview on the IEC website.

International Standard IEC 62103 has been prepared by IEC
technical
committee 22: Power electronic systems and equipment.

The text of this standard is based on the European Standard EN
50178,
prepared by the CENELEC Task Force BTTF 60-1: Assembly of
electronic equipment.

John McAuley

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





Compliance Position at Xantrex in Burnaby (Vancouver) BC

2008-08-21 Thread Jim Eichner
We are looking to hire a full-time compliance engineer for our Burnaby
BC (Canada) product development operation.  We develop a wide variety of
power conversion products for renewable energy, mobile power, and
consumer electronics applications, ranging from 10W to 10kW.  The
position deals with product safety, utility interconnection, EMC, and
environmental compliance, with significant product safety compliance
experience a mandatory pre-requisite. 

The full job description is under my signoff below and on our website,
where you can also apply. 

http://www.xantrex.com/corporate/careers/index.asp  

Thanks, 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

Title:  Compliance Engineer (Burnaby) 

Xantrex Technology Inc. is a world leader in advanced power electronics
headquartered near Vancouver, Canada. We are a fast-paced, dynamic,
cross-functional team-based company. Xantrex makes a positive difference
in the lives of people around the world by combining proven technology
with unparalleled market understanding to bring our customers products
that enable the delivery of electricity anytime, anywhere.

Position Summary:

Responsible for ensuring and maintaining product compliance with
worldwide regulatory requirements for product safety, Electromagnetic
Compatibility (EMC), hazardous substance restrictions, utility
interconnection, etc. for power conversion products and accessories in
Xantrex's renewable energy, mobile power, and portable power markets.
Works with design teams to provide guidance, evaluate and improve
designs, and test for compliance. Works with regulatory agencies and
standards to obtain and maintain certifications. 

Responsibilities:

Plan and manage all compliance tasks for assigned programs

Perform product safety, EMC, and utility interconnection testing and
produce formal test reports for agencies and internal and external
customers

Evaluate product designs to ensure and document compliance in the final
design: 

 o Provide interpretations of requirements to design teams 

 o Provide ongoing feedback and data to design teams

Write and maintain the reports required to document regulatory
compliance

Work with agencies and 3rd party test laboratories for the purposes of: 

o Obtaining testing and evaluation services 

o Obtaining and maintaining product approvals 

o Obtaining interpretations of requirements

Perform as a cross-functional team member to achieve the technical,
schedule and budget objectives of development programs

Stay current with applicable standards, skills, and trends in regulatory
compliance

Participate in standards development committees relevant to Xantrex
products
 
Requirements: 

Electrical Engineering degree preferred, will consider technologist with
appropriate experience

At least 5 years experience in product safety compliance testing and
evaluation, preferably in the power electronics industry

Extensive knowledge of worldwide product safety regulations, standards,
and test methods

Preference given to candidates with one or more of the following:
experience with EMC regulations, standards, and testing; working
knowledge of power conversion technology (motor drives, inverters, power
supplies); experience in renewable energy systems; experience in marine
or RV electrical systems;

Enjoys hands-on work - testing, troubleshooting, prototyping, etc.

Detail oriented and thorough

Ability to read schematics and specifications, perform circuit analysis

Strong written and oral communication skills, with emphasis on the
ability to create quality technical reports, test reports, and test
procedures

Ability to work effectively with multi-disciplined design teams

Strong organizational and time-management skills

Ability to multi-task and to adapt to changing priorities

Proficiency in MS Office (Excel, Powerpoint, Word  the internet)

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc

RE: UL 2054 testing for lithium batteries

2008-07-07 Thread Jim Eichner
Does anybody have any insight into the changes that those standards are
going to make in light of the incidents and recalls?  If we can't rely
on UL2054's requirements, and want to apply additional testing or
requirements to UL2054 battery packs, then it would be helpful to know
where that standard is headed. 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Scott Xe
Sent: Monday, July 07, 2008 7:30 AM
To: kazimier_gawrzy...@dell.com; rpick...@rpqconsulting.com;
oconne...@tamuracorp.com; emc-p...@ieee.org
Subject: RE: UL 2054 testing for lithium batteries

Richard,

If you want to prevent the battery pack from explosion/fire, compliance
of
those standards might not accomplish it for the time being.  UL 2054, UL
1642 and UL 60950-1 were prepared and published before Sony's battery
recall.  All the standards are being revised to address the issue.
After a
large scale of Sony's battery recall, the Li-ion battery pack continues
to
explode and catch fire in a smaller scale.  The users are awaiting the
new
replacement of battery pack or a firm solution to the probable explosion
of
existing Li-ion battery pack.

Regards.

Scott


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
kazimier_gawrzy...@dell.com
Sent: Thursday, July 03, 2008 12:24 AM
To: rpick...@rpqconsulting.com; oconne...@tamuracorp.com;
emc-p...@ieee.org
Subject: RE: UL 2054 testing for lithium batteries

Also.For end use systems seeking compliance with UL 60950-1, see
Annex P.1 with reference to cl. 4.3.8

Kaz
kazimier_gawrzy...@dell.com



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ron
Pickard, RPQ
Sent: Wednesday, July 02, 2008 11:07 AM
To: 'Brian O'Connell'; 'emc-p...@ieee.org'
Subject: RE: UL 2054 testing for lithium batteries

Richard,

 

IMHO, if the lithium batteries are user replaceable (such as a removable
battery pack), then they would need to be separately approved to UL
2054. I
say that because in my experience, UL has required it in past Listing
efforts of products with them. And, if this is a cell phone application,
please note that the CTIA has recently imposed requirements for lithium
batteries.

Supporting this, from UL2054's scope:

 

- These requirements cover portable primary (nonrechargeable) and
secondary
(rechargeable) batteries for use as power sources in products. These
batteries consist of either a single electrochemical cell or two or more
cells connected in series, parallel, or both, that convert chemical
energy
into electrical energy by chemical reaction.

- These requirements are intended to reduce the risk of fire or
explosion
when batteries are used in a product. The proper use of these batteries
in a
particular application is dependent on their use in a complete product
that
complies with the requirements applicable to such a product.

- These requirements are intended to cover batteries for general use and
do
not include the combination of the battery and the host product which
are
covered by requirements in the host product

standard.

- These requirements are also intended to reduce the risk of injury to
persons due to fire or explosion when batteries are removed from a
product
to be transported, stored, or discarded.

- These requirements do not cover the toxicity risk that results from
the
ingestion of a battery or its contents, nor the risk of injury to
persons
that occurs if a battery is cut open to provide access to its contents.

 

The battery manufacturer would quite likely be already aware of all of
this.
They would be the one to approach for getting this work done.

 

Also, in addition to what Brian stated about shipping, the US and
international shipping authorities have specific testing and labeling
requirements for lithium batteries or products containing lithium
batteries.
Testing involves the UN T1-T8 tests.

 

IHTH.

 

Best regards,

 

Ron Pickard

RPQ Consulting

7372 West Luke Avenue

Glendale, AZ 85303

+623.512-3451 tel, +623.848-9033 fax

rpick...@rpqconsulting.com

www.rpqconsulting.com http://www.rpqconsulting.com/ 

 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Wednesday, July 02, 2008 7:21 AM
To: 'emc-p...@ieee.org'
Subject: RE: UL 2054 testing for lithium batteries

 

The following are personal opinions only.

 

In general, conformity to the applicable standard is always

necessary; but not always 'required'. In any case, note that UL

1642 is scoped specifically for Li

RE: FW: 60950-1:2006 clause 2.5 - Limited power sources

2008-06-23 Thread Jim Eichner
That's my feeling - it's an illogical exclusion.  At most the standard
should disallow the use of any (ie technology neutral) device that has
not been tested to a relevant standard that takes cycle life into
account, but to pick on auto-reset electromechanical devices while
allowing auto-reset solid state devices seems very odd, especially since
the latter are more likely to be damaged by surges and the like.

Any '950 authors lurking who haven't commented yet?

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John
Woodgate
Sent: Friday, June 20, 2008 5:15 AM
To: emc-p...@ieee.org
Subject: Re: FW: 60950-1:2006 clause 2.5 - Limited power sources

In message 
de87437fe365cb458c265ea3d73b6f1d039ad...@xbc-mail1.xantrex.com, dated 
Fri, 20 Jun 2008, Jim Eichner jim.eich...@xantrex.com writes:


To be clear, the LPS application would not be a circuit breaker as 
the term is commonly used.  The language from '950 that I objected to 
was regarding automatically resetting overcurrent protective devices, 
so rather than a circuit breaker it would be something like a thermal 
auto-reset device that I would call a current limiter or a circuit 
protector not a breaker.  Semantics to some extent, but auto-reset was

the main attribute for this discussion.

Well, if it's not a circuit-breaker (electromechanical, and therefore 
reliability is an issue), it makes even less sense to allow PTCs. I 
suspect that the ban on auto-reset was lifted for PTCs because if not it

would be an absolute ban on their use. But it's not logical.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Either we are causing global warming, in which case we may be able to
stop it,
or natural variation is causing it, and we probably can't stop it. You
choose!
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





Compliance position at Xantrex in Livermore, CA

2008-06-23 Thread Jim Eichner
We are looking to hire a full-time compliance engineer for our Livermore
operation, which focuses on 3-phase solar and wind power products from
30kW into the low megawatts.  The position deals mostly with product
safety and utility interconnection compliance, with any EMC or other
product regulatory knowledge being an asset but not essential.  The job
description is under my signoff below.  If you are interested please
apply through our website at
http://www.xantrex.com/corporate/careers/index.asp , but if you are
serious and have specific questions first, you can contact me directly,
off-line.

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



Job Description:

Xantrex Technology Inc. is a world leader in advanced power electronics
headquartered near Vancouver, Canada. We are a fast-paced, dynamic,
cross-functional team-based company. Xantrex makes a positive difference
in the lives of people around the world by combining proven technology
with unparalleled market understanding to bring our customers products
that enable the delivery of electricity anytime, anywhere.

Position Summary:

Responsible for ensuring and maintaining product compliance with
regulatory requirements for product safety, utility interconnection and
Electromagnetic Compatibility (EMC) of solar and wind power conversion
products and accessories.  Work with design teams to provide guidance,
evaluate designs and test for compliance.  Work with regulatory agencies
and their standards to obtain and maintain certifications. 
   
Responsibilities:

* Plan and manage all compliance tasks for assigned programs
* Perform product safety, utility interconnection and EMC testing and
produce formal test reports for agencies, electric utilities and design
teams
* Evaluate product designs to ensure compliance in the final design:
* Provide interpretations of requirements to design teams
* Provide ongoing feedback and data to design teams
* Write and maintain the reports required to document regulatory
compliance
* Work with utilities, agencies and 3rd party test laboratories for the
purposes of:
 * Obtaining testing and evaluation services
 * Obtaining and maintaining product approvals
 * Obtaining interpretations of requirements
* Perform as a cross-functional team member to achieve the technical,
schedule and budget objectives of the program
* Stay current with applicable skills and trends in regulatory
compliance
* Participate in standard development committees relevant to Xantrex
products

Requirements:

* Electrical Engineering degree preferred, will consider technologist
with appropriate experience
* At least 5 years experience in product safety standards compliance,
preferably in the power electronics industry 
* Preference given to candidates with one or more of the following:
experience in solar or 
wind power, experience working with utilities and commissioning high
power systems, working knowledge of power conversion technology (motor
drives, inverters, power supplies) preferably at high power levels (10kW
- 2.5MW), experience in both low- and medium voltage (up to 20kV)
beneficial, experience with water-cooled systems
* Extensive knowledge of current worldwide regulations, standards, and
test methodology applicable to product safety, and ideally also utility
interconnection and EMC
* Hands-on skills - testing, troubleshooting, prototyping, etc.
* Detail oriented and thorough
* Ability to design and test compliance solutions, perform circuit
analysis 
* Strong written and oral communication skills, with emphasis on the
ability to create quality technical reports, test reports, and test
procedures
* Ability to work effectively with multi-disciplined design teams
* Strong organizational and time-management skills
* Ability to multi-task and to adapt to changing priorities
* Proficiency in MS Office (Excel, Powerpoint, Word  the internet)


**

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

FW: 60950-1:2006 clause 2.5 - Limited power sources

2008-06-20 Thread Jim Eichner
To be clear, the LPS application would not be a circuit breaker as the
term is commonly used.  The language from '950 that I objected to was
regarding automatically resetting overcurrent protective devices, so
rather than a circuit breaker it would be something like a thermal
auto-reset device that I would call a current limiter or a circuit
protector not a breaker.  Semantics to some extent, but auto-reset was
the main attribute for this discussion. 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
phone: (604) 422-2546
mobile: (604) 418-8472
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John
Woodgate
Sent: Thursday, June 19, 2008 12:25 PM
To: emc-p...@ieee.org
Subject: Re: 60950-1:2006 clause 2.5 - Limited power sources

In message 002201c8d233$ee8de1e0$d600a...@tamuracorp.com, dated Thu, 
19 Jun 2008, Brian O'Connell oconne...@tamuracorp.com writes:


As for 'reliability', can we assume that safety standards such as 
60730, 61058, 61015, 60384, etc address the issue of reliability 
through a min number of cycles, or am I making an invalid comparison of

apples to oranges ?

Well, they are all, as far as I know, based on experience rather than 
formal analysis, and consider 'known UNreliability' rather than 'tested 
reliability'. In other words, something is not allowed because 
experience has shown that it should not be allowed.

But when that was applied to circuit-breakers in LPS circuits, and what 
the evidence was, who knows? While 60950 is not a very old standard, it 
has ancestors. LPS is actually a concept from UL standards rather than 
European, which may give a clue.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Either we are causing global warming, in which case we may be able to
stop it,
or natural variation is causing it, and we probably can't stop it. You
choose!
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





RE: 60950-1:2006 clause 2.5 - Limited power sources

2008-06-19 Thread Jim Eichner
I don't understand why electromechanical devices cannot be proven to
have reliable cycle life.  There are electromechanical devices tested
for 6,000 cycles and 100,000 cycles commonly available, and there may be
other classes with even higher cycle life.  The standards all require
that holding the breaker handle/button down after it has tripped must
NOT allow the contacts to be held closed (so-called trip-free
operation).  The environmental and other stresses listed in your items
a) to g) all seem to me to be something that a thermal breaker designer
could design for.  

Take for example a simple bimetallic circuit protector.  I can't imagine
such a device having a problem with any of this, except perhaps if the
thermal expansion properties of either of the two metals changes too
much during the cycling required by the standard.  Is that the issue?

The reason for my enquiry is standards committee work.  We are importing
this Limited Power Sources section, and it doesn't seem right to not
allow auto-reset electro-mechanical devices.  At the very least, we
should allow them with a condition that they comply with a relevant
standard that tests them for adequate cycle life (perhaps one of the
60730 series, but I'm sure there are more relevant standards for
breakers and protectors that are electro-mechanical).

Comments?

Thanks as always for the forum's help.

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: Brian O'Connell [mailto:oconne...@tamuracorp.com] 
Sent: Tuesday, June 17, 2008 7:08 AM
To: Jim Eichner; emc-p...@ieee.org
Subject: RE: 60950-1:2006 clause 2.5 - Limited power sources

Ok, brain damaged after several long nights as a code monkey - did not
finish my answer.

as you know, the last choice is delimited by
Where an overcurrent protective device is used, it shall be a fuse or a
non-adjustable,
non-autoreset, electromechanical device.

Because electromechanical devices cannot meet the cycle (reliability)
requirments of IEC60730, they are not allowed. As breakers age, there
trip level and time-to trip may not always age gracefully. Also, there
is the risk that an operator may attempt to hold the breaker closed
during overload.

In any case, UL60730-1A states
DVD.4.1 A power limiting component - resistor, positive temperature
coefficient THERMISTOR, diode, or the like - employed to limit the
output of a power source to within the required current or power levels,
or otherwise relied upon to comply with the performance requirements in
Sub-clause DVD.6 shall have permanence and stability so as not to
decrease its limiting capabilities. Among the factors considered when
determining the acceptability of a power limiting component are:
a) Effect of operating temperature,
b) Electrical stress level,
c) Effect of transient surges,
d) Resistance to moisture,
e) Endurance,
f) Temperature change shock, and
g) If appropriate, thermal runaway.


R/S,
Brian 


From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Tuesday, June 17, 2008 6:50 AM
To: 'Jim Eichner'; 'emc-p...@ieee.org'
Subject: RE: 60950-1:2006 clause 2.5 - Limited power sources


Logic error - the requirements of cl 2.5 are connected by 'OR' logic.
Note that one of the choices is
b) a linear or non-linear impedance limits the output in compliance
with Table 2B. If a
positive temperature coefficient device is used, it shall pass the tests
specified in IEC60730-1, Clauses 15, 17, J.15 and J.17; or

Assuming that this is for a mains-isolated LPS output, we can say that
this is not related to overcurrent protection for branch circuits, and
will also assume that another overcurrent protective device is being
used to satisfy NEC 240.10.

If the above is true, then a PTC, that is certified as a current
interrupt where the end-use meets its conditions of acceptability,
should be acceptable if a short or overload meets the limits of table
2C.

I have used 'auto-resetting' PTCs to meet the requirements of both
UL60950-1 and UL1012, their use IS, in fact, allowed. But I have also
'encouraged' the designers to include other series impedances that will
also provide ultimate current limits not dependent on the PTC.

luck,
Brian 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Jim
Eichner
Sent: Tuesday, June 17, 2008 2:24 AM
To: emc-p...@ieee.org
Cc: Jim Eichner
Subject: 60950-1:2006 clause 2.5 - Limited power sources

If an overcurrent protective device is used, it is not allowed to be
auto-resetting.  Why?  Just above this requirement is an allowance to
use PTC's

60950-1:2006 clause 2.5 - Limited power sources

2008-06-17 Thread Jim Eichner
If an overcurrent protective device is used, it is not allowed to be
auto-resetting.  Why?  Just above this requirement is an allowance to
use PTC's and they auto-reset, so why the bias against auto-reset
breakers?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend.

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





RE: IEC/EN 60664-4 - Insulation Coordination for frequencies over 30kHz

2008-06-17 Thread Jim Eichner
If anyone has posted a reply to this without copying me, I may have
missed it, since I had vacation mode turned on to avoid sending Out of
Office messages to everyone.  I have now turned vacation mode off again,
but please re-send to me off-line if indeed you had replied without
copying my personal e-mail address.

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.


_
From: Jim Eichner 
Sent: Monday, June 16, 2008 5:48 AM
To: emc-p...@ieee.org
Cc: Jim Eichner
Subject: IEC/EN 60664-4 - Insulation Coordination for frequencies over
30kHz


Does anybody have any background on what drove the writing of 60664-4?
I am on TC22 PT5 writing a safety standard for power electronics, and we
are wondering if the -4 requirements were driven by real-life issues
(breakdown of clearances, tracking across creepage distances, etc.) with
application of existing (ie 60664-1 based) requirements on higher
frequency circuits?  Or did this standard get written out of a
theoretical basis, in the absence of real-life issues? 

If there is a track record of real-life issues, the follow-on question
is whether those issues manifest in the lower frequencies of the broad
range of 60664-4 (which goes from 30kHz to 10MHz), since power
electronics would typically use only the low end of that range, up to
perhaps 1MHz.

Thanks in advance,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who looks just
the same at 29kHz has he does at 31kHz. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





IEC/EN 60664-4 - Insulation Coordination for frequencies over 30kHz

2008-06-16 Thread Jim Eichner
Does anybody have any background on what drove the writing of 60664-4?
I am on TC22 PT5 writing a safety standard for power electronics, and we
are wondering if the -4 requirements were driven by real-life issues
(breakdown of clearances, tracking across creepage distances, etc.) with
application of existing (ie 60664-1 based) requirements on higher
frequency circuits?  Or did this standard get written out of a
theoretical basis, in the absence of real-life issues? 

If there is a track record of real-life issues, the follow-on question
is whether those issues manifest in the lower frequencies of the broad
range of 60664-4 (which goes from 30kHz to 10MHz), since power
electronics would typically use only the low end of that range, up to
perhaps 1MHz.

Thanks in advance,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who looks just
the same at 29kHz has he does at 31kHz. 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





FW: European Equivalent for: National Fire Code, National Electric Code, Uniform Building Code, and OSHA

2008-05-30 Thread Jim Eichner
So how do I buy what I need?  I guess I have to go to some webstore that sells
the IEC or EN version of the 60364 series, read the scope of each of the many
subsections, decide which ones I need, and buy them one at a time at a cost of
$100+ each?

 

I suppose that’s a rhetorical question.

 

Argh.

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/  


Any opinions expressed are those of my invisible friend, who sells
dictionaries one letter at a time - buy only what you need! 


Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

 

 

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Wednesday, May 21, 2008 5:19 AM
To: emc-p...@ieee.org
Subject: RE: European Equivalent for: National Fire Code, National Electric
Code, Uniform Building Code, and OSHA

 

I am unaware of a consolidated version of IEC 60364.  Any national adoption
will have national deviations which will likely not be marked.  

 

BS 7671 may be a place to start.  Much of it aligns closely with IEC 60364 and
there is even correspondence between the clause numbers.  However, without the
two side by side, you won't be able to tell where BS 7671 is different from
the IEC standard.

 

Ted Eckert

The opinions expressed are strictly my own and do not necessarily reflect
those of my employer.


Jim Eichner jim.eich...@xantrex.com wrote:

Has the EU, or any member states or standards bodies, published a
consolidated package yet, that would allow me to be buy all of IEC 60364
at once?

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.


-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Tuesday, May 20, 2008 8:25 AM
To: emc-p...@ieee.org
Subject: RE: European Equivalent for: National Fire Code, National
Electric Code, Uniform Building Code, and OSHA

BS7671
IEC60364

of course, my favorite fire-code directive is provide by the
'Talking Heads'

luck,
Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of
Christine Rodham
Sent: Tuesday, May 20, 2008 8:06 AM
To: emc-p...@ieee.org
Subject: Re: European Equivalent for: National Fire Code,
National Electric Code, Uniform Building Code, and OSHA


Dear List Members,

Are there European equivalent codes/directives for the:

National Fire Code:

National Electric Code:

Uniform Building Code:

OSHA:


Thank you!

Christine Rodham

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions: http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc

RE: European Equivalent for: National Fire Code, National Electric Code, Uniform Building Code, and OSHA

2008-05-21 Thread Jim Eichner
Has the EU, or any member states or standards bodies, published a
consolidated package yet, that would allow me to be buy all of IEC 60364
at once?

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com  

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Tuesday, May 20, 2008 8:25 AM
To: emc-p...@ieee.org
Subject: RE: European Equivalent for: National Fire Code, National
Electric Code, Uniform Building Code, and OSHA

BS7671
IEC60364

of course, my favorite fire-code directive is provide by the
'Talking Heads'

luck,
Brian


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of
Christine Rodham
Sent: Tuesday, May 20, 2008 8:06 AM
To: emc-p...@ieee.org
Subject: Re: European Equivalent for: National Fire Code,
National Electric Code, Uniform Building Code, and OSHA


Dear List Members,

Are there European equivalent codes/directives for the:

 National Fire Code:

 National Electric Code:

 Uniform Building Code:

 OSHA:


Thank you!

Christine Rodham

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc





German regulation relating to equipment built into vans, trucks, etc.

2004-09-20 Thread Jim Eichner
We have had an enquiry whether or not our products comply with a German
regulation. Here's the information we were given...
Nutzfahrzeugeverordnungen = a law that regulates what you built into
vans, trucks and caravans

A Google search on the term came up empty, but the translation is
Commercial motor vehicle regulations.  Sounds like the FMVSS.  

Does anybody know what this is, and/or have any links to useful internet
sites on the topic?

Thanks,
Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend.
Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:

 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



EN62040-1-1 and wiring compartments

2003-10-07 Thread Jim Eichner

In revising and renumbering EN50091-1-1 to EN62040-1-1, a change seems to
have occurred that may not have been intentional.  If anyone can shed any
light on this I'd appreciate it!

EN50091-1-1:  Refers to EN60950:1992 +A1+A2 for most of its requirements.
In particular, for wiring compartments, EN50091-1-1 calls out EN60950
clauses 3.2.2 through 3.2.8, the last of which contains requirements for
wiring space for permanent connections (sufficient space to allow conductors
to be introduced, designed to permit inspection of wiring, etc.).

EN62040-1-1:  Refers to EN60950-1 (latest and greatest), in particular
clauses 3.2.2 through 3.2.8.  However in EN60950-1 there is a clause 3.2.9
(lines up with the old 3.2.8 discussed above) which is NOT called out as a
requirement by EN62040-1-1.  Is this intentional, or an error of omission?

Here's the real question:  Does an EN62040-1-1 product require a wiring
compartment at all?  With 3.2.9 omitted, there is nothing referenced that
requires a wiring space with a cover.  You could (why you would is a
different matter, but you could...) interpret the standard as allowing
wiring to come up to the product, be secured in a cable clamp (or conduit
secured in a knockout) and then the final connections made outside the main
enclosure.  As long as connector types met all the requirements for
prevention of access to live parts (etc) such a scheme would seem to be
acceptable.  Or 3.2.9 was meant to be included and was left out by mistake.
Thanks in advance for any light anyone can shed on this.
Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: fan question

2003-09-19 Thread Jim Eichner

Interesting story.  I wonder though if the result of the risk assessment
would have been It takes 2 faults for this to be hazardous, so probability
of occurrence is low, and we don't need to act on it.  Since most product
safety standards consider safety to be adequate with only single fault
scenarios applied, some may feel justified making the above assessment.  I'm
not sure I like the idea that what's good enough for a published and adopted
standard is not good enough for the courts.  It seems to me, if that's the
case, that the standards writing bodies had better raise the bar a notch.
If safety approvals are to add value beyond mere market access, ie liability
reduction, then they need to be considered adequate by the courts.

Of course the courts are always going to find someone to blame, regardless
of safety standards, fault assessments, warnings and instructions, etc.
There is no such thing as oh well, shxx happens in liability court.

Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No, really. 

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






From: Duncan Hobbs [mailto:duncan_ho...@xyratex.com]
Sent: Friday, September 19, 2003 1:43 AM
To: marko.radoji...@nokia.com; emc-p...@majordomo.ieee.org
Subject: RE: fan question



Marko and group,

There was an interesting liability case in the UK in the late
eighties involving a certain brand and model of washer/drier.

The situation was that the machine had an aluminum heater box with the
drying element and a fan to blow air over it. The heater box was
provided with an over-temperature trip as a safety feature.

The problem was that in some cases the over-temperature trip was
failing. The result of failure of this part was not apparent to the user
and the machine continued to apparently function normally with this
fault. This fault only became apparent when the absence of the safety
function provided by this device was highlighted by another fault (fan
failure). 

There were several fires reported (including one fatality) and the case
went to court where the manufacturer was found to be at fault. The
appliance had been approved by an approvals agency and met the required
standard.

I guess this illustrates the difference between compliance and safety.

Safety  = Freedom from unacceptable risk
Compliance  = Acting in accordance with a request or command

It was interesting to note that it was argued, that had an adequate risk
based assessment have been conducted on the appliance then such a hazard
would have been identified.

Regards,
Duncan.


Duncan Hobbs, Senior Compliance Engineer
Xyratex Product Compliance Lab.
Havant, Hants, U.K.
tel: 02392 496444
fax: 02392 496014
duncan_ho...@xyratex.com
 
 


From: marko.radoji...@nokia.com [mailto:marko.radoji...@nokia.com] 
Sent: 18 September 2003 15:53
To: peter.tar...@sanmina-sci.com; emc-p...@majordomo.ieee.org
Subject: RE: fan question


Back at a former employer, we were fond of saying that there was a
difference between Safe and Compliant. These scenarios are perfect
illustrations.

If there is a dormant fault in your equipment which could mask a safety
hazard, that is Compliant but not Safe. I personally would try and
reduce the exposure to a minimum using whatever means possible and then
document this situation to executive management for their express
approval.

Consider yourself on the witness stand with a lawyer asking you if you
were aware of the situation which caused their client to have come to
harm. What would you say? How would you feel?

Cheers,
Marko


From: ext Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: Thursday, September 18, 2003 6:39 AM
To: PSTC
Subject: RE: fan question



Amen.

The test house might attempt to invoke the forward to a
standard, if it contains text that provides them an out,
where there is clear engineering rationale and a very
specific risk of a hazard being evaluated not anticipated by
the standard.  Even so, the sand beneath their feet would be
shifting.

For instance (not a directly related one), during previous
test house employment, I stopped an evaluation and refused a
certification for a coffee percolator, because it barely
warmed water.

OTOH, if a double fault scenario seems plausible, you may
wish to perform the testing for your own edification,
irrespective of the content of the safety standard.  I might
be inclined to do such a thing on equipment intended for
installation in a hazardous location.  This is more a matter

RE: earthline choke

2003-09-11 Thread Jim Eichner

For emissions reduction, the usefulness of a ground-wire choke is dependent
on the relative magnitudes of the 2 types of common-mode noise your product
emits.  I refer to them as 2-wire and 3-wire common-mode noise:

2-wire:  Noise common to L and N, returning to the product on the G
3-wire:  Noise common to L, N, and G, returning to the product through other
parts of the system or the system's parasitic capacitance to ground

Of course there are more combinations in 3-phase systems.

It is easy with a clamp-on RF current probe to determine the types of noise
present on the conductors in a cable, by selecting which conductors go
through the probe, and in which direction.  For example:

- putting the L and N through and leaving out the G gives the 2-wire
common-mode noise
- putting all 3 conductors through gives the 3-wire common-mode noise
- putting the L through one way, and N the other way gives 2 x differential
mode noise (so take off 6dB)

By the way, you can apply the measurement idea to chokes:  a 2-wire
common-mode choke or a 3-wire common-mode choke are both helpful in some
circumstances.  Note that in a jacketed cable, where the L, N, and G are all
held tightly together and therefore have limited loop area between L/N and
G, a 3-wire common-mode choke is often more helpful than 2-wire.

Hope this is some help.

Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.





From: Morse, Earl (E.A.) [mailto:emo...@ford.com]
Sent: Thursday, September 11, 2003 7:06 AM
To: 'Muriel Bittencourt de Liz'; Ken Javor; Paolo Peruzzi;
emc-p...@majordomo.ieee.org
Subject: RE: earthline choke



In the computer world of switch mode power supplies this choke is usually
used as a means to control common mode radiation from the 1.5-2 meter line
cord in the 30-100 MHz range.  Typically consisting of a ferrite (850mu)
with several turns of the green/yellow safety ground through it.  If a real
inductor were used here then it would be required to meet a minimum
resistance to keep from being a safety issue.  

This configuration may have an effect on the higher frequencies in line
conducted measurements but most conducted emissions are controlled by the X
and Y caps along with the CM choke on the line and neutral in the AC input.

Earl


From: Muriel Bittencourt de Liz [mailto:mur...@eel.ufsc.br]
Sent: Thursday, September 11, 2003 8:41 AM
To: Ken Javor; Paolo Peruzzi; emc-p...@majordomo.ieee.org
Subject: Re: earthline choke



I have got some good results using a choke in the safety ground (or
protective earth-PE, as you wish) for reducing conducted emissions in
switched mode power supplies.

I also remember that I read somewhere (i think it was Clayton Paul's book)
that the use of this choke on safety wire is a problem for conformity with
the safety standards, so its use it is not recommended from this viewpoint.

I'd like to know if someone could give some additional details about using
this kind of solution for reducing conducted EMI, and if it is possible to
use it or not, depending on the safety standards. Another issue would be:
what is the effect of using this solution in terms of radiated emissions??
They are increased or not??

Thanks in advance, and best regards,

Muriel

- Original Message - 
From: Ken Javor ken.ja...@emccompliance.com
To: Paolo Peruzzi paolo.peru...@esaote.com;
emc-p...@majordomo.ieee.org
Sent: Thursday, September 11, 2003 9:11 AM
Subject: Re: earthline choke



A choke in the safety ground  could replace a common mode choke in the mains
lines, but only if the enclosure of the filtered device is isolated from
trolley structure completely, and the capacitance between equipment
enclosure and trolley structure is controlled to provide a higher impedance
than through the filtered safety ground wire (over the frequency range of
interest).

If there is a short and the ground wire performs its function the choke will
saturate and become ineffective but that is a moot point under short circuit
conditions.  During the time it takes the choke to saturate it will buck the
increase in current and keep the shorting potential on the equipment
enclosure; I expect this will be on the order of a millisecond or less and
shouldn't be a safety issue, but there are lots of product safety people on
the list who can weigh in on that subject more authoritatively than I do.


on 9/11/03 4:03 AM, Paolo Peruzzi at paolo.peru...@esaote.com wrote:






 Dear all,
 I'm

RE: Software and Safety

2003-08-22 Thread Jim Eichner

Seminars or short courses that people have taken and found useful would be
of interest too, please.

Thanks,
Jim Eichner, P.Eng.
Compliance Engineering Manager 
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really. 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.
 

 -Original Message-
From: peter merguerian [mailto:pmerguerian2...@yahoo.com]
Sent: Thursday, August 21, 2003 8:54 AM
To: emc-p...@majordomo.ieee.org
Subject: Software and Safety


Dear All,

Many of today's equipment utilizes software which is also relied for safety.
This is true in Machinery, NEBS, Alarm Systems, Medical Systems and CPU
cooling in many computers, etc.

I am interested in articles and links discussing software and safety in all
of the above and additional product categories. 


Peter


Do you Yahoo!?
Yahoo! SiteBuilder - Free, easy-to-use web site design software


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: e-mark labeling

2003-07-23 Thread Jim Eichner

There are no standards under the Automotive EMC Directive:  it contains its
own requirements.  All you should list is the Directive number itself.

Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.





From: Binnom, Cyril A [mailto:binno...@ems-t.com]
Sent: Wednesday, July 23, 2003 8:35 AM
To: emc-p...@majordomo.ieee.org
Subject: e-mark labeling 



Forum:

I have an aftermarket product that has been approved under 95/54/EC. For
specification literature purposes, (product or user's manual) I am not sure
what compliance standards should be listed for reference.

I do have a Type Approval # and a e-mark # required for the product.

An example would be 89/336/EEC. I currently list EN55022:1998 and
EN55024:1998 as the ITE product specific standards under the directive on
the DoC and any literature.

For 95/54/EC is there a standard that falls under the directive that I
should list. As I am not familiar with the directive, I am not sure. 

Regards,

Cyril A. Binnom Jr.
EMI/EMC Approvals Engineer
LXE, Inc.
(770) 447-4224 Ext. 3240
(770) 447-6928 Fax
binno...@lxe.com









This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN50091-1 question

2003-07-04 Thread Jim Eichner

The answer from EN50091-1-1 is...

Worst case voltage within the range specified by the manufacturer.  If a
range is not specified, it's +6%, -10%.  Note that this over-rules the '950
bit about increasing that range to +10% for 230Vac single-phase or 400Vac
3-phase.  This version of the UPS standard uses the old EN60950 +A1 +A2 as a
reference.

From EN62040-1-1, the answer is slightly different.  This version of the UPS
standard uses the new EN60950-1 as a reference, and accepts its requirements
of 1.4.1, 1.4.2, 1.4.3, 1.4.6, 1.4.7, 1.4.8, 1.4.10, 1.4.11, 1.4.12, 1.4.13,
and 1.4.14 as is (but not the missing subclauses) and then adds a note
saying only the heating and leakage tests are done with voltage tolerances,
all the rest being done at nominal voltage.

Hope this helps,

Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






From: Nick Williams [mailto:nick.willi...@conformance.co.uk]
Sent: Thursday, July 03, 2003 1:29 PM
To: emc-p...@majordomo.ieee.org
Subject: EN50091-1 question



I have a need to know a detail of the above standard more quickly 
than I can obtain a copy, if someone would be so good as to help me.

What is the voltage range (percentage of rated voltage) defined for 
heating and other tests in the above standard for normal and abnormal 
operation?

Any help in this regard appreciated.

Nick.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Jim Eichner

Ed - You were asking about output power quality standards for UPS, and while
I don't know the current correct answer (maybe someone from a UPS company
can help us), here are 3 standards that all cover UPS performance:

1. EN50091-3
2. IEC62040-3
3. IEC 146-4

I suspect all 3 are the same document in different stages of life, or at
least have the same basis.

Hope this helps,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: David Heald [mailto:hea...@symbol.com]
Sent: Monday, June 02, 2003 11:52 AM
To: ed.pr...@cubic.com; emc-p...@majordomo.ieee.org
Subject: Re: Surge Suppressors on a UPS



Most UPS's use a stepped approximation of a sine wave when in battery
mode.  While most switching supplies don't care (and are the intended
loads for these UPS's), surge suppressors can cause real issues - It has
something to do with capacitive overload of the output circuits.  

And for the second question - there are huge variances in the output
wave quality.  The brand I am familiar with has both stepped
approximation and true sine wave output models - the sine models being
the expensive ones.  The stepped approximation models are ideal for
switching supplies, while the sine output models can handle all kinds of
loads including motors (but a quick check says that they still can't use
surge supressors - this one has me puzzled!)

The UPS EMC standard is 50091-2 (or was it 92-1?), but I'm not sure how
much help it may offer.

Best Regards,
Dave Heald

 Price, Ed ed.pr...@cubic.com 06/02/03 11:18AM 
Hi Group!


Last Friday, I got ambushed in a meeting. I hate it when that happens!

A question was asked about whether it's OK to put a surge suppressor on
the
output of a UPS that is supplying power to some expensive equipment. I
opined that I didn't think it should be necessary, but that it also
shouldn't hurt anything either. So then somebody asks me why all the
UPS
manufacturer's sites say not to use a surge suppressor. I expertly
reply
that gosh, I don't know, but I'll take a look.

The next question nails me again. Are there any standards for UPS
output
power quality? Uh, well, I'll look into that too.

Now, the market is light industrial, USA, but are there any applicable
EN
standards also?

Just for some background, here's a typical entry from Tripp-Lite's FAQ
list
for UPS's (not to pick on Tripp-Lite; they just said it most succinctly
of
several sites I looked at):

http://www.tripplite.com/support/faq/tech_ups.cfm 
Can I plug a surge suppressor or extension cord into my UPS?
No. Using an extension cord will void your equipment coverage warranty,
as
all equipment must be plugged directly into the UPS. Tripp Lite does
not
recommend plugging a surge protector into a battery backup outlet of a
UPS
either as this can overload it. Also, when some UPS systems switch to
battery power they will output a waveform that a surge suppressor may
see as
a surge and short-circuit the UPS. Again, this setup will void the
equipment
coverage warranty.

Now this is getting to be a big can of worms! What do they mean by
some
UPS? Is there one kind that does, and another kind that doesn't; and
how do
you know which is which? And if some UPS will create a voltage
transient (is
that what they mean?) sufficient to trigger a surge suppressor, then
why is
it OK to let the UPS apply that transient to my protected equipment?
All
this talk about uninterrupted power isn't worth anything if the UPS
kills my
equipment when it switches to battery power mode.

And who's fault is this? I mean, a surge suppressor is pretty dumb; it
just
sits there waiting for the voltage to go over a certain level and then
it
conducts. What's this about the surge suppressor may see something as
a
surge? That's saying the surge suppressor could mis-interpret the
waveform
it sees. If the surge suppressor is conducting, then I think the UPS
has
just done something very naughty.

I also don't understand the prohibition of an extension cord. Maybe
this is
a legal issue, as I can't see any valid safety or regulation issues
here. We
regularly put a UPS in the bottom of a rack system, and then wire a
stripline outlet set for the height of the rack. Isn't that the
electrical
equivalent of an extension cord? What am I missing?

Thanks in advance!

Ed


Ed Price
ed.pr...@cubic.com 
NARTE Certified EMC Engineer  Technician
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our

RE: Altitude specifications

2003-05-22 Thread Jim Eichner

Thanks Rich and everyone else who has responded. I now have the basics I
need.

By the way my rule of thumb exists.  It turns out that IEC 76 and ANSIC
57.12  both let you go to 3300ft without applying correction factors.

Jim Eichner, P.Eng. 
Compliance Engineering Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.





From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Thursday, May 22, 2003 4:34 PM
To: jim.eich...@xantrex.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: Altitude specifications





Hi Jim:


   My understanding is that the main 2 effects of increased altitude on
   electronics are reduced  effectiveness of forced-air and convection
cooling
   methods and reduced dielectric strength of air-gaps (clearances).  

I concur.

   I believe the effects are linear with altitude, from sea level up,
however
   it occurred to me that there may be a simple rule of thumb along the
lines
   of up to approx.  feet, you can expect very little effect.  I
realize
   that rules of thumb like this need to be treated with scepticism (hence
my
   intent to test anyway), but I'm interested in peoples opinions and
   experiences.

The electric strength of air is a function of the air
pressure.  The more air you can pack between the two 
electrodes (the higher the pressure), the higher the 
electric strength.  

As you go up in altitude, you need to reduce the hi-pot
test voltage or risk a breakdown (if the distance is 
marginal at sea level).

Conversely, when you are at a low altitude, you can 
simulate a high altitude by increasing the hi-pot test 
voltage.

The breakdown of air as a function of pressure (altitude)
is nicely described in:

http://home.earthlink.net/~jimlux/hv/paschen.htm

From a more practical sense, here are the altitude 
correction factors for distance from IEC 664 (the factors 
are normalized for 2000 m altitude) for voltage breakdown:

ALTITUDE   PRESSURE  FACTOR
   m kPa (for distance)
     --
 0   101.30.79
   50095.00.84
  100090.00.89
  200080.01.00
  300070.01.14
  400062.01.29
  500054.01.48
  600047.01.70
  700041.01.95
  800035.52.25
  900030.52.62
 126.53.02
 1500012.06.67
 2 5.5   14.5


If you accept that the hi-pot test is based on normal
and expected mains overvoltages, then a reduction in
hi-pot test voltage as a function of altitude is not
warranted.  Mains overvoltages are normally-occurring
voltages due to switching of inductive loads.  These
overvoltages are NOT a function of altitude.

Consequently as one moves the equipment to a higher
altitude, the same hi-pot test voltage must be used.
To withstand the same hi-pot test voltage at the
higher altitude, the distances must be increased 
according to the IEC 664 table.


Best regards,
Rich




 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Altitude specifications

2003-05-22 Thread Jim Eichner

Thanks Ken.  A quick search uncovered the following website showing the
curve, which is indeed non-linear.
http://www.reynoldsindustries.com/product/2multipin/page17.asp

It appears, however, that the curve is close to linear in the limited
altitude range experienced by our products which typically are used in RV's,
boats, and buildings.  For the product in question, there are no aerospace
applications, so my gut feel is that we top out around 10,000 feet.  Anyone
responding to my initial enquiry please keep that estimate in mind.

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Thursday, May 22, 2003 11:56 AM
To: Jim Eichner; 'EMC-PSTC - forum'
Subject: Re: Altitude specifications


The Paschen curve that describes air dielectric breakdown vs. pressure is
not linear.  I think you can find it in the Reference Handbook for Radio
Engineers.

 From: Jim Eichner jim.eich...@xantrex.com
 Reply-To: Jim Eichner jim.eich...@xantrex.com
 Date: Thu, 22 May 2003 10:47:36 -0700
 To: 'EMC-PSTC - forum' emc-p...@majordomo.ieee.org
 Subject: Altitude specifications
 
 
 My understanding is that the main 2 effects of increased altitude on
 electronics are reduced  effectiveness of forced-air and convection
cooling
 methods and reduced dielectric strength of air-gaps (clearances).
 
 We are looking into this to determine an altitude specification for a new
 product under development, and we intend to use a 3rd party lab to do
hipot
 and temperature testing in an altitude chamber to determine our specs.
 
 I believe the effects are linear with altitude, from sea level up, however
 it occurred to me that there may be a simple rule of thumb along the lines
 of up to approx.  feet, you can expect very little effect.  I
realize
 that rules of thumb like this need to be treated with scepticism (hence my
 intent to test anyway), but I'm interested in peoples opinions and
 experiences.
 
 Thanks,
 
 Jim Eichner, P.Eng.
 Compliance Engineering Manager
 Xantrex Technology Inc.
 phone: (604) 422-2546
 fax: (604) 420-1591
 e-mail: jim.eich...@xantrex.com
 web: www.xantrex.com
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Altitude specifications

2003-05-22 Thread Jim Eichner

My understanding is that the main 2 effects of increased altitude on
electronics are reduced  effectiveness of forced-air and convection cooling
methods and reduced dielectric strength of air-gaps (clearances).  

We are looking into this to determine an altitude specification for a new
product under development, and we intend to use a 3rd party lab to do hipot
and temperature testing in an altitude chamber to determine our specs.  

I believe the effects are linear with altitude, from sea level up, however
it occurred to me that there may be a simple rule of thumb along the lines
of up to approx.  feet, you can expect very little effect.  I realize
that rules of thumb like this need to be treated with scepticism (hence my
intent to test anyway), but I'm interested in peoples opinions and
experiences.

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



EFT and surge immunity test equipment brands

2003-05-13 Thread Jim Eichner

So far, we have quotes on 2 manufacturer's units for the above tests.  I'm
looking for more sources.  My general impression so far is no surprise -
this is an exercise in trade-offs.  

EMC-Partner TRA-2000:  This unit is an all-in-one product with a decent
price and has had favourable reviews in this forum.  The drawback with an
all-in-one is that you can't have one project doing EFT while another
project is working on surge, and you lose both capabilities if the unit is
out for maintenance or calibration.  Also we already have ESD equipment, so
we don't need this unit's capabilities in that area.

Haefely:  Have quotes on the PEFT4010 and the PSURGE4010 with necessary
accessories.  The total cost of the two units is far higher (+60%), but
having separate units mitigates the objections above.

So...

1. What other companies should I look at?

2. Anybody want to share any experiences / opinions on the Haefely
equipment?  Does the extra $$ get us extra performance and reliability?

Thanks in advance for your help,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Anyone know when EN62040-1-1 will be published in the OJ?

2003-03-31 Thread Jim Eichner

This standard covers safety of UPS systems, and I guess it replaces
EN50091-1-1 at some point.  I need to know when EN62040-1-1 will be
published in the OJ (if anyone knows), when EN50091-1-1 ceases to be useful
for new approvals, and when products approved to it have to be updated to
the new standard.

I'd also appreciate any information anyone has as to whether there are any
substantial differences between the two standards or is it simply
re-numbered and re-confirmed?  Does it still, as EN50091-1-1 did, rely on
frozen-in-time references to the  EN60950:1992+A1+A2 or has it moved to the
current '950?

Thanks,
Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Compliance Technologist Position - Livermore, CA

2003-02-13 Thread Jim Eichner

I accidentally sent an old revision of the position summary earlier. Here's
the updated one, below the e-mail below this one!

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



  -Original Message-
 From: Jim Eichner  
 Sent: Thursday, February 13, 2003 4:20 PM
 To:   'EMC-PSTC - forum'
 Subject:  Compliance Technologist Position - Livermore, CA
 
 Xantrex Technology is hiring a Regulatory Technologist (product safety and
 EMC) for our Livermore, CA facility.  For general information about
 Xantrex, go to www.xantrex.com and have a look.  Our Livermore operation
 is primarily working on high power inverter systems for commercial and
 utility scale distributed generation applications, with specific
 information available at
 http://www.xantrex.com/applications/index.asp?did=321.  
 
 Please see the position summary below for details, and e-mail me directly
 with a resume and cover letter if you are interested in applying for the
 position.  Note that the position is not restricted to technologists:  a
 suitably qualified engineer would be considered.
 
 Thanks,
 Jim Eichner, P.Eng. 
 Compliance Engineering Manager
 Xantrex Technology Inc. 
 e-mail: jim.eich...@xantrex.com 
 web: www.xantrex.com 
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
  

***
Xantrex Technology
Regulatory Technologist
Livermore, California


Xantrex Technology Inc. develops, manufactures and markets leading advanced
power electronic and control products for a variety of distributed, mobile
and programmable power markets. The company's enabling technology converts
raw electrical power from any central, distributed, or backup power source
into high-quality power required by electronic and electrical equipment.

Xantrex products are used for various applications: for renewable and
distributed power solutions such as solar, wind, microturbines and fuel
cells; to supply backup power for homes, small businesses and traffic lights
during electric grid disruptions; to provide auxiliary electricity in boats,
recreational vehicles, cars, work vehicles, and heavy duty trucks; and to
develop, test, and power precision equipment such as semi-conductor
manufacturing and medical equipment. 

A privately owned company with 550 employees, Xantrex is headquartered in
Vancouver, British Columbia with additional facilities in Arlington,
Washington, Livermore, California, and Miami, Florida.

We are currently seeking a Regulatory Technologist to join our team in
Livermore.  This individual will be responsible for ensuring and maintaining
product compliance with regulatory requirements for product safety and
Electromagnetic Compatibility (EMC).  Works with design teams to provide
guidance, evaluate designs, and test for compliance.  Works with regulatory
agencies to obtain and maintain certifications.  Specific duties include:

*   Performs and supervises product safety and EMC testing, and produces
formal test reports for agencies, electric utilities, and design teams
*   Evaluates product designs to help ensure compliance in the final
design:
*   Provides interpretations of requirements to design
teams
*   Provides ongoing feedback and data to design teams
*   Writes and maintains the reports required to document regulatory
compliance
*   Works with utilities, agencies and 3rd party test labs for the
purposes of:
*   Obtaining testing and evaluation services
*   Obtaining and maintaining product approvals
*   Obtaining interpretations of requirements
*   Obtaining and maintaining a collection of current
standards
*   Performs as a project team member to achieve the technical,
schedule, and budget objectives of the team


Candidates must meet the following minimum qualifications:

*   Requires a 2-or 3-year technical degree or equivalent
*   Requires at least 5 years experience in regulatory compliance in the
power electronics industry, preferably in both the product safety and EMC
fields
*   Requires ability to design and test

Compliance Technologist Position - Livermore, CA

2003-02-13 Thread Jim Eichner

Xantrex Technology is hiring a Regulatory Technologist (product safety and
EMC) for our Livermore, CA facility.  For general information about Xantrex,
go to www.xantrex.com and have a look.  Our Livermore operation is primarily
working on high power inverter systems for commercial and utility scale
distributed generation applications, with specific information available at
http://www.xantrex.com/applications/index.asp?did=321.  

Please see the position summary below for details, and e-mail me directly
with a resume and cover letter if you are interested in applying for the
position.  Note that the position is not restricted to technologists:  a
suitably qualified engineer would be considered.

Thanks,
Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.


*

Position Summary:

Responsible for ensuring and maintaining product compliance with regulatory
requirements for product safety and Electromagnetic Compatibility (EMC).
Works with design teams to provide guidance, evaluate designs, and test for
compliance.  Works with regulatory agencies to obtain and maintain
certifications.

Responsibilities:

*   Provides and supervises product safety and EMC testing, and produces
formal test reports for agencies and design teams
*   Evaluates product designs to help ensure compliance in the final
design:
*   -   Provides interpretations of requirements to design teams
*   -   Provides ongoing feedback and data to design teams
*   Writes and maintains the reports required to document regulatory
compliance
*   Works with agencies and 3rd party test labs for the purposes of:
*   -   Obtaining testing and evaluation services
*   -   Obtaining and maintaining product approvals
*   -   Obtaining interpretations of requirements
*   -   Obtaining and maintaining a collection of current standards
*   Performs as a project team member to achieve the technical,
schedule, and budget objectives of the team
*   
*   Qualifications:
*   
*   Requires at least a two year technical degree or equivalent
*   Requires at least 5 years experience in regulatory compliance in the
power electronics industry, preferably in both the product safety and EMC
fields
*   Requires ability to design and test compliance solutions, perform
circuit analysis, breadboard solutions
*   Experience working with utilities and commissioning high power
systems
*   Extensive knowledge of current regulations applicable to product
safety and EMC (UL, CSA, CE, FCC, IEC, etc.)
*   Extensive hands-on experience with and knowledge of product safety
test methodology
*   Working knowledge of EMC pre-compliance test methodology
*   Working knowledge of power conversion technology, particularly at
high power levels (10kW - 2.5MW)
*   Strong written and oral communication skills, with emphasis on the
ability to create quality technical reports, test reports, and test
procedures, and to interact effectively with design teams
*   Strong organizational and time-management skills
*   Ability to adapt to changing priorities


Xantrex Technology Inc. is an equal opportunity employer.  We provide equal
employment opportunity to all applicants and employees without regard to
gender, national origin, religion, race, colour, sexual orientation,
physical or mental disability, or any other criterion that contravenes
legislated requirements.


*



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-31 Thread Jim Eichner

The approach that CSA takes is sensible in that it includes both the long
duration overload and high-current short circuit capabilities of the source.
Depending on your situation you can end up needing to do one or both of the
following:

1. Bond Impedance - run a current equal to 200% of the branch circuit
breaker rating through the bonding path for 2 minutes (derived from the I
vs. t curves allowed by CSA breaker standards).

2. Bond Limited short-circuit withstand - done at up to 5000A depending on
the supply circuit the product will be connected to; this test is performed
only when the capacity of the bonding path is in doubt (e.g. pcb traces).

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: Friday, January 31, 2003 9:23 AM
To: John Woodgate; emc-p...@majordomo.ieee.org
Subject: RE: Circuit Breaker Tripping Dring Fault Tests



John -

This proposal is based on a North American D1 Deviation to
IEC60950, Subclause 2.6.3.3, and is derived from CSA 22.2 No
0.4.  I have a product in my lab that this applies to and
two more products coming in to which it will also apply.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com

 From: John Woodgate

 There is a proposed amendment to IEC/EN 60950-1
 requiring a test of the
 protective conductor network at *prospective
 short-circuit current* for
 the time it takes for the mains circuit
 protective device to operate.
 The details are controversial at present, because
 the test currents
 appear not to have taken into account the
 differences between
 prospective short-circuit currents in different
 wiring systems and
 supply voltages. Given that reservation, the
 lowest test current is 200
 A.

 The amendment is aimed at protective conductors
 which are surface or
 internal traces of multi-layer printed boards. It
 is said that such
 traces have failed in the field under
 high-current fault conditions.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Automotive v. EMC Directives

2003-01-29 Thread Jim Eichner

You're right that the link I gave only gets you a copy of the Directive
without the figures.  The only downloadable versions I've found that do have
the figures are the .tif format ones available if you search on the document
from the following location:
http://europa.eu.int/eur-lex/en/search/search_lif.html

The search results will offer you the option of having a .tif file e-mailed
to you.  There are drawbacks to this - slow fuzzy viewing and large file
size which resulted in them breaking the directive into 2 parts when they
sent it to me.

Does anyone know another way to get directives on-line complete with the
figures, without resorting to .tif files?

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: KC CHAN [PDD] [mailto:kcc...@hkpc.org]
Sent: Tuesday, January 28, 2003 7:40 PM
To: alan.hud...@amsjv.com; emc-p...@majordomo.ieee.org;
jim.eich...@xantrex.com
Subject: RE: Automotive v. EMC Directives



Where can I have the figures referenced in the link?

 Jim Eichner jim.eich...@xantrex.com 01/29/03 03:46am 

The requirements are very different, especially in the test setup, and I
don't think you can make assumptions in either direction.  For an electronic
sub-assembly, for example, you do radiated emissions at a measurement
distance of 1m, which is very much in the near field.  You won't likely be
able to make any assumptions from that as to how you will fare in a 3m or
10m emissions test for the EMC Directive, which is arguably in the far
field.  There are lots of other significant differences, so I'm afraid
you'll need to do the reading and do some testing.  

One bit of good news:  the Automotive EMC Directive contains its own
requirements, so you don't need to buy standards to go along with it.
Here's a link:

http://europa.eu.int/smartapi/cgi/sga_doc?smartapi!celexapi!prod!CELEXnumdoc

lg=ENnumdoc=31995L0054model=guichett

Good luck,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






From: Hudson, Alan [mailto:alan.hud...@amsjv.com] 
Sent: Tuesday, January 28, 2003 9:34 AM
To: EMC-pstc (E-mail)
Subject: Automotive v. EMC Directives






G'Day!

Is anyone familiar with the standards needed to comply with the Automotive
*and* the EMC Directives? How do they compare? Or to put it another way, if
an item of equipment was known to be compliant with the Automotive
Directive, is it likely that it would therefore meet the requirements of the
EMC Directive?

Alan
-- 
Alenia Marconi Systems
Scotland


This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-28 Thread Jim Eichner
I've been trying to solve this one myself.  I work with one pair of standards
(UL458 / CSA107.1) where they specifically say that opening the branch circuit
protection is acceptable during component fault testing, but NOT during short
circuit tests done for the purposes of validating inadequate trace spacings
(an easement offered in the standards in some situations).  I've always been
puzzled why we can't rely on branch circuit protection for both situations,
but neither agency has been able to explain the difference to me.
 
Jim Eichner, P.Eng.
Regulatory Compliance Manager
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.


From: peter merguerian [mailto:pmerguerian2...@yahoo.com]
Sent: Tuesday, January 28, 2003 11:54 AM
To: emc-p...@majordomo.ieee.org
Subject: Circuit Breaker Tripping Dring Fault Tests



Dear All,

For safety, it is not clear from the standards whether the main branch circuit
breaker tripping during fault conditions is an acceptable result.

I see no reason why this should not be acceptable. What is your view? Some
third party labs find it acceptable and others do not.

Anyone can lead me to some inernational decisions regarding this issue?

Thanks,

Peter

 

 




  _  

Do you Yahoo!?
Yahoo! Mail  http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com
Plus - Powerful. Affordable. Sign up  
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com now




RE: Automotive v. EMC Directives

2003-01-28 Thread Jim Eichner

The requirements are very different, especially in the test setup, and I
don't think you can make assumptions in either direction.  For an electronic
sub-assembly, for example, you do radiated emissions at a measurement
distance of 1m, which is very much in the near field.  You won't likely be
able to make any assumptions from that as to how you will fare in a 3m or
10m emissions test for the EMC Directive, which is arguably in the far
field.  There are lots of other significant differences, so I'm afraid
you'll need to do the reading and do some testing.  

One bit of good news:  the Automotive EMC Directive contains its own
requirements, so you don't need to buy standards to go along with it.
Here's a link:

http://europa.eu.int/smartapi/cgi/sga_doc?smartapi!celexapi!prod!CELEXnumdoc
lg=ENnumdoc=31995L0054model=guichett

Good luck,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






From: Hudson, Alan [mailto:alan.hud...@amsjv.com]
Sent: Tuesday, January 28, 2003 9:34 AM
To: EMC-pstc (E-mail)
Subject: Automotive v. EMC Directives






G'Day!

Is anyone familiar with the standards needed to comply with the Automotive
*and* the EMC Directives? How do they compare? Or to put it another way, if
an item of equipment was known to be compliant with the Automotive
Directive, is it likely that it would therefore meet the requirements of the
EMC Directive?

Alan
-- 
Alenia Marconi Systems
Scotland


This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Ferrite clamps

2002-11-22 Thread Jim Eichner

Isn't that the basis for measuring conducted emissions below 30MHz rather
than radiated, since you reach the limits of practical antenna size?

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Thursday, November 21, 2002 12:20 PM
To: don_borow...@selinc.com; emc-p...@majordomo.ieee.org
Subject: Re: Ferrite clamps



There was/is a very smart engineer named Balint Szentkuti (a good Hungarian
name, just like Javor) who about twenty years ago proposed replacing
radiated measurements of cable-sourced emissions with measurement of cable
common mode conducted emissions.  This seems an eminently sensible idea to
me.  You base the conducted current emission limits on a reasonable worst
case radiating efficiency of a cable of a certain length a certain distance
above ground.

Mr. Szentkuti wrote several papers on this subject, to my recollection.
Here is one reference:

Szentkuti, B., Give Up Radiation Testing In Favour Of Conduction Testing,
Proceedings, EMC Zurich 1989.

--
From: don_borow...@selinc.com
To: emc-p...@majordomo.ieee.org
Subject: RE: Ferrite clamps
Date: Thu, Nov 21, 2002, 12:59 PM




 David-

 I agree with what you say, but it is even more complicated than that.

 As you say, ferrite clamps can be ineffective. Their effectiveness all
 depends on the wave impedance at the point where they are attached. Due to
 standing waves, the wave impedance varies greatly. If a ferrite clamp is
 attached at a high wave impedance point (current minimum point), there
will
 be minimal effect.

 A ferrite clamp tries to insert a high series impedance in the cable.
There
 are several problems:
  1. It is difficult to obtain a high series impedance over a broad
 range of frequencies.
  2. If all you have is a series impedance, the S21 is highly dependant
 on the system impedance. In the limit where the series impedance Z is much
 greater than the system impedance Zs, |S21| = |2Zs/Z|. The system
impedance
 is the wave impedance (which varies greatly) at the clamp.

 One could use clamps that measure a consistent, small value of S21
measured
 in a 50 ohm system and still have a quite a bit of variation during
 application. On the other hand, if S21 is very small (series impedance is
 very high), it probably doesn't make much difference that it varies, since
 the signal passed though would always be rather small. Unfortunately,
 making such a high impedance over a broad range of frequencies is very
 difficult.

 The only way I see to get really good repeatability would be to have
 devices with high impedance series element(s) and low impedance shunt
 element(s). But then we are talking coupling-decoupling networks (CDNs),
 and need to connect them to the ground plane. This is possible to do, more
 more costly and complex.

 Just controlling insertion loss (unless it is very large) will not do the
 trick.

 Having said all that, while ferrite clamps are not the be-all and end-all,
 they certainly do improve the test to some degree, since they do indeed
 isolate the EUT from the cable beyond the clamp when the wave impedance is
 moderately low (which it is at least some of the time).

 Don Borowski
 Schweitzer Engineering Labs
 (Ex-HP/Agilent)





 Pommerenke, David davi...@umr.edu@majordomo.ieee.org on 11/21/2002
 07:54:34 AM

 Please respond to Pommerenke, David davi...@umr.edu

 Sent by:owner-emc-p...@majordomo.ieee.org


 To:Pettit, Ghery ghery.pet...@intel.com, Conway, Patrick R
conw...@louisville.stortek.com, emc-p...@majordomo.ieee.org
 cc:
 Subject:RE: Ferrite clamps



 Dear Patrick,

 The aim of the standard was to avoid having standing current waves on
 cables between the EUT and the point at which they leave the chamber.
 Those resonances will cause highly setup and termination impedance
 dependent radiation measurements leading to large site-to-site
 correlation problems.

 The ferrite clamps have been added for absorbing the current wave in a
 defined fashion.

 The problem is that the standard is fundamentally wrong!

 Why ?
 The ferrite clamps are only specified by their insertion loss. Insertion
 loss says NOTHING about the reflection. So the ferrite clamps may not
 absorb at all, they may just reflect the current wave worsening the
 resonance problem or shifting it to a different frequency.

 The overall uncertainty is not a bit reduced by inserting the clamps due
 to false

Harmonics - IEC/EN 61000-3-4 for equipment 16A

2002-10-15 Thread Jim Eichner

I have not been able to find any info on an EN version of the above, but
there is a published IEC version.  The Europa site does not list -3-4 as
having been published in the OJ for the EMC directive.  

The IEC site contains the scope of the standard, including the following:
These recommendations specify the information required to enable a
supply authority to assess equipment regarding harmonic disturbance and to
decide wether or not the equipment is acceptable for connection with regard
to the harmonic distortion aspect. This document is not to be regarded as an
International Standard.

Questions:

1. This quote leaves me a bit puzzled.  Does this standard contain test
methods and pass/fail criteria, or is it somewhat less concrete than that?  

2. Is anyone aware of a published or draft EN version?

3. Is there an upper limit to the current (e.g. EN61000-3-11 goes from 16A
to 75A)?

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Twisting the LVD (was: RE: CE Mark vs. e-Mark)

2002-10-11 Thread Jim Eichner

Thanks everyone.  We do indeed want to use the LVD anyway, and have adopted
the interpretation for years that has now been made official by the
guideline quoted below.

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




-Original Message-
From: John Allen [mailto:john.al...@era.co.uk]
Sent: Wednesday, October 09, 2002 10:25 AM
To: 'Peter L. Tarver'; emc-p...@majordomo.ieee.org
Subject: RE: Twisting the LVD (was: RE: CE Mark vs. e-Mark)



Peter

I think that your question is answered quite clearly in the second paragraph
that I quoted from the guidelines, where it states:
'Following discussions with Member States the Commission has taken the
position that the term designed for use with a voltage range shall be
understood at equipment having either a rated input voltage or a rated
output
voltage inside this voltage range.'

Therefore the 12V to 120V (or 230V for Europe) device described in your
example is quite clearly within the scope of the LVD - and, Yes, similar
devices are available in Europe. For example, see the illustration of a
similar device for sale on the RS Components Website in the UK at
http://rswww.com/cgi-bin/bv/browse/Module.jsp?BV_SessionID=1646810601.10
34183756BV_EngineID=ccchadcghdjlhhmcfngcfkmdgkldfhk.0stockNo=597475lo
gText=uk520logType=103prmstocknum=597475logText=uk520logType=103

This has a UK BS1363 13A socket and carries a CE Mark - but under what
Directive, or Directives, I do not know as I do not have the DoC. In fact it
might well include the EMC Directive as it could be used outside of a
vehicle and directly from a 12V automobile battery (a good way to run your
central heating timer and boiler controls when there is a mains power cut!)

The aim of the LVD is to ensure protection of persons (and domestic
animals!), and the shock and fire hazards from such a device are just at
least as high as a unit where the equipment is supplied at 230V and has a
230V convenience outlet - so application of the LVD (and possibly the EMCD)
is entirely appropriate.

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:+44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:+44 (0) 1372-367102 (Fax)



-Original Message-
From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 09 October 2002 15:50
To: emc-p...@majordomo.ieee.org
Subject: Twisting the LVD (was: RE: CE Mark vs. e-Mark)



John -

The case of internal use of elevated voltages (as in a lap
top computer screen backlight) is clearly addressed by the
interpretation.

To test the consistency of the interpretation, imagine a
product with a supply voltage below the limits in the LVD,
where the LVD would not apply to that product.  That product
then performs power transformation (or conversion) and, in
turn, supplies other equipment (whether ancillary to the
equipment performing the conversion or not) at voltages
within the scope of the LVD, making the LVD applicable to
the latter product.

Does the term supply in reference to the aforementioned
interpretation apply only to the energy sinking port of
equipment or to all equipment ports, whether sinking or
sourcing electrical energy?

Example: A product available in the US (and possibly in
Europe) is a power inverter that can supply household
appliances using an automobile battery as its source.  Handy
for weekend campers that prefer to bring a few conveniences
along with them.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com

 -Original Message-
 From: John Woodgate
 Sent: Wednesday, October 09, 2002 12:37 AM
 To: emc-p...@majordomo.ieee.org
 Subject: Re: CE Mark vs. e-Mark

 Although the wording of the LVD implies that
 the voltage limits
 apply to internally-generated voltages, there is
 now an official
 'interpretation' that they apply only to supply voltages.
 --
 Regards, John Woodgate



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard

RE: CE Mark vs. e-Mark

2002-10-09 Thread Jim Eichner

Thanks everyone -  I have my answer.  By the way, the LVD is in fact
applicable, because the product in question creates 120Vac from the 12Vdc it
gets from the car.  

So the answer is that since the EMCD is not applicable where the AEMCD is
applicable, there is nothing wrong with a CE Mark and a Declaration only to
the LVD.

We should do the CE Mark for LVD only, and e-Mark for AEMCD.

Thanks as always for the invaluable sounding board that this forum provides.


Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Tuesday, October 08, 2002 3:38 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: CE Mark vs. e-Mark



I read in !emc-pstc that Jim Eichner jim.eich...@xantrex.com wrote (in
67C475A5ECE7D4118AEC0002B325CAB603510F7E@BCMAIL1) about 'CE Mark vs.
e-Mark' on Mon, 7 Oct 2002:
However using the CE Mark requires using all applicable
directives, 

True, but, as you just said, the EMCD is NOT applicable.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Newcomer to NEBS

2002-10-09 Thread Jim Eichner

I'm starting up the learning curve on NEBS compliance, and am looking for
any web resources or articles that would have a management-level primer on
the requirements.

All I know is that it covers EMC, safety, and environmental, there are
different levels (1, 2, and 3?), and different potential customers disagree
on what level we need to have.  We need to understand the basic differences
between these levels, how much testing is involved for each level, and what
the cost might be.

Of course we are going to get our hands on the standard(s) and study them,
but in the meantime a primer would be very useful.  We would also consider
seminars if there's something close by the Pacific northwest.

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


CE Mark vs. e-Mark

2002-10-08 Thread Jim Eichner

Let's suppose you have a product that is bound only for automotive
aftermarket applications, and while it complies with the LVD and the
Automotive EMC Directive (AEMCD), it fails to pass the EMC Directive (EMCD).


For EMC purposes, the directives are very clear:  you do not need to meet
the EMCD if your product is solely automotive, only the AEMCD.  However for
safety purposes the LVD still seems to apply, suggesting you need to have
the CE Mark. However using the CE Mark requires using all applicable
directives, therefore necessitating compliance with the EMCD, which our
theoretical product does not comply with.

Is there any way to do a safety only CE Mark accompanied by the e-Mark for
EMC, thus covering both required bases in the automotive world?

Am I missing a more obvious solution?

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


FW: EMC Prosecution in UK

2002-09-26 Thread Jim Eichner
I read this article with some consternation, since in my mind it challenges
not the manufacturer or importer, but the concept of Presumption of
Conformity (I'll use PofC...).
 
Quote:  If the standard in question only covers some of the EM phenomena,
or is limited in its scope, then full compliance cannot be guaranteed. The
products thus failed the essential protection requirements and were
incorrectly CE marked.
 
I am in strong disagreement with that statement.  If the standard in
question only covers some of the EM phenomena, then the standard in question
does NOT provide PofC and should NOT have been published in the OJ or on the
Europa site as a harmonized standard under the EMC Directive.  It is not the
manufacturer's fault if the EU incorrectly publishes references in the OJ
implying PofC where there are essential requirements not covered.  In my
mind, the CE Mark was correctly applied by the mfr, and the fault lies with
EN55014 (which I have always thought is flawed) and with the EU/CEN for
issuing a standard that fails to provide PofC.
 
Am I right or am I delusional, naive, misinformed, an idealist, or all of
the above?!?!?
 
At the very least, it seems to me that the EU has an obligation to provide
more information.  If a standard is listed as applicable to the EMC
Directive and does not provide PofC, then the standard's preamble and the
Europa listing should say so, and should point out which essential
requirements are not addressed, and which standards should be used to cover
the missing requirements.  I am getting extremely tired of the let the mfr
figure it out approach used by the EU.
 
Ok, I'll stop whining now.
Jim Eichner, P.Eng.
Regulatory Compliance Manager 
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com  


Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really. 


Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.


 -Original Message-
From: Alan E Hutley [mailto:nutwoo...@nutwood.eu.com]
Sent: Wednesday, September 25, 2002 11:43 PM
To: Emc-Pstc Discussion Group
Subject: EMC Prosecution in UK


EMC Prosecution, the company mentioned in the report Hot UK Ltd is owned by
Helen of Troy based in El Paso Texas.
 
For full story go click below
 
 http://www.compliance-club.com/TS%20Prosecution.doc
http://www.compliance-club.com/TS%20Prosecution.doc 
 
Alan E Hutley
EMC Compliance Journal
www.compliance-club.com http://www.compliance-club.com 
 


RE: EN61000-3-2

2002-09-25 Thread Jim Eichner

This harmonics thing is still, after all these years, annoyingly slippery.
I have a very basic question, that until yesterday and today I thought I
knew the answer to:  What harmonic current limits standard should I tell
designers to design to today?  

I thought the answer was EN61000-3-2:2000, on the understanding that it was
the same as, but clearer than, the A14 version, and that it was the final
foreseeable version.  Now I hear that no, there are actually differences
that make the 2000 version tougher to meet, and I hear that the 2000 edition
will be superceded (yet again) by an updated IEC version that has so far not
been voted on and could therefore incorporate further changes.

How is a manufacturer supposed to design products, with 3-10 year expected
lifetimes and long development cycle times, in the face of constantly
changing requirements and effectivity dates?  

At present, it seems the only thing I can do is to tell designers to work to
A14, even though it will be superceded, since the 2000 edition is also going
to be superceded.

Comments? 

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, September 25, 2002 4:10 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: EN61000-3-2



I read in !emc-pstc that Frazee, Douglas (Douglas) dfra...@lucent.com
wrote (in b5113b318d44bbe87dc50092eda96c6...@nj7460exch006u.ho.luce
nt.com) about 'EN61000-3-2' on Tue, 24 Sep 2002:

  Note that A14 is essentially 
optional as it expires on the same date at which it becomes mandatory. 


This apparently nonsensical situation persists because of a problem
raised about the IEC edition including the same provisions as A14. For
formal reasons, this problem can only be resolved by National Committees
voting on an amendment, which has still to be drafted, AFAIK (and I
should K, being a member of the IEC WG concerned)!

When the IEC standard is finally published, it will be adopted by
CENELEC in place of the 2000 edition.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Surge and EFT test equipment for AC, DC, and signal ports

2002-09-24 Thread Jim Eichner

Thanks to all who have responded so far.  One note of clarification: we are
already set up for doing ESD testing in-house, and I agree that's where most
of our failures will happen.  I also agree that much of the immunity suite
will take care of itself on a well designed unit that has low emissions, but
I don't think that's true with surge.  Maybe EFT, but not surge.

Note:  please refrain from replying both to me and to the forum - you only
need to reply to the forum.  I suspect some, but by no means all, of our
double-posting complaints stem from people sending 2 replies.  Having said
that, I am getting 3 of everything this morning!

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.


-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Monday, September 23, 2002 2:45 PM
To: 'EMC-PSTC - forum'
Subject: Surge and EFT test equipment for AC, DC, and signal ports



 We are starting to look into the costs and issues around gearing up for
 some immunity testing, with the intent of determining whether or not it is
 too hard or too expensive to gear up to do some of it at home. We are
 not looking for final formal compliance results here, only for
 pre-compliance peace of mind. In particular, I need to consider the
 following:
 
 1. EFT (EN61000-4-4) - AC input, output, and ground lines, DC input and
 output lines, signal/control lines
 2. Surges (EN 61000-4-5) - AC input, output, and ground lines, DC input
 and output lines, signal/control lines
 3. Surges (SAE J1113/11) on DC power leads
 4. Fast transients (SAE J1113/12) on other than power leads
 
 The products which we hope to be able to test in-house are power
 conversion and control products, and have a wide range of input/output
 voltages and power:
 
 - AC inputs up to 120V, 60A, or 230Vac, 30A single-phase, 120/240V, 50A,
 split-phase, and 120/208V, 30A, 3-phase
 - AC outputs up to 120Vac, 60A, 230Vac, 30A, 120/240V, 50A split-phase 
 - DC inputs up to 12V, 500A; 24V, 300A; 48V, 200A
 - DC outputs up to 12kW at 10 - 600Vdc (1200A - 20A)
 
 Questions:
 
 1. Is there any single piece of equipment (with accessories/modules/etc.)
 available that can do both Surge and EFT tests on equipment, or are these
 tests just too different?
 
 2. Surge - Is there any single piece of equipment (with
 accessories/modules/etc.) available that can do surges on all these types
 of ports: AC and DC and signal/control?  Any info re mfr, cat. no., price,
 etc. would be appreciated.
 
 3. EFT - Is there any single piece of equipment (with
 accessories/modules/etc.) available that can do EFT on all these types of
 ports: AC and DC and signal/control?  Any info re mfr, cat. no., price,
 etc. would be appreciated.
 
 4. Do these tests have to be run at full output (which may limit my
 ability to find 3rd party labs with suitable equipment, let alone gear up
 in-house) or can they be run with a light load on the equipment and then
 test full output after each test to confirm return to normal operation?  
 
 Thanks in advance for your help,
 Jim Eichner, P.Eng. 
 Regulatory Compliance Manager
 Xantrex Technology Inc. 
 e-mail: jim.eich...@xantrex.com 
 web: www.xantrex.com 
 Any opinions expressed are those of my invisible friend, who really
 exists.  Honest.  No, really.
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc

Surge and EFT test equipment for AC, DC, and signal ports

2002-09-23 Thread Jim Eichner

 We are starting to look into the costs and issues around gearing up for
 some immunity testing, with the intent of determining whether or not it is
 too hard or too expensive to gear up to do some of it at home. We are
 not looking for final formal compliance results here, only for
 pre-compliance peace of mind. In particular, I need to consider the
 following:
 
 1. EFT (EN61000-4-4) - AC input, output, and ground lines, DC input and
 output lines, signal/control lines
 2. Surges (EN 61000-4-5) - AC input, output, and ground lines, DC input
 and output lines, signal/control lines
 3. Surges (SAE J1113/11) on DC power leads
 4. Fast transients (SAE J1113/12) on other than power leads
 
 The products which we hope to be able to test in-house are power
 conversion and control products, and have a wide range of input/output
 voltages and power:
 
 - AC inputs up to 120V, 60A, or 230Vac, 30A single-phase, 120/240V, 50A,
 split-phase, and 120/208V, 30A, 3-phase
 - AC outputs up to 120Vac, 60A, 230Vac, 30A, 120/240V, 50A split-phase 
 - DC inputs up to 12V, 500A; 24V, 300A; 48V, 200A
 - DC outputs up to 12kW at 10 - 600Vdc (1200A - 20A)
 
 Questions:
 
 1. Is there any single piece of equipment (with accessories/modules/etc.)
 available that can do both Surge and EFT tests on equipment, or are these
 tests just too different?
 
 2. Surge - Is there any single piece of equipment (with
 accessories/modules/etc.) available that can do surges on all these types
 of ports: AC and DC and signal/control?  Any info re mfr, cat. no., price,
 etc. would be appreciated.
 
 3. EFT - Is there any single piece of equipment (with
 accessories/modules/etc.) available that can do EFT on all these types of
 ports: AC and DC and signal/control?  Any info re mfr, cat. no., price,
 etc. would be appreciated.
 
 4. Do these tests have to be run at full output (which may limit my
 ability to find 3rd party labs with suitable equipment, let alone gear up
 in-house) or can they be run with a light load on the equipment and then
 test full output after each test to confirm return to normal operation?  
 
 Thanks in advance for your help,
 Jim Eichner, P.Eng. 
 Regulatory Compliance Manager
 Xantrex Technology Inc. 
 e-mail: jim.eich...@xantrex.com 
 web: www.xantrex.com 
 Any opinions expressed are those of my invisible friend, who really
 exists.  Honest.  No, really.
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Current from Car 12V cigarette lighter socket / 42 VDC

2002-09-19 Thread Jim Eichner

Well that's the $1M question, isn't it!  

My involvement is tangential at best, but my understanding is that the
effort is not going to be coordinated as a grand simultaneous roll-out.
Rather each mfr of cars, trucks, boats, etc, will get around to it based on
their own needs.  The drivers for this effort vary widely - vehicle
emissions, increased electrical loads, drive-by-wire technology, etc. - and
the 42Vdc agenda for a given mfr is to some extent determined by the agenda
for those features or regulations.  There is much technology still to be
developed and much standardization work still to be done, but the work is
well in progress.

Is there anyone on the forum who has a more inside view of this and can
share some information with us?

In the meantime, have a look at the web.  Searching on 42V can yield a lot
of hits.  Here's one I found that summarizes things a bit:

http://www.sae.org/42volt/dual_higher_sum.pdf

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






-Original Message-
From: Price, Ed [mailto:ed.pr...@cubic.com]
Sent: Wednesday, September 18, 2002 6:42 PM
To: 'EMC-PSTC - forum'
Subject: RE: Current from Car 12V cigarette lighter socket / 42 VDC

Pardon the slight topic shift, but when will we be seeing 42 VDC automotive
systems? I understand that there has already been some fleet vehicle
production with the 42 VDC standard, but when will it be introduced to the
consumer market?

Regards,

Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis

---

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Current from Car 12V cigarette lighter socket

2002-09-18 Thread Jim Eichner

Thanks.

The solution you propose is in the works.  The SAE is working on a
completely different style connector for power connections to 12Vdc, and 2
other styles for 42Vdc and 120Vac connectors.  This effort is just getting
off the ground however.

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.





-Original Message-
From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Wednesday, September 18, 2002 1:14 PM
To: Jim Eichner; 'EMC-PSTC - forum'
Subject: Re: Current from Car 12V cigarette lighter socket


An excellent post.  Seems like a solution here would be for the newer 
electrical outlet to be designed differently and not mate with the older
male cigarette lighter insert, and then provide an adapter that would take
the cigarette lighter insert to the new electrical outlet.  Then the 8 Amp
limit could be relaxed for appliances with the new plug, and any old devices
would still be taken care of.

--
From: Jim Eichner jim.eich...@xantrex.com
To: 'EMC-PSTC - forum' emc-p...@majordomo.ieee.org
Subject: RE: Current from Car 12V cigarette lighter socket
Date: Wed, Sep 18, 2002, 1:47 PM



 UL2089 covers appliance using the socket.  There is no UL or CSA standard
 covering the socket itself, but there is SAE J563, which provided
dimensions
 and limits the continuous current drawn through lighter sockets by
 appliances to 8Adc.

 The intent is to protect the wiring in behind the lighter socket, because
 that wiring is based on an intermittent 10-15A load (how often do you
light
 a cigarette?) and is therefore undersized for its overcurrent protection.
 In a sample of 7 or 8 cigarette lighter sockets and wiring harnesses that
I
 pulled out of different makes of car in the mid 90's, I found wire sizes
 ranging from No. 16AWG to 22AWG, being protected by fuses ranging from 15
to
 30A!

 In the world of continuous 12Vdc loads - aftermarket accessories like
 chargers for cell phones and laptops, in-your-car coffee makers and vacuum
 cleaners, etc - we need to know what continuous load the lighter socket
and
 its harness can sustain.  The SAE pegs this at 8A and UL and CSA are
 enforcing that limit, both in what they will allow a 12Vdc appliance to
 draw, and in requiring a max. 8A fuse in the lighter plug.

 Recognizing the limitations on lighter sockets, the automotive industry
has
 come up with the power point: a cylindrical connector based on the
 cigarette lighter socket but designed, fused, wired, and rated for
 continuous loads and lacking the bimetal fingers that release the lighter
 plug when it's hot.  These are usually rated for 15-20Adc continuous,
 allowing designers to be free of the 8A limit. In theory.

 However, since the male plugs on 12Vdc automotive appliances will fit both
 the true lighter socket and these newer power points, UL and CSA will not
 back down (nor should they) from the 8A limit for a 12Vdc appliance
equipped
 with a male plug that fits a lighter socket.  They also will not accept a
 marking such as Use only with power points, not with lighter sockets
 because too many cars only have lighter sockets.

 Not sure you're trying to do anything with that kind of power level, but
you
 should be aware of the limitations.

 Regards,

 Jim Eichner, P.Eng.
 Manager, Engineering Services
 Xantrex Technology Inc.
 e-mail: jim.eich...@xantrex.com
 web: www.xantrex.com
 Any opinions expressed are those of my invisible friend, who really
exists.
 Honest.  No really.

 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.




 -Original Message-
 From: Ron Baugh [mailto:ron...@verifone.com]
 Sent: Wednesday, September 18, 2002 3:41 AM
 To: 'Charles Blackham'; 'emc-p...@majordomo.ieee.org'
 Subject: RE: Current from Car 12V cigarette lighter socket



 Yes Charles it's UL 2089 Vehicle Battery Adapters.  I also have a unit
 (ITE
 Listed) that will operate from a auto battery and I have to make sure that
 all
 my 12V devices meets this standard.

 Ron Baugh
 VeriFone, Inc.
  -Original Message-
  From: Charles Blackham [SMTP:cblac...@airspan.com]
  Sent: Wednesday, September 18, 2002 2:07 AM

RE: Current from Car 12V cigarette lighter socket

2002-09-18 Thread Jim Eichner

UL2089 covers appliance using the socket.  There is no UL or CSA standard
covering the socket itself, but there is SAE J563, which provided dimensions
and limits the continuous current drawn through lighter sockets by
appliances to 8Adc.  

The intent is to protect the wiring in behind the lighter socket, because
that wiring is based on an intermittent 10-15A load (how often do you light
a cigarette?) and is therefore undersized for its overcurrent protection.
In a sample of 7 or 8 cigarette lighter sockets and wiring harnesses that I
pulled out of different makes of car in the mid 90's, I found wire sizes
ranging from No. 16AWG to 22AWG, being protected by fuses ranging from 15 to
30A!  

In the world of continuous 12Vdc loads - aftermarket accessories like
chargers for cell phones and laptops, in-your-car coffee makers and vacuum
cleaners, etc - we need to know what continuous load the lighter socket and
its harness can sustain.  The SAE pegs this at 8A and UL and CSA are
enforcing that limit, both in what they will allow a 12Vdc appliance to
draw, and in requiring a max. 8A fuse in the lighter plug.

Recognizing the limitations on lighter sockets, the automotive industry has
come up with the power point: a cylindrical connector based on the
cigarette lighter socket but designed, fused, wired, and rated for
continuous loads and lacking the bimetal fingers that release the lighter
plug when it's hot.  These are usually rated for 15-20Adc continuous,
allowing designers to be free of the 8A limit. In theory. 

However, since the male plugs on 12Vdc automotive appliances will fit both
the true lighter socket and these newer power points, UL and CSA will not
back down (nor should they) from the 8A limit for a 12Vdc appliance equipped
with a male plug that fits a lighter socket.  They also will not accept a
marking such as Use only with power points, not with lighter sockets
because too many cars only have lighter sockets.

Not sure you're trying to do anything with that kind of power level, but you
should be aware of the limitations.

Regards,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




-Original Message-
From: Ron Baugh [mailto:ron...@verifone.com]
Sent: Wednesday, September 18, 2002 3:41 AM
To: 'Charles Blackham'; 'emc-p...@majordomo.ieee.org'
Subject: RE: Current from Car 12V cigarette lighter socket



Yes Charles it's UL 2089 Vehicle Battery Adapters.  I also have a unit
(ITE
Listed) that will operate from a auto battery and I have to make sure that
all
my 12V devices meets this standard.

Ron Baugh
VeriFone, Inc.
-Original Message-
From:   Charles Blackham [SMTP:cblac...@airspan.com]
Sent:   Wednesday, September 18, 2002 2:07 AM
To: 'emc-p...@majordomo.ieee.org'
Subject:Current from Car 12V cigarette lighter socket


Some of our equipment runs off 12Vdc. Typically this is provided by
a UL
Listed ac/dc power supply that meets the Limited Power Source requirement of
IEC60950. We wish to be able to power this from the 12V cigarette lighter
socket in a car:

Is there a standard that covers the output of 12V sockets in cars?
Do
they have to meet something similar to the Limited Power Source requirements
of
IEC60950?

regards 

Charlie Blackham 
Senior Approvals Engineer 
Airspan Communications Ltd. 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org

RE: harmonic current on inverters for industrial uses in Japan

2002-09-13 Thread Jim Eichner

Sorry - industrial motor drives, frequency converters, or other AC-AC
converters didn't occur to me as the source of the question, since I don't
consider them inverters.  They are AC-AC converters containing DC-AC
inverters. (IMHO).

Ahh the joys of semantics.


Jim Eichner, P.Eng. 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.





-Original Message-
From: gunter_j_ma...@embraco.com.br
[mailto:gunter_j_ma...@embraco.com.br]
Sent: Friday, September 13, 2002 3:36 AM
To: Jim Eichner; emc-p...@majordomo.ieee.org
Subject: RE: harmonic current on inverters for industrial uses in Japan



Most of the industrial inverters draw harmonics current from the AC power
supply, and this input current is independent of the inverter current.
The input stage (that converts AC to DC) is usually a diode bridge
rectifier.

Günter J. Maass
Researcher - Power Electronics Development
EMBRACO S.A.



 

  Jim Eichner

  Jim.eichner@Xantrex.cTo:   EMC-PSTC
(E-mail) emc-p...@ieee.org   
  om   cc:

  Sent by:  Subject:  RE: harmonic
current on inverters for industrial uses in Japan
  owner-emc-pstc@majordo

  mo.ieee.org

 

 

  12/09/2002 22:45

  Please respond to Jim

  Eichner

 

 






Minor correction of myself.  Of course inverters draw harmonic current,
from
their DC source: harmonics of the inverter's internal switching frequency.
What I meant was inverters don't draw the type of harmonic currents that
have been the subject of new regulations over the past few years
(EN61000-3-2 etc).


Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Thursday, September 12, 2002 10:43 AM
To: 'POWELL, DOUG'; EMC-PSTC (E-mail)
Subject: RE: harmonic current on inverters for industrial uses in Japan



Hi Doug:  Please let me know what you find out on this.  I recently came
across a reference to inverters, in searching the JEITA site for harmonic
current limitation standards.  That didn't make sense to me:  an inverter
is
a DC-AC converter that has no connection to an AC source and draws no
harmonic current.  The only thing I could think of is that maybe they were
on about harmonic content of the output, not the input.  If so, I hope they
are talking about voltage, because the harmonic content in the output
current will depend upon the nature of the load.

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, September 12, 2002 7:58 AM
To: EMC-PSTC (E-mail)
Subject: harmonic current on inverters for industrial uses in Japan



Hello esteemed colleagues,

I am searching for an English language version of a report writtne in
Japanese, I already have the title translated:

Calculation methods of harmonic current on inverters for industrial uses.
JEM- TR 201


Can enayone help with location of this report in English?


thank you so much,

-doug

---
Douglas E. Powell, Compliance Engineer
Advanced Energy Industries, Inc.
Mail stop: 203024
1626 Sharp Point Drive
Ft. Collins, CO 80525

970.407.6410 (phone)
970-407.5410 (fax)
mailto:doug.pow...@aei.com

RE: harmonic current on inverters for industrial uses in Japan

2002-09-13 Thread Jim Eichner

Minor correction of myself.  Of course inverters draw harmonic current, from
their DC source: harmonics of the inverter's internal switching frequency.
What I meant was inverters don't draw the type of harmonic currents that
have been the subject of new regulations over the past few years
(EN61000-3-2 etc).


Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Thursday, September 12, 2002 10:43 AM
To: 'POWELL, DOUG'; EMC-PSTC (E-mail)
Subject: RE: harmonic current on inverters for industrial uses in Japan



Hi Doug:  Please let me know what you find out on this.  I recently came
across a reference to inverters, in searching the JEITA site for harmonic
current limitation standards.  That didn't make sense to me:  an inverter is
a DC-AC converter that has no connection to an AC source and draws no
harmonic current.  The only thing I could think of is that maybe they were
on about harmonic content of the output, not the input.  If so, I hope they
are talking about voltage, because the harmonic content in the output
current will depend upon the nature of the load.

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, September 12, 2002 7:58 AM
To: EMC-PSTC (E-mail)
Subject: harmonic current on inverters for industrial uses in Japan



Hello esteemed colleagues,

I am searching for an English language version of a report writtne in
Japanese, I already have the title translated:

Calculation methods of harmonic current on inverters for industrial uses.
JEM- TR 201


Can enayone help with location of this report in English?


thank you so much,

-doug

---
Douglas E. Powell, Compliance Engineer
Advanced Energy Industries, Inc.
Mail stop: 203024
1626 Sharp Point Drive
Ft. Collins, CO 80525

970.407.6410 (phone)
970-407.5410 (fax)
mailto:doug.pow...@aei.com
---


___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC

RE: harmonic current on inverters for industrial uses in Japan

2002-09-12 Thread Jim Eichner

Hi Doug:  Please let me know what you find out on this.  I recently came
across a reference to inverters, in searching the JEITA site for harmonic
current limitation standards.  That didn't make sense to me:  an inverter is
a DC-AC converter that has no connection to an AC source and draws no
harmonic current.  The only thing I could think of is that maybe they were
on about harmonic content of the output, not the input.  If so, I hope they
are talking about voltage, because the harmonic content in the output
current will depend upon the nature of the load.

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, September 12, 2002 7:58 AM
To: EMC-PSTC (E-mail)
Subject: harmonic current on inverters for industrial uses in Japan



Hello esteemed colleagues,

I am searching for an English language version of a report writtne in
Japanese, I already have the title translated:

Calculation methods of harmonic current on inverters for industrial uses.
JEM- TR 201


Can enayone help with location of this report in English?


thank you so much,

-doug

---
Douglas E. Powell, Compliance Engineer
Advanced Energy Industries, Inc.
Mail stop: 203024
1626 Sharp Point Drive
Ft. Collins, CO 80525

970.407.6410 (phone)
970-407.5410 (fax)
mailto:doug.pow...@aei.com
---


___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


WAS......RE: Inrush and EN61000-3-3

2002-09-10 Thread Jim Eichner

Could we change the name of this thread please?  I'm not sure I'm done
getting responses on my EN61000-3-3 question and suddenly it's turned into a
thread on NEBS stuff!

Thanks,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: Gary McInturff [mailto:gary.mcintu...@worldwidepackets.com]
Sent: Tuesday, September 10, 2002 11:22 AM
To: Joe Finlayson; John Juhasz; Dorin
Cc: EMC-PSTC - forum
Subject: RE: Inrush and EN61000-3-3



Check out section 9.10 Compatibility with former IBN Equipment with
CBN Currents. I think this more directly relates to the signal connections,
whether or not, they have to be isolated from the equipment chassis until
grounded at the Isolated bonding point. 
I don't think(?) isolated bonding is much used these days. I know we
used to make equipment that keep signals from chassis (grounding the chassis
to the rack) but most of the RBOC's also wanted the ability to make a signal
to chassis ground, and most seemed to be using that connection.
This is one of the more confusing issues, at least to me on the NEBS
specifications. Still not sure I know what it says.
Gary

-Original Message-
From: Joe Finlayson [mailto:jfinlay...@telica.com]
Sent: Tuesday, September 10, 2002 9:03 AM
To: 'John Juhasz'; 'Dorin'
Cc: 'EMC-PSTC - forum'
Subject: RE: Inrush and EN61000-3-3



John  Dorin,

Please clarify as I am not aware of a requirement to isolate Signal
Ground from Frame Ground.  Please reference GR-1089-CORE, Section 9.6.2 as
well.

Thx,


Joe

-Original Message-
From: John Juhasz [mailto:john.juh...@ge-interlogix.com]
Sent: Tuesday, September 10, 2002 11:12 AM
To: 'Dorin'
Cc: 'EMC-PSTC - forum'
Subject: RE: Inrush and EN61000-3-3



Be careful Dorin. For Central Offices, they need to be isolated.


John A. Juhasz

GE Interlogix
Fiber Options Div.
Bohemia, NY 

-Original Message-
From: Dorin [mailto:dorin.op...@alcatel.com]
Sent: Tuesday, September 10, 2002 9:12 AM
Cc: 'EMC-PSTC - forum'
Subject: Re: Inrush and EN61000-3-3



Hi,

I am looking for a comparison, pros and cons, on the signal ground
connected versus not connected to the chassis in a telecom system. Any
help is appreciated.

Thanks,
Dorin



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com

Inrush and EN61000-3-3

2002-09-09 Thread Jim Eichner

Does the flicker standard have requirements that limit one-time events like
inrush current when first powering up a product, or does it just focus on
repetitive events? In short, do we have to limit our inrush current?

Thanks,
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: PFC or Harmonic Current Limitations outside Europe

2002-09-09 Thread Jim Eichner

Quite right John - thanks for catching the slip.

Here's my amended running compilation:
 
- Japan - Has requirements based on the previous rev. of 61000-3-2 (still
has the special waveshape in it) that appear to be guidelines only (ie
voluntary) unless you are a member of JEITA. 

- China - standard is GB17625.1, presently aligned to IEC61000-3-2:1995,
amendment 1 (reflecting EN61000-3-2:A14) is in the works.

- USA - IEEE 519 covers distortion, which is related to harmonic content.
It is a utility standard that doesn't seem likely to get applied to product
approvals.  I was also told that it seems exceedingly unlikely...that the
present edition of IEC 61000-3-2 will get adopted in the US.

- Australia / New Zealand -  I'm told the current edition of IEC 61000-3-2
is being studied, but the level of controversy over it makes adoption
unlikely.

- Korea - moving in this direction
For the forum, here's my amended running compilation.  If anyone has
anything more to add, I'll keep this going for a while.

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Friday, September 06, 2002 6:41 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: PFC or Harmonic Current Limitations outside Europe



I read in !emc-pstc that Jim Eichner jim.eich...@xantrex.com wrote (in
67C475A5ECE7D4118AEC0002B325CAB60176826D@BCMAIL1) about 'PFC or
Harmonic Current Limitations outside Europe' on Fri, 6 Sep 2002:
- China - standard is GB17625.1, presently aligned to
IEC61000-3-2:1995, 
amendment 1 (EN60950:A14) is in the works.


No, that 'amendment 1' is EN61000-3-2:A14. EN 60950 has nothing to do
with it.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: PFC or Harmonic Current Limitations outside Europe

2002-08-30 Thread Jim Eichner

John:  

Re the US:  Is IEEE519 given force in any way?  Is there any agency, body,
or utility that is requiring IEEE519 compliance?

Re Japan:  Do you know the name/number of the trial standard and where I
can find a list of what types of products it applies to?

Thanks,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Tuesday, August 27, 2002 11:54 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: PFC or Harmonic Current Limitations outside Europe



I read in !emc-pstc that Jim Eichner jim.eich...@xantrex.com wrote (in
67C475A5ECE7D4118AEC0002B325CAB6017681D7@BCMAIL1) about 'PFC or
Harmonic Current Limitations outside Europe' on Mon, 26 Aug 2002:

Can anyone provide any information on the requirements for (or lack of) PFC
or harmonic current limitation now or in the future, in the following
areas:

1. Japan

Japan has had a 'trial standard' for some years. It is not the same as
IEC/EN 61000-3-2, but is based on it. It does not apply to everything,
as the EN does.

2. North America (I think I've heard rumours)

There is already IEEE 519. I think it is exceedingly unlikely that USA
will adopt the present edition of IEC 61000-3-2, particularly since it
doesn't claim to apply to 120V 60 Hz systems.

3. Australia / New Zealand

I understand that the current edition of IEC 61000-3-2 is being studied,
but the level of controversy over it makes adoption unlikely.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: PFC or Harmonic Current Limitations outside Europe

2002-08-30 Thread Jim Eichner
Joshua:  Re Japan, I didn't have much luck on the JEITA website.  Can you
give me a specific reference (standard name/number, URL, etc.)?  Also, is
there a list of what types of products this requirement applies to?
 
Thanks,

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

-Original Message-
From: Joshua Wiseman [mailto:jwise...@printronix.com]
Sent: Wednesday, August 28, 2002 8:34 AM
To: 'Jim Eichner'; 'EMC-PSTC - forum'
Subject: RE: PFC or Harmonic Current Limitations outside Europe



Jim, 

When China converted to the CCC approval scheme they adopted the Chinese
version of EN 61000-3-2. 

Japan has a requirement under JEITA to test harmonics at 120V while using an
impedance in line. 

I have heard that Australia and Korea are also moving in this direction. 

Taiwan follows the US for the most part and I have not heard anything in
this arena. 

I am curious to hear the responses you get on this one.  Good luck. 

Regards, 
Josh 

Josh Wiseman 
EMC/Product Safety 
(714) 368-2737 
[ mailto:jwise...@printronix.com mailto:jwise...@printronix.com ] 


-Original Message- 
From: Jim Eichner [ mailto:jim.eich...@xantrex.com
mailto:jim.eich...@xantrex.com ] 
Sent: Monday, August 26, 2002 12:33 PM 
To: 'EMC-PSTC - forum' 
Subject: PFC or Harmonic Current Limitations outside Europe 



Can anyone provide any information on the requirements for (or lack of) PFC 
or harmonic current limitation now or in the future, in the following areas:


1. Japan 
2. North America (I think I've heard rumours) 
3. Australia / New Zealand 
4. Any other location you are aware of where it definitely IS a requirement 

Thanks as always for the group's input. 

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power 
web: www.xantrex.com  http://www.xantrex.com http://www.xantrex.com  
Any opinions expressed are those of my invisible friend, who really exists. 
Honest. 


Confidentiality Notice: This email message, including any attachments, is 
for the sole use of the intended recipient(s) and may contain confidential 
and privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message. 



--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
http://www.ewh.ieee.org/soc/emcs/pstc/  

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
http://ieeepstc.mindcruiser.com/ http://ieeepstc.mindcruiser.com/  
Click on browse and then emc-pstc mailing list 



PFC or Harmonic Current Limitations outside Europe

2002-08-27 Thread Jim Eichner

Can anyone provide any information on the requirements for (or lack of) PFC
or harmonic current limitation now or in the future, in the following areas:

1. Japan
2. North America (I think I've heard rumours)
3. Australia / New Zealand
4. Any other location you are aware of where it definitely IS a requirement

Thanks as always for the group's input.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists.
Honest.


Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


CISPR 16 compliant voltage probe

2002-08-14 Thread Jim Eichner
We bought ours from Solar Electronics, and it was quite cheap if I recall.
Came with insertion loss curves and has worked well.  Their info is
attached.
 
 

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power 
phone:  (604) 422-2546 
fax:  (604) 420-1591 
e-mail:  jim.eich...@xantrex.com 
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 
-Original Message-
From: Tony [mailto:raym...@bellsouth.net]
Sent: Wednesday, August 14, 2002 7:43 AM
To: emc-p...@ieee.org
Subject: 



Hello Group,

I am researching building a CISPR 16 compliant voltage probe as shown in
CISPR 16-1.12.2.

The Insertion loss is mentioned. I have looked into how to measure it and
everything I have found so far uses two power meters. I have one. Is there
an alternative measurement technique that I could employ? 

 

I am researching building it because I have not had any success in finding
one I can rent.  If anyone could point me in the direction of a rental
source I would appreciate that also. 

 

Tony Rayman

Compliance Engineer

Advanced Compliance Solutions

5015 B.U. Bowman DR

Buford, GA 30518

Tele (770) 831 8048

FAX (770) 831 5898

 

---BeginMessage---
---End Message---


Banned Substances in Sweden

2002-08-09 Thread Jim Eichner

We have had a request from a customer to verify a lack of certain substances
in one of our products.  Rather than provide us with a regulatory-based list
of substances, they have provided us with a particular company's proprietary
list of substances it bans (and that company is in no way involved in the
dealings between us and our customer).  

Does anyone know where I can get an official list of what substances Sweden
bans in electronic products?

Thanks as always,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really exists
and contains reams and reams of brominated flame retardants.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Changes to FCC Conducted Limits for Part 15 18

2002-07-24 Thread Jim Eichner

A philosophical .vs practical question:  Why is the FCC doing this?  Is it
harmonization for the sake of harmonization, or are there real-life issues
driving it?  If it's the latter, what sorts of products have susceptibility
issues between 150kHz and 450kHz?  

Thanks,
 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists
but only in the far field.


Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Price, Ed [mailto:ed.pr...@cubic.com]
Sent: Wednesday, July 24, 2002 10:28 AM
To: 'John Barnes'; emc-p...@majordomo.ieee.org
Subject: RE: Changes to FCC Conducted Limits for Part 15  18



Also notice, in the same directory, a newer version from July 7, 2002, at:

http://www.fcc.gov/oet/info/rules/part15/part15_7_22_02.pdf



Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis


-Original Message-
From: John Barnes [mailto:jrbar...@iglou.com]
Sent: Wednesday, July 24, 2002 8:15 AM
To: emc-p...@majordomo.ieee.org
Subject: Changes to FCC Conducted Limits for Part 15  18



EMC-PSTC'ers,
There has been talk for several months about the FCC changing the
conducted emission limits for Part 15 and Part 18 devices.  Well, it is
official.  FCC docket 98-80 was published in the Federal Register on
July 10, 2002- volume 67, number 132, pages 45666-45671, see (all one
URL):
   http://frwebgate1.access.gpo.gov/
   cgi-bin/waisgate.cgi?WAISdocID=38880224794+0+0+0WAISaction=retrieve

FCC Part 15, incorporating the new Section 15.107, may be downloaded
from
   http://www.fcc.gov/oet/info/rules/part15/part15_5_30_02.pdf

This will not be printed in the Code of Federal Regulations (CFR),
downloadable from the National Archives and Records Administration
(NARA) at:
   http://www.access.gpo.gov/nara/cfr/cfr-table-search.html
until spring 2003.

This change probably will not affect products that have been 
marketed in
Taiwan and Japan, because they have already had to meet the 
CISPR limits
for those markets.  But products that are sold only in the 
US/Canada may
be affected, because conducted emissions are now to be tested 
clear down
to 150kHz, versus the former 450kHz lower limit.

The new conducted emission limits are:
*  Mains port on Class B devices:
   -  66dB(uV) quasi-peak and 56dB(uV) average at 0.15MHz, to
  56dB(uV) quasi-peak and 46dB(uV) average at 0.50MHz, decreasing 
  linearly with the logarithm of the frequency.
   -  56dB(uV) quasi-peak and 46dB(uV) average from 0.50MHz to 5MHz.
   -  60dB(uV) quasi-peak and 50dB(uV) average from 5MHz to 30MHz.
*  Mains port on Class A devices:
   -  79dB(uV) quasi-peak and 66dB(uV) average from 0.15MHz to 0.50MHz.
   -  73dB(uV) quasi-peak and 60dB(uV) average from 0.50MHz to 30MHz.

Paragraph 15 of FCC Docket 98-80, Transition Provisions, says that FCC
part 15/18 products may be authorized using the old or the new FCC
limits for two years (until July 10, 2004).  After July 10, 2004, FCC
part 15/18 products must be authorized using the new FCC limits. 
Furthermore, the new limits will apply to all FCC part 15/18 products
that are manufactured or imported after three years (after July 10,
2005).

So for the next two or three years you have a third option for meeting
FCC Part 15/18 requirements:
1.  Meet the old FCC conducted-emission and radiated-emission limits.
2.  Meet CISPR conducted-emission and radiated-emission limits.
3.  Meet CISPR conducted-emission limits and the old FCC radiated- 
emission limits.
John Barnes
dBi Corporation
http://www.dbicorporation.com/


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http

RE: Nema 5-15R sockets

2002-07-22 Thread Jim Eichner

Wow - so it is, and I now have my free copy!

Thanks,

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Robert Johnson [mailto:john...@itesafety.com]
Sent: Monday, July 22, 2002 9:41 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: Nema 5-15R sockets


In fact, soft copy of NEMA WD-6 from www.nema.org is free!!
If only IEC ...

Bob Johnson
ITE Safety
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of
ron_well...@agilent.com
Sent: Monday, July 22, 2002 9:02 AM
To: jim.eich...@xantrex.com; emc-p...@majordomo.ieee.org
Subject: RE: Nema 5-15R sockets


Hello Jim,

By now you have received many replies to your message. However, since
your orientation question has been asked many, many times before in my
neck of the woods, here is what I know regarding your two questions:

1) Not specified in the NEC or the CEC. However, receptacle orientation
is usually determined by either: a) the electrician who installs the
receptacle, by their preference, or b) a localized code or practice. In
some cases, various hospitals have their own requirements for receptacle
installation.

2) Get a copy of NEMA WD-6. It's available electronically (www.nema.org)
and doesn't cost big bucks. Besides, it's a good reference to have for
all North American plug and receptacle configurations.

Regards,
+=+
|Ronald R. Wellman|Voice : 408-345-8229   |
|Agilent Technologies |FAX   : 408-553-2412   |
|5301 Stevens Creek Blvd.,|E-Mail: ron_well...@agilent.com|
|Mailstop 54L-BB  |WWW   : http://www.agilent.com |
|Santa Clara, California 95052 USA|   |
+=+



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Nema 5-15R sockets

2002-07-20 Thread Jim Eichner

Well, I certainly seemed to have launched a popular thread!

Thanks everyone for your input and anecdotes.  I have my answers...

- no regulatory requirement for up or down
- dimensions being faxed to me

Once again, the forum is invaluable!

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Scott Lacey [mailto:sco...@world.std.com]
Sent: Friday, July 19, 2002 2:22 PM
To: Art Michael
Cc: emc-p...@majordomo.ieee.org
Subject: Re: Nema 5-15R sockets



Art and JIm,
One other thing to note: All of the flat (air conditioner type) heavy-
duty cords and extensions I've seen that fit this type socket seem to 
be designed for use with the ground pin at the bottom.

Also, although there is some shock hazard from the partially 
retracted Hot lead with the ground at bottom, when an outlet is 
installed with the ground pin up it is possible to have the ground lead 
disconnect first. If this happens with a product with high (but 
acceptable) leakage a potentially lethal situation exists.

Scott Lacey

On 19 Jul 2002 at 13:59, Art Michael wrote:

 
 Hello Jim,
 
 I don't believe the orientation of the U-ground pin is declared
 anyplace in the NEC. When I recently approached my local AHJ with this
 question he related that it is a matter of custom (locality
 dependent). In this area, central Connecticut, the custom is: 
 
 For commercial/industrial applications, U-Ground topmost
 For household wiring, U-Ground towards the bottom
 
 The rationale offered for the U-Ground topmost; if the plug partially
 separates from the outlet, anything falling into the opening between
 the plug and the outlet will first encounter the grounding pin. (seems
 to me that argument holds whether the use is commercial/industrial or
 household).
 
 Re dimensions of the outlet; send me your fax # and I'll fax you the
 dimensions.
 
 Regards, Art Michael
 
 
   -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --
  |http://www.safetylink.com   |  |
| |  The Safety Link is the most
  comprehensive collection  | |of product safety and standards
  links on the WEB| |Check our latest offer.   
   | |   | |   
 | |  Int'l Product Safety News
  | |   Founded in 1988
   | |   | |   
   P.O.Box 1561 - WWW | |Middletown
  CT 06457-8061 U.S.A. | | Phone: (860) 344-1651   
   Fax: (860) 346-9066  | | email:
  i...@safetylink.com |
   -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --
 
 --- On
 Fri, 19 Jul 2002, Jim Eichner wrote:
 
  
  A couple of questions about our standard North American 120Vac
  socket:
  
  1. Orientation:  We have lots of people in the office here on both
  sides of this one, and I can't find a normative reference in the CEC
  or the NEC. Which is the correct way up when installing a socket
  on a wall - ground pin above the L and N blades, or L and N above
  the ground?  What is the code reference for this requirement, or is
  there none?
  
  2. Dimensions:  Can anybody share the spec's for the dimensions,
  with tolerances, of the line, neutral, and ground blades for this
  configuration? I'm sure it's in the UL and CSA standards but I don't
  want to spend hundreds of $ for a one-time question.  We have no
  on-going need for these standards!
  
  Thanks in advance for your help,
  
  Regards, 
  Jim Eichner, P.Eng. 
  Manager, Engineering Services 
  Xantrex Technology Inc. 
  Mobile Power
  web: www.xantrex.com http://www.xantrex.com 
  Any opinions expressed are accidental.  I have none.
  
  
  Confidentiality Notice: This email message, including any
  attachments, is for the sole use of the intended recipient(s) and
  may contain confidential and privileged information. Any
  unauthorized review, use, disclosure or distribution is prohibited.
  If you are not the intended recipient, please contact the sender by
  reply e-mail and destroy all copies of the original message.
  
  
  
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical

RE: Nema 5-15R sockets

2002-07-19 Thread Jim Eichner

Thanks Bob.  I've also had it pointed out to me that the writing on the
sockets themselves is usually oriented ground-up, and some are even marked
TOP with ground-up orientation.  Seems to be a preference but not a
requirement.

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Robert Johnson [mailto:john...@itesafety.com]
Sent: Friday, July 19, 2002 3:13 PM
To: 'Jim Eichner'
Subject: RE: Nema 5-15R sockets


The NEC does not establish an orientation. Proposals to establish an
orientation have been proposed to the code panel and rejected. See 
http://electrical-contractor.net/ubb/Forum2/HTML/000553.html
for a discussion.

You will find ground up preferred by some to provide protection as
mentioned by Art Michaels. However, you will find many direct plug in
products configured with ground down.

Dimensions for these and twist lock plugs are in NEMA standard WD6-88. 
Sorry, I don't have a copy.

Bob Johnson
ITE Safety
 
-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Jim Eichner
Sent: Friday, July 19, 2002 1:40 PM
To: 'EMC-PSTC - forum'
Subject: Nema 5-15R sockets


A couple of questions about our standard North American 120Vac socket:

1. Orientation:  We have lots of people in the office here on both sides
of
this one, and I can't find a normative reference in the CEC or the NEC.
Which is the correct way up when installing a socket on a wall -
ground
pin above the L and N blades, or L and N above the ground?  What is the
code
reference for this requirement, or is there none?

2. Dimensions:  Can anybody share the spec's for the dimensions, with
tolerances, of the line, neutral, and ground blades for this
configuration?
I'm sure it's in the UL and CSA standards but I don't want to spend
hundreds
of $ for a one-time question.  We have no on-going need for these
standards!

Thanks in advance for your help,

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are accidental.  I have none.


Confidentiality Notice: This email message, including any attachments,
is
for the sole use of the intended recipient(s) and may contain
confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient,
please
contact the sender by reply e-mail and destroy all copies of the
original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Nema 5-15R sockets

2002-07-19 Thread Jim Eichner

Thanks for the reply Art.  I was starting to convince myself that it was
indeed local custom, not code, that determined the orientation.  

I heard another explanation that I find amusing and perhaps practical:  that
with the ground at the bottom it looks too much like a face and children
will be more tempted to play with it, so it should be mounted ground-up!

My fax number is below, and I really appreciate you providing whatever
dimensions you can.  Note that I am interested in the blade and ground pin
dimensions of the male plug, not the female socket, please.

Thanks,

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Art Michael [mailto:amich...@connix.com]
Sent: Friday, July 19, 2002 10:59 AM
To: Jim Eichner
Cc: 'EMC-PSTC - forum'
Subject: Re: Nema 5-15R sockets


Hello Jim,

I don't believe the orientation of the U-ground pin is declared anyplace
in the NEC. When I recently approached my local AHJ with this question he
related that it is a matter of custom (locality dependent). In this area,
central Connecticut, the custom is: 

For commercial/industrial applications, U-Ground topmost
For household wiring, U-Ground towards the bottom

The rationale offered for the U-Ground topmost; if the plug partially
separates from the outlet, anything falling into the opening between the
plug and the outlet will first encounter the grounding pin. (seems to me
that argument holds whether the use is commercial/industrial or
household).

Re dimensions of the outlet; send me your fax # and I'll fax you the
dimensions.

Regards, Art Michael


  -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --
 |http://www.safetylink.com   |  
 ||
 |  The Safety Link is the most comprehensive collection  |
 |of product safety and standards links on the WEB|
 |Check our latest offer. |
 ||
 ||
 |  Int'l Product Safety News |
 |   Founded in 1988  |
 ||
 | P.O.Box 1561 - WWW |
 |Middletown CT 06457-8061 U.S.A. |
 | Phone: (860) 344-1651 Fax: (860) 346-9066  |
 | email: i...@safetylink.com |
  -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --

---
On Fri, 19 Jul 2002, Jim Eichner wrote:

 
 A couple of questions about our standard North American 120Vac socket:
 
 1. Orientation:  We have lots of people in the office here on both sides
of
 this one, and I can't find a normative reference in the CEC or the NEC.
 Which is the correct way up when installing a socket on a wall - ground
 pin above the L and N blades, or L and N above the ground?  What is the
code
 reference for this requirement, or is there none?
 
 2. Dimensions:  Can anybody share the spec's for the dimensions, with
 tolerances, of the line, neutral, and ground blades for this
configuration?
 I'm sure it's in the UL and CSA standards but I don't want to spend
hundreds
 of $ for a one-time question.  We have no on-going need for these
standards!
 
 Thanks in advance for your help,
 
 Regards, 
 Jim Eichner, P.Eng. 
 Manager, Engineering Services 
 Xantrex Technology Inc. 
 Mobile Power
 web: www.xantrex.com http://www.xantrex.com 
 Any opinions expressed are accidental.  I have none.
 
 
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list

Nema 5-15R sockets

2002-07-19 Thread Jim Eichner

A couple of questions about our standard North American 120Vac socket:

1. Orientation:  We have lots of people in the office here on both sides of
this one, and I can't find a normative reference in the CEC or the NEC.
Which is the correct way up when installing a socket on a wall - ground
pin above the L and N blades, or L and N above the ground?  What is the code
reference for this requirement, or is there none?

2. Dimensions:  Can anybody share the spec's for the dimensions, with
tolerances, of the line, neutral, and ground blades for this configuration?
I'm sure it's in the UL and CSA standards but I don't want to spend hundreds
of $ for a one-time question.  We have no on-going need for these standards!

Thanks in advance for your help,

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are accidental.  I have none.


Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Conductive Conformal Coatings for reducing PCB Emissions

2002-07-03 Thread Jim Eichner

Has anyone ever used this technology on a pcb that was required to pass
agency creepage and clearance requirements?  Which agency was involved, and
how did they handle it?

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Aschenberg, Mat [mailto:matt.aschenb...@echostar.com]
Sent: Wednesday, July 03, 2002 9:45 AM
To: 'Chris Chileshe'; emc-p...@ieee.org
Subject: RE: Conductive Conformal Coatings for reducing PCB Emissions



Chris, 
They way it was described to me...
The conformal coating would encase the board, creating a sort of shield. 

Understandably, care is taken to prevent shorting of circuits.
Whoever designed the technology has certainly dealt with those concerns. 
Mat 

 -Original Message-
 From: Chris Chileshe [SMTP:chris.chile...@ultronics.com]
 Sent: Wednesday, July 03, 2002 9:22 AM
 To:   emc-p...@ieee.org
 Subject:  RE: Conductive Conformal Coatings for reducing PCB Emissions
 
 
 Mat,
 
 Can we assume you mean conductive spray coatings for plastic
 caseworks? Wouldn't a conductive conformal coating would short 
 out all the components on the PCB? Or is a two-pass technology
 with the ordinary insulating coating over the components and a 
 conductive layer on the outside?
 
 Awaiting your clarification.
 
 - Regards
 
 - Chris 
 
 -Original Message-
 From: Aschenberg, Mat [SMTP:matt.aschenb...@echostar.com]
 Sent: Tuesday, July 02, 2002 3:36 PM
 To:   emc-p...@ieee.org
 Subject:  Conductive Conformal Coatings for reducing PCB Emissions
 
 
 Hi All,
 A while back there was a push to use conductive conformal 
 coatings for PCB emissions. Does anyone know if the 
 technology still exists and if so who makes it??
 
 Thanks
 
  
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 
 
 This e-mail has been scanned for all viruses by Star Internet. The
 service is powered by MessageLabs. For more information on a proactive
 anti-virus service working around the clock, around the globe, visit:
 http://www.star.net.uk
 
 
 
 This e-mail has been scanned for all viruses by Star Internet. The
 service is powered by MessageLabs. For more information on a proactive
 anti-virus service working around the clock, around the globe, visit:
 http://www.star.net.uk
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard

RE: ESAs certification to 95/54/EC

2002-06-24 Thread Jim Eichner
We have been talking to the UK's Vehicle Certification Agency regarding the
Automotive EMC Directive (AEMCD).  Their US office website is attached, and
the contact I've got is Mark Rushton. 
 
There are labs in the US with accreditation to do this testing.  We're going
to use Acme Testing in Acme Washington (website also attached).

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power 
phone:  (604) 422-2546 
fax:  (604) 420-1591 
e-mail:  jim.eich...@xantrex.com 
web: www.xantrex.com 

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 
-Original Message-
From: Fang Han [mailto:f...@qualcomm.com]
Sent: Monday, June 24, 2002 10:45 AM
To: emc-p...@majordomo.ieee.org
Subject: ESAs certification to 95/54/EC


Hi Colleagues,

It looks like all products for vehicle application, even they have been
certified to EMC Directive or RTTE Directive, must be certified to 95/54/EC
(vehicle EMC directive) before Oct 1, 2002.  It seems to me that the
certification route for vehicle EMC directive is different with EMC
directive or RTTE directive certification.   I am looking for an accredited
lab/body that is authorized to certify ESAs products to 95/54/EC.  I wonder
if all these labs/bodies are located in Europe or there are some in USA.  I
understand that these labs/bodies should be authorized by the Ministry of
Transportation of a EU member state.  A certification done by such a lab
will be accepted by all other EU member states.

I appreciate it very much if someone familiar with this can shed some light.


Thanks a lot,

Fang




Vehicle Certification Agency.zlt
Description: Binary data


Acme Testing.zlt
Description: Binary data


RE: Coaxial Switches - use with spectrum analyzer and gear?

2002-05-23 Thread Jim Eichner

Actually we use the clamp-on RF probes up to a few hundred MHz (we don't
manufacture anything requiring compliance above 1GHz), but since it's only a
trouble-shooting precompliance setup, I tend to agree that we can stay with
moderate quality and price and parts.  

I love the idea of using an IEEE488 driver and automating the testing, and
certainly the periodic maintenance check is good advice.

Thanks everyone, 


Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Thursday, May 23, 2002 12:54 PM
To: Price, Ed; emc-p...@majordomo.ieee.org
Subject: Re: Coaxial Switches - use with spectrum analyzer and gear?



I agree with Ed that there is no problem using switches, but I don't see the
need for 18 GHz, all the measurements you describe stop at 30 MHz.  I don't
see why Mini-Circuits would be out-of-line here, and you can check losses by
using a tracking generator or known signal sources.

--
From: Price, Ed ed.pr...@cubic.com
To: emc-p...@majordomo.ieee.org
Subject: RE: Coaxial Switches - use with spectrum analyzer and gear?
Date: Thu, May 23, 2002, 11:53 AM

-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Wednesday, May 22, 2002 12:55 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: Coaxial Switches - use with spectrum analyzer and gear?



In our pre-compliance lab, we've got a pair of LISN's, a LISN-mate type
thing that I'll call a DMRN (DM rejection network), a
transient limiter,
some clamp-on RF current probes, an amplifier, the front end of the
analyzer, and a 50 ohm terminator.  All this gear is connected and
unconnected a hundred times a day when we're deep into
trouble-shooting, and
I'm sick of doing up and undoing coax connectors.  I don't
trust push-on
coax connectors.

What I envision is a system with a few of these coax switches
in it. The
analyzer input would go to a switch that selected either the
amp (used only
with the clamp-on probes) or the transient limiter (used with
the LISN's).
The limiter input would go to a switch that selected between
the output of
the DMRN or the Line LISN or the Neutral LISN.  Etc.  You get the idea.

Is there anything to stop me from using coax switches with suitable CW
power, insertion loss, and frequency spec's? Am I headed for
trouble if I
have 2 or 3 of these switches in the signal path, due to cumulative
insertion loss?

Thanks for your feedback,

Regards,
Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
web: www.xantrex.com http://www.xantrex.com
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



 Jim:

 There's no reason why you can't implement the switching system you
 described. The only concern is that you use really good parts. (Your
 spectrum analyzer likely has a couple of internal relays in its signal
 path.) Since you likely need to measure up to about 5 GHz, I would use
 components rated for up to 18 GHz. This is not the place to skimp on cost.
 Don't use Dow-Key relays with SO239 UHF connectors; go with something like
 Agilent relays with SMA connectors. Connect the internal paths with
 semi-rigid solid-wall coax, and use a good grade of flexible external coax
 cabling too. If your system is computer-controlled, you can use something
 like an IEEE488 Relay Driver interface to automate the switching
functions.

 Your lab procedures should be amended to include some type of periodic
 verification of the loss along all signal paths.

 Regards,

 Ed

 Ed Price
 ed.pr...@cubic.com
 Electromagnetic Compatibility Lab
 Cubic Defense Systems
 San Diego, CA  USA
 858-505-2780  (Voice)
 858-505-1583  (Fax)
 Military  Avionics EMC Services Is Our Specialty
 Shake-Bake-Shock - Metrology - Reliability Analysis



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All

RE: Coaxial Switches - use with spectrum analyzer and gear?

2002-05-23 Thread Jim Eichner

In our pre-compliance lab, we've got a pair of LISN's, a LISN-mate type
thing that I'll call a DMRN (DM rejection network), a transient limiter,
some clamp-on RF current probes, an amplifier, the front end of the
analyzer, and a 50 ohm terminator.  All this gear is connected and
unconnected a hundred times a day when we're deep into trouble-shooting, and
I'm sick of doing up and undoing coax connectors.  I don't trust push-on
coax connectors.

What I envision is a system with a few of these coax switches in it. The
analyzer input would go to a switch that selected either the amp (used only
with the clamp-on probes) or the transient limiter (used with the LISN's).
The limiter input would go to a switch that selected between the output of
the DMRN or the Line LISN or the Neutral LISN.  Etc.  You get the idea.

Is there anything to stop me from using coax switches with suitable CW
power, insertion loss, and frequency spec's? Am I headed for trouble if I
have 2 or 3 of these switches in the signal path, due to cumulative
insertion loss?

Thanks for your feedback,

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.

Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.



-Original Message-
From: richwo...@tycoint.com [mailto:richwo...@tycoint.com]
Sent: Tuesday, May 21, 2002 7:45 AM
To: emc-p...@majordomo.ieee.org
Subject: Coaxial Switches



Other than Adilent, what are some other sources for low power (1W) and high
power (100W) coaxial switches for frequencies up to 2 GHz?

Richard Woods
Sensormatic Electronics
Tyco International


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Let's change the topic to something more descriptive Re: stun guns onaircraft

2002-05-08 Thread Jim Eichner

Let's just return to the main subject matter of this forum, and ban further
discussion of firearm philosophy.  This is an un-moderated forum, so it is
up to us to be respectful of the rules and intent of the forum, and of each
other's time.  These long off-topic threads are a major disappointment.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



-Original Message-
From: Gary McInturff [mailto:gary.mcintu...@worldwidepackets.com]
Sent: Tuesday, May 07, 2002 1:55 PM
To: Penny D. Robbins; emc-p...@majordomo.ieee.org
Subject: RE: Let's change the topic to something more descriptive Re:
stun guns onaircraft



I also find it very easy to set up a rule that throws e-mail from specific
names/destinations straight into the electronic trashcan. Put it to good use
on this once promising but now useless thread.
Gary

-Original Message-
From: Penny D. Robbins [mailto:probb...@telcordia.com]
Sent: Tuesday, May 07, 2002 10:26 AM
To: emc-p...@majordomo.ieee.org
Subject: Let's change the topic to something more descriptive Re: stun
guns onaircraft



Folks-
For those of us who care to know the real info about the original topic -
stun guns and the RF problems they cause on aircraft, how about changing
your subject line. Let's have everyone who wants to give their opinions
about who should and shouldn't own guns and what the real problem is with
society change the subject line to something more reflective of the topic
at hand. How about: Guns - Pro or Con?
It certainly would make reading though and filtering out the information we
want to see easier.
Penny
- Forwarded by Penny D. Robbins/Telcordia on 05/07/02 01:20 PM -
 

Robert Wilson

robert_wilson@tTo:
emc-p...@majordomo.ieee.org   
irsys.com  cc: (bcc: Penny D.
Robbins/Telcordia) 
Subject: RE: stun guns on
aircraft
05/07/02 12:41

PM

Please respond

to Robert

Wilson

 

 







Crime rates drop drastically in nations where guns are freely owned by
the PUBLIC?? I suppose this explains why the US has a murder rate some
10 to 20 times that of western Europe, and whose extreme violent crime
rates make it a pariah in the eyes of so many other nations? And where
do you think the criminal approaching your wife with a gun managed to
get a gun in the first place? Could it be because he lives in a country
that believes owning a gun should be a citizen's right? Nah! Couldn't
possibly be a connection!

Reminds me of a cartoon I once saw, where Uncle Sam is pointing a gun at
himself and has just managed to shoot another hole through his head. The
caption is Damn! It did it again! I wonder what causes that?

Ah, well, what else can one expect from yet another proud member of the
NRA. Certainly not rational thinking when it comes to playing with toys
that go bang.

I'll get off my soap box now.

Bob Wilson
TIR Systems Ltd.
Vancouver.

-Original Message-
From: Sam Davis [mailto:sda...@ptitest.com]
Sent: May 7, 2002 6:51 AM
To: Gert Gremmen; Pettit, Ghery; 'Ted Rook'; 
Subject: RE: stun guns on aircraft


This has nothing to do with EMC or Product safety, but with personal and
public safety.

I'm with Ghery.  Gert, your misrepresentation of his statement is
ludicrous.
Statistics bear this out.  Crime rates drop drastically in nations where
guns are freely owned by the PUBLIC.  Look at Australia.  The gov't took
the
gun ownership rights away, and violent crime rose horribly.

Guns are not only offensive weapons, but defensive weapons as well.  If
some
criminal approaches your wife with a gun, would you prefer her to have a
pistol, or a whistle?

What do you want your cops to defend your streets with?  What about your
military, to guard your ability to go to work, make a living, support
your
family, without having to worry if you'll be a captive prisoner of war,
or
worse?  What about the security force at your airport?

Guns even the playing field.

When you outlaw guns, only outlaws have guns.  Law abiding citizens turn
them in, and can no longer defend their homes with the NECESSARY force.
Fortunately, I live in a locale where gun ownership is not only allowed,
but
almost expected.  Statistically, there are more guns than people per
household.  There is also a very low rate of home invasion.
Since concealed carry permits have been issued, all violent crimes have
dropped.

Hijackers take planes because law-abiding travelers are not packing
heat.

I own multiple guns, legally, and I pray I never have to fire them in
self
defense

RE: Using PCB traces as transient voltage suppressor

2002-02-20 Thread Jim Eichner

Isn't the other issue here that creepage and clearance are normally required
between live parts and from live parts to ground?  

If you buy components, you can go get approved components.  

If you do it yourself on the board, you're going to invoke all kinds of
extra approvals work - evaluating your home-made spark gap to the standard
for transient voltage suppressors, or your home made fuse to the standard
for supplemental fuses, or...

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.




-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Wednesday, February 20, 2002 11:16 AM
To: chris.maxw...@nettest.com
Cc: gab...@simex.ca; emc-p...@majordomo.ieee.org
Subject: Re: Using PCB traces as transient voltage suppressor






Hi Chris:


   1.  Can anyone else verify the breakdown voltage of 1Megavolt/meter for
   air?  Seems different than what I can remember; but I don't have a
   reference handy.  It also seems to me that this would be very dependent
   upon humidity and pollution degree?

In a separate message, I will send you the air
breakdown voltage curves from IEC 664.

Humid air has a very slightly higher electric
strength than dry air.  (Water vapor, a gas,
has quite different properties than water as 
a liquid.)  I believe air temperature has more 
effect on electric strength than does humidity.

Pollution affects the electric strength of
the scheme because it is deposited on the 
electrodes.  This tends to reduce the electric 
strength between the two electrodes.  This is 
a larger effect than humidity.

The biggest factor affecting the electric 
strength of air is air pressure.  Pollution,
temperature, and humidity have relatively 
low effects.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: SV: Generic emissions - EN 61000-6-3

2002-02-01 Thread Jim Eichner

Thanks to Enci, and the link he provided, I have my answer, and perhaps it
will cut through some of the semantics discussion, by introducing the one
term that seems to really count in discussing the standards route:
presumption of conformity.

The New Approach guideline seems pretty clear:  a standard is NOT considered
to provide a presumption of conformity until it has been published in the
OJ.

That tells us 2 things:

1. Until it is published in the OJ it does not satisfy the standards route
to compliance.  You can use it but you're not within the bounds of the
standards route.

2. If a single standard applicable to your equipment is published in the OJ
without limitations, it provides presumption of conformity for your
equipment.  You do not need to use any other standard, even if others that
appear also to cover your equipment have been published in the OJ.  

Comments?

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: Brian Jones [mailto:e...@brianjones.co.uk]
Sent: Friday, February 01, 2002 1:01 AM
To: John Woodgate; emc-p...@majordomo.ieee.org
Subject: Re: SV: Generic emissions - EN 61000-6-3



John

We will have to agree to disagree on the semantic issues

BUT I will not accept your putting words in my mouth on interpretations of
the current and draft EMC Directives.

For the record, I deliberately used the word apply which is the wording of
the current Directive.  Apply does not necessarily mean test.

I did not mention the draft revision.

Brian Jones
EMC Consultant and Competent Body Signatory



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: SV: Generic emissions - EN 61000-6-3

2002-01-30 Thread Jim Eichner

My question should have been stated more clearly - my apologies.

If you are using the standards route to compliance, what determines which
standards you MUST use?  Are we obligated to apply all applicable EN's that
are published, regardless of whether or not they have appeared in the OJ, or
are we only obligated to apply all EN's that have been published in the OJ?

Related questions:

- If more than one standard seems to apply, do you have to use all of them
in order to satisfy the standards route, or is one sufficient?

- If we are obligated to apply all applicable EN's that are published,
regardless of whether or not they have appeared in the OJ, how the hell are
we supposed to know those standards even exist?!?!  The Europa site's lists
of standards that are published in the OJ as pertaining to the various New
Approach directives are the tool I count on as coming from an official
source and being accurate and up to date.  If we have to apply EN's that
haven't been published in the OJ, where is an equivalent exhaustive list,
how official is it, and how up to date is it?  

Thanks,

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: Allen, John [mailto:john.al...@uk.thalesgroup.com]
Sent: Wednesday, January 30, 2002 12:59 AM
To: 'Jim Eichner'; emc-p...@majordomo.ieee.org
Subject: RE: SV: Generic emissions - EN 61000-6-3


Hi Folks

To answer Jim's point: 

LVD Annex IV Internal Production Control states:

1) Internal production control is the procedure whereby the manufacturer or
his authorized representative established within the Community, who carries
out the obligations laid down in point 2, ensures and declares that the
electrical equipment satisfies the requirements of this Directive that apply
to it. The manufacturer or his authorized representative established within
the Community must affix the CE marking to each product and draw up a
written declaration of conformity. 

2) The manufacturer must establish the technical documentation described in
point 3 and he or his authorized representative established within the
Community must keep it on Community territory at the disposal of the
relevant national authorities for inspection purposes for a period ending at
least 10 years after the last product has been manufactured.

3) Technical documentation must enable the conformity of the electrical
equipment to the requirements of this Directive to be assessed. It must, as
far as relevant for such assessment, cover the design, manufacture and
operation of the electrical equipment. It must include: 
a general description of the electrical equipment,

- conceptual design and manufacturing drawings and schemes of components,
sub-assemblies, circuits, etc.,

- descriptions and explanations necessary for the understanding of said
drawings and schemes and the operation of the electrical equipment,

- a list of the standards applied in full or in part, and descriptions of
the solutions adopted to satisfy the safety aspects of this Directive where
standards have not been applied,
(and so on)

The last item clearly allows a solution that does not involve full - or even
partial compliance - with standards may be acceptable provided that it
satisfies the essential safety aspects of the Directive.

Thus strict compliance with harmonised standards is not obligatory under an
LVD self-declaration process. 

However, bear in mind that compliance with harmonised standards does bring a
presumption of conformity - and most people would thus not stray far from
the standards route.

John Allen
Thales 
Bracknell, UK

-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: 29 January 2002 20:11
To: emc-p...@majordomo.ieee.org
Subject: RE: SV: Generic emissions - EN 61000-6-3



It may be applied, but MUST it be applied?  Does the OJ not still provide
force to the use of the standard, or is that only in the EMC Directive?

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: richwo...@tycoint.com [mailto:richwo...@tycoint.com]
Sent: Tuesday, January 29, 2002 9:49 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: SV: Generic emissions - EN 61000-6-3



As long as we are getting picky, let's don't forget that the Directives
don't have a harmonized definition of what harmonized means. The defintion
in the LVD does not include the need to be referenced in the OJ. Publication
is for information only. Thus, a CENELEC safety standard may be applied as
soon as it is ratified and presuption of conformity to the essential
requirements is provided.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Brian Jones [mailto:e

RE: SV: Generic emissions - EN 61000-6-3

2002-01-29 Thread Jim Eichner

It may be applied, but MUST it be applied?  Does the OJ not still provide
force to the use of the standard, or is that only in the EMC Directive?

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: richwo...@tycoint.com [mailto:richwo...@tycoint.com]
Sent: Tuesday, January 29, 2002 9:49 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: SV: Generic emissions - EN 61000-6-3



As long as we are getting picky, let's don't forget that the Directives
don't have a harmonized definition of what harmonized means. The defintion
in the LVD does not include the need to be referenced in the OJ. Publication
is for information only. Thus, a CENELEC safety standard may be applied as
soon as it is ratified and presuption of conformity to the essential
requirements is provided.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Brian Jones [mailto:e...@brianjones.co.uk]
Sent: Tuesday, January 29, 2002 9:23 AM
To: John Woodgate; emc-p...@majordomo.ieee.org
Subject: Re: SV: Generic emissions - EN 61000-6-3



John, and everyone

It is not true that all ENs are harmonised.  The term, in this context,
means specifically ENs which have been selected as relevant standards under
one or more directives, and listed as such in the Official Journal.  Thus,
for example, basic standards are not harmonised.

EN 61000-6-3, as a generic standard, will be listed in the OJ, but it is not
in the current list published on 5 April 2001 as amended on 26 July 2001.
It was published in October 2001 and will supersede EN 50081-1 on a date
(the doc) which will be published when it is listed in the OJ.  This may
be the dow published in the front of the EN (1 July 2004) or may be a
different date decided by the Commission.

Note that there are differences between the IEC and EN versions.


The following is an extract from the Commission's website

http://europa.eu.int/comm/enterprise/newapproach/standardization/harmstds/vo
rwort.html

which explains in detail the extra requirements for harmonised standards.


---
The New Approach directives are supported by harmonised standards which
play a significant role in ensuring their application. Such standards have
first the characteristics inherent to European Standards :

The standards (typically EN, ETSs) are drafted by one of three European
Standard Organisations (CEN,CENELEC, ETSI)

The work is based on consensus

Standards are adopted after a public inquiry with the national votes based
on corresponding weighting features

Standards remain voluntary but their transposition into national standards
and the withdrawal of diverging national standards is mandatory according to
the internal rules of the European Standards Organisations.

Within the context of the New Approach additional conditions are
superposed to the European Standards to cover the specific role of
harmonised standards :

The Commission issues a standardisation mandate according to the procedure
of Directive 98/34/EC (consolidating Directive 83/189/EEC)

The standards are developed in taking due account of the essential
requirements

The reference of the standard is published in the Official Journal with the
indication of the Directive for which the presumption of conformity should
apply



Best wishes

Brian Jones
EMC Consultant and Competent Body Signatory




- Original Message -
From: John Woodgate j...@jmwa.demon.co.uk
To: emc-p...@majordomo.ieee.org
Sent: Tuesday, January 29, 2002 10:46 AM
Subject: Re: SV: Generic emissions - EN 61000-6-3



 I read in !emc-pstc that am...@westin-emission.no wrote (in LFENJLPMMJB
 mhpeibnilaehgccaa.am...@westin-emission.no) about 'SV: Generic
 emissions - EN 61000-6-3', on Tue, 29 Jan 2002:

 AFAIK EN61000-6-3 is not harmonized yet.

 ALL ENs are AUTOMATICALLY harmonized. I expect you mean that it may not
 have been 'notified' in the OJEC. I think it has.

 I have a problem to access the
 CENELEC web in order to check the current status of this standards.
 I have a copy of CISPR/CEI-IEC 1000-6-3:1996,

 Really? Then why have you not given the reference as '61000-6-3'?

 but I don't know if this issue
 is the latest version because the IEC site is also down for the moment.
In
 this version they still describe 30-1000MHz radiated emission (same
limits
 as in 81-1) and 0.15-30MHz conducted emission (same limits as in 81-1).

 That IS the latest (and only) issue.
 

 --
 Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk
 After swimming across the Hellespont, I felt like a Hero.
 PLEASE do NOT copy news posts to me by E-MAIL

RE: CSA labeling requirements to EN61010-1 (deviation)

2002-01-25 Thread Jim Eichner

My understanding is that CSA is content with a date, a date-code, or a
date-traceable serial number.  The traceability of the serial number IS
allowed, unlike UL, to rely on the manufacturer's records.
 
Does anyone disagree?
 
Thanks,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power 
phone:  (604) 422-2546 
fax:  (604) 420-1591 
e-mail:  jim.eich...@xantrex.com 
web: www.xantrex.com 

 
-Original Message-
From: jsarell...@tuvam.com [mailto:jsarell...@tuvam.com]
Sent: Friday, January 25, 2002 11:46 AM
To: emc-p...@majordomo.ieee.org
Subject: CSA labeling requirements to EN61010-1 (deviation)



Hello Group, 

Does anyone know if the date of manufacturing is required to be in the label
of the equipment? I remember having seen this before but I don't know if
this is still the case. Asking a colleage, he said that it is not neccesary?
Any feedback is appriciated. Thank you in advance,

Regards, 

Jorge Sarellano 
TUV PRODUCT SERVICE 
Compliance Engineer 
Phone 408-919-3744 
Fax 408-919-0585 

Have you visited http://www.tuvam.com http://www.tuvam.com  


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: marine equipment

2002-01-18 Thread Jim Eichner

Quite right - it works well and I now have the text including the tables!

Thanks,

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



-Original Message-
From: h.knud...@niros.com [mailto:h.knud...@niros.com]
Sent: Friday, January 18, 2002 1:06 AM
To: jim.eich...@xantrex.com; emc-p...@majordomo.ieee.org
Subject: SV: marine equipment



Hello Jim,
Since 01/01/2002 it is possible to receive copies of old OJ in TIFF format
at no cost - I think back to 1989 and from 1998 also in PDF format.
Try it! http://europa.eu.int/eur-lex/en/search/search_lif.html


Best regards

Helge Knudsen
Test  Approval manager
Niros Telecommunication
Hirsemarken 5
DK-3520 Farum
Denmark
Tel +45 44 34 22 51
Fax +45 44 99 28 08
email h.knud...@niros.com

-Oprindelig meddelelse-
Fra: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sendt: 18. januar 2002 01:04
Til: 'Kim Boll Jensen'; EMC-PSTC
Emne: RE: marine equipment


I believe the answer is that the Marine Equipment Directive (96/98/EC) is
not a New Approach directive. Rather than the mechanism you're used to, the
directive and its amendment(s) contain direct references to standards.

Have a look at http://europa.eu.int/eur-lex/en/lif/dat/1998/en_398L0085.html
and you'll see Appendix A1 that would list standards if it weren't for the
fact that the Europa site seems to always blank out tables.  I'm not sure if
it's possible to get a free copy of the full text, including the tables, on
the internet.  Does anyone know?

For more info on this directive, go to the Europa site and search on
96/98/EC.


Thanks,

 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



-Original Message-
From: Kim Boll Jensen [mailto:kimb...@post7.tele.dk]
Sent: Thursday, January 17, 2002 1:54 PM
To: EMC-PSTC
Subject: marine equipment


Hi all

Why doesn't marine equipment under 96/98/EC have a page on:

http://europa.eu.int/comm/enterprise/newapproach/standardization/harmstds/re
flist.html

with more details as the other directives. Is there another place on the
Web where I can get more details about this directive ?

Best regards,

Kim Boll Jensen


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: marine equipment

2002-01-18 Thread Jim Eichner
I believe the answer is that the Marine Equipment Directive (96/98/EC) is
not a New Approach directive. Rather than the mechanism you're used to, the
directive and its amendment(s) contain direct references to standards.

Have a look at http://europa.eu.int/eur-lex/en/lif/dat/1998/en_398L0085.html
and you'll see Appendix A1 that would list standards if it weren't for the
fact that the Europa site seems to always blank out tables.  I'm not sure if
it's possible to get a free copy of the full text, including the tables, on
the internet.  Does anyone know?

For more info on this directive, go to the Europa site and search on
96/98/EC.


Thanks,

 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



-Original Message-
From: Kim Boll Jensen [mailto:kimb...@post7.tele.dk]
Sent: Thursday, January 17, 2002 1:54 PM
To: EMC-PSTC
Subject: marine equipment


Hi all

Why doesn't marine equipment under 96/98/EC have a page on:

http://europa.eu.int/comm/enterprise/newapproach/standardization/harmstds/re
flist.html

with more details as the other directives. Is there another place on the
Web where I can get more details about this directive ?

Best regards,

Kim Boll Jensen



EUR-Lex Community legislation in force - Document 398L0085.url
Description: Binary data


RE: EN50091-2:1995

2002-01-11 Thread Jim Eichner

That is the correct version of the standard as far as I know, and I agree it
does not require application of the 801-5 surge immunity requirements.  I
too find that surprising, since surge is one of the most basic and
longest-standing immunity considerations, and real life problems occur if
it's ignored.
 
Regardless of the standard's content, however, the customer can of course
demand whatever they want, and you can voluntarily do surge testing too.  It
may cover you if and when EN50091-2 is reissued, at which time it will
likely add the surge requirement, along with 316 other immunity tests you
and I have never even heard of.

Regards, 
Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
web: www.xantrex.com  http://www.xantrex.com http://www.xantrex.com/  
Any opinions expressed are those of my invisible friend, who really exists.
Honest. 

-Original Message-
From: Sam Wismer [mailto:swis...@bellsouth.net]
Sent: Friday, January 11, 2002 7:06 AM
To: EMC Forum
Subject: EN50091-2:1995



Hi all,

I am reviewing EN50091-2:1995 to determine the immunity requirements for UPS
systems.  According to the harmonized list, this is the correct version of
the standard under the EMCD.  It calls for radiated emissions, IEC 801-2, -3
and -4.  It then says 801-5 is under consideration.  Our customer is
requesting 801-5, but based on how I read the standard, it is not required
at this time.  Could that be true?   

 

 

Kind Regards,

 

 

Sam Wismer

Engineering Manager

ACS, Inc.

 

Phone:  (770) 831-8048

Fax:  (770) 831-8598

 

Web:  www.acstestlab.com

 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Thermal effects on EMC and Earth Leakage

2001-12-17 Thread Jim Eichner

Have a look at the manufacturer's data sheets for the capacitors, and you'll
see spec's or graphs indicating the % capacitance change vs. temperature.
This can be substantial for ceramic cap's in particular.  I don't know how
much of an effect it is for the typical film-type X and Y cap's, but that is
likely the source of the change in leakage current.  

Keep in mind that the EMC performance of a SMPS may be related to many
factors, not just X or Y capacitor performance.  There are often capacitors
located further inside the product that are not X or Y types (and aren't
required to be) yet serve an EMC-reduction function, that could be ceramic
types with significant value change vs. temperature. 

There will also be temperature-related changes in electrolytic filter cap's,
magnetic components, snubbers, the power semiconductors themselves, etc.
Many of these changes may seem subtle in absolute value, but given the
impact that parasitics have on EMC, the change could make a big difference.

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: duncan.ho...@snellwilcox.com [mailto:duncan.ho...@snellwilcox.com]
Sent: Monday, December 17, 2001 7:59 AM
To: emc-p...@majordomo.ieee.org
Subject: Thermal effects on EMC and Earth Leakage



Group.
I am interested to find out peoples opinions on a particular trend we've
seen time and time again on most switch mode PSU's. It seems that once a PSU
is
warm its earth leakage decreases and its EMC emission performance decreases
(i.e. it gets noisier). This would suggest that there is some sort of
thermal
effect, probabaly in the Y caps, that reduces their capacitance.

Has anyone done any work in this area or can anyone explain the physics of
this
change. Is it as simple as expansion of the dielectric or is it more
complicated
than this? Any thoughts or opinions would be greatly recieved. 

Many thanks in advance,

Duncan Hobbs


--
The contents of this communication are confidential to the normal user of
the email address to which it was sent.  If you have received this email
in error, any use, dissemination, forwarding, printing or copying of this
email is strictly prohibited.  If this is the case, please notify the
sender and delete this message.
-- 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: ULC vs. CUL

2001-11-13 Thread Jim Eichner

Perhaps they can reply if they are monitoring this forum, but I'll give it a
shot...

ULC is Underwriters Laboratories of Canada, and while they do product
approvals, they generally in the past have not done the sort of product
safety work that UL does.  ULC has focussed more on building products for
fire safety - things like fire doors, fire extinguishers, gas burning
appliances, etc.  Their approval mark looks much like the UL listing mark,
but it's ULC, with the C inside the circle.

The CUL mark has the C outside the circle, with the normal UL listing
mark inside the circle, and maybe a US outside the circle as well.  This
mark is used by UL for product safety approvals where it needs to be made
clear whether the requirements used were only US ones (read UL standards),
only Canadian ones (CSA standards), or both.  Normally where it is only the
UL standards, they will just use the normal UL mark without either the C or
the US.  When CSA requirements are included, the C(UL)US mark is used to
make it clear that both country's requirements were met.  If they truly are
approving only to the CSA requirements, the C(UL) mark would be used without
the US.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: geor...@lexmark.com [mailto:geor...@lexmark.com]
Sent: Tuesday, November 13, 2001 12:47 PM
To: emc-p...@ieee.org
Subject: Re: ULC vs. CUL





There is a UL mark acceptable for the U.S.
There was a c-UL mark, acceptable to both Canada and the U.S.
The more correct mark from UL for the c-UL mark is now the
c-UL-us mark, i.e. circled UL with small c outside lower left of
circle and small us outside lower right of circle.

I have never heard any of these referred to as a ULC mark.

George Alspaugh




burchj%andovercontrols@interlock.lexmark.com on 11/13/2001 03:18:12 PM

Please respond to burchj%andovercontrols@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  ULC vs. CUL

Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?
Your help is always appreciated.

Thanks,
Joe

Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555  x335
(978)-470-3615  Fax





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: skinny power cords.

2001-10-25 Thread Jim Eichner

Got it - thanks for the explanation.  

Jim 


-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Thursday, October 25, 2001 1:58 PM
To: jim.eich...@xantrex.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: skinny power cords.





Hi Jim:


   Thanks Rich:  I suspect you're right. Isn't that mechanism exactly what
the
   tracking index tests are meant to address?  I thought that any
UL-approved
   wiring device like this would have a material that is designed to resist
   tracking, hence my speculation that contamination might be involved.  

No, I believe the UL tracking index tests do not address 
the scenario I described.

My scenario starts with heating the insulating material
to the point where it begins to pyrolyze, i.e., decompose
by heat alone.

The UL tracking index test starts with a drop of saline
solution to provide a resistive path on the surface of
the plastic insulator.  The micro-arcs occur in the saline 
solution.

In my scenario, pyrolysis, not pollution, leads to the 
micro-arcs.  

So, I don't believe the tracking index is necessarily a
predictor of tracking due to pyrolysis.

I could be wrong...


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



RE: skinny power cords.

2001-10-25 Thread Jim Eichner

Thanks Rich:  I suspect you're right. Isn't that mechanism exactly what the
tracking index tests are meant to address?  I thought that any UL-approved
wiring device like this would have a material that is designed to resist
tracking, hence my speculation that contamination might be involved.  

I guess there are a few more comments to be made here...

1. From what I know, the tracking index tests are horribly non-repeatable
and are therefore somewhat meaningless.

2. The standards for plug caps and for multi-taps may not refer to UL746 and
may not have any of their own requirements for tracking index of insulation.


3. We could take this as evidence that even compliance with the tracking
index requirements doesn't prevent carbonization of the material where
there's a high temperature heat source involved.

There are lots of people who unplug anything they are not actively using. I
guess it's not such a paranoid practice!

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.




-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Thursday, October 25, 2001 12:14 PM
To: jim.eich...@xantrex.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: skinny power cords.





Hi Jim:


   I'm curious:  given that North American plug blades are 1/2 apart,
there
   must have been substantial contamination to aid in 120Vac jumping that
far
   (arcing).  Did you identify any sort of contamination or moisture?

I don't believe contamination is a significant factor
in events such as this one.

I believe such events start with a loose connection
between the plug and the socket (or between the wire
and the socket parts).  A loose connection means 
that the contact area is relatively small.  In turn, 
this means high current density at the point of 
contact.  

The smaller the contact area, the greater the 
resistance of the contact.

The smaller the contact area, the greater the current 
density at the point of contact.

These two factors contribute to heating of the two
parts, the plug blade and the socket.  Heating tends
to reduce the springiness of the socket part, and
of the connection between the supply wire and the
socket (because they are thermally connected).

The heating also tends to degrade the surface of the
insulating material in which the conductors are mounted.

Heating also enhances oxidation of the plating on the
parts, which further increases the resistance of the
connections.

If the plug-connected appliance is ON, arcing can
occur as the parts expand due to heating and make
various intermittant connections.  Arc temperatures
are very high, and can burn the surface of nearby 
insulating materials via radiation.

As the surface degrades, leakages occur across the
surfaces.  At this point, whether or not the appliance
is on or even connected is not a factor.  There is a
current path between the two poles along the surface
of the insulator.  This can either be between the 
socket parts, or between the wired parts.  The leakage
current causes further heating and micro-arcs where
the leakage path opens due to current density.  The
micro-arcs further damage the insulator until there
is nearly continuous micro-arcing.  I suggest this
is the source of the noise.  The heat from the micro-
arcing and the resistance of the carbonized surface 
of the insulator eventually lead to ignition and 
flames.

I admit that this is a hypothesis.  I believe that 
the process is more-or-less correct, but the details 
may not be correct.


Best regards,
Rich





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



RE: skinny power cords.

2001-10-25 Thread Jim Eichner

I'm curious:  given that North American plug blades are 1/2 apart, there
must have been substantial contamination to aid in 120Vac jumping that far
(arcing).  Did you identify any sort of contamination or moisture?

Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: Robert Macy [mailto:m...@california.com]
Sent: Thursday, October 25, 2001 8:50 AM
To: Roman, Dan; emc-p...@majordomo.ieee.org
Subject: Re: skinny power cords.



Just have to jump in here with personal experience:

In our bedroom we have a deLonghi radiator heater which uses an extension
cord (high cost UL approved) heavy guage #12 wire to power it - when it's
used.  This extension cord plugs into a multi outlet adapter, also heavy
duty UL approved.  At the time of the incident there was no power being used
from this outlet.

I was in another room, my wife was sitting on the edge of the bed watching a
news blurb on TV when she heard a funny sound, a scritch, scritch.   She
called to me to come listen.  Scritch, scritch, scritch got louder.  As I
arrived, flames started lapping up the wall from the outlet while still
making arcing sounds.  The flames were less than 6 inches from curtains.  I
reached into all this and unplugged the extension cord which luckily stopped
the fireworks display.  Imagine, if we had not been there.

Upon examination, it appeared that an arc had formed between the blades of
the extension cord (remember no power at the time).  That arc was not
sufficient to drop the 15A breaker to the outlet, yet was sufficient to
carbonize the UL approved material which further sustained the arc.

I posted this to the newsgroup alt.home.repair where a fireman jumped in
describing how this exact mechanism is what starts most home fires!  Isn't
that an encouraging thought!

Anyway, a little damn fuse in the plug would not have helped in this
circumstance, complete waste of time, much like the main breaker was.

 - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112

-Original Message-
From: Roman, Dan dan.ro...@intel.com
To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, October 25, 2001 7:41 AM
Subject: RE: skinny power cords.



I agreed completely with Scott.  A 6 to 9 foot 18AWG cord will handle well
in excess of 20A for a short period of time without starting to smoke
(heck,
it'll handle close to in excess of 60A for a very very short time without
bursting into flames--not that it was a good experience finding this out).
Point is, the cordage will handle a fault either indefinitely or long
enough
for the branch circuit breaker to trip provided you are connected to a 15A
or 20A branch circuit.

Another data point, you routinely pass more current through the cord when
doing the earthing test and that uses more current than the cord is rated.
Leave the tester on for awhile and the cord does not really heat up either.

What this list needs is a power cord manufacturer or agency safety engineer
that does power cords to settle this once and for all!

Dan

-Original Message-
From: Scott Lacey [mailto:sco...@world.std.com]
Sent: Wednesday, October 24, 2001 7:43 PM
To: Gary McInturff
Cc: emc-p...@majordomo.ieee.org
Subject: RE: skinny power cords.



Gary,
I believe the answer is that the power cord rating of 6 or 10 amps is the
operating current, at which it will have minimum temperature rise. Under
fault conditions it will experience a rather dramatic temperature rise that
is still well below the melting temperature of the insulation. The breaker
or fuse should clear well before the cord is cooked to the point of
failure.

Scott Lacey




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http

RE: skinny power cords.

2001-10-25 Thread Jim Eichner

I'll join the speculation...

I think it is also based on the likelihood of undetected damage to the cord
leading to a situation.  The cord lengths are limited by standards, they are
jacketed with materials designed to withstand some abuse, the condition is
easily (albeit rarely) inspected by the user, they are not supposed to be
physically attached to the wall (so no fear of damage by a metal cable clamp
for example), and so on.

The wiring in your walls, by comparison, may be more at risk, since it can't
be inspected, it is stapled to the studs, and you're always drilling or
pounding nails into walls having no idea whether or not there is wiring
behind the drywall.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists, and frequently has gas. Honest.  




-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Wednesday, October 24, 2001 12:21 PM
To: gary.mcintu...@worldwidepackets.com
Cc: emc-p...@ieee.org
Subject: Re: skinny power cords.






Hi Gary:


Somewhere in my past, I've heard the rationale for
this conundrum.  I'm just guessing here.

Power cords and similar mains devices are sized 
based on rated load, and are not sized based on
fault-condition load.

The requirement should be that, under fault 
conditions, the device is capable of withstanding 
the fault until the overcurrent device operates 
without igniting or otherwise causing a hazard.  
It can get hot; indeed, it can exceed rated 
temperature under the fault, and it can fail, 
but it should not ignite or otherwise cause a 
hazardous condition.

A power cord is supposed to be sufficiently robust 
as to withstand the rigors of use.  There are 
different degrees of robustness according to use.
In other words, the power cord itself is not
expected to fail under normal conditions of use.  

So, the power cord should only be subject to load
faults.  Since the load is protected against 
faults, the fault-protection in the load also 
provides fault-protection for the power cord.


Best regards,
Rich






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



RE: Shrunk-die power MOSFET's and compliance

2001-10-24 Thread Jim Eichner

Well for example, I have just finished specifying what compliance re-testing
I am going to need to do on 4 different products whose power conversion
stages use IRF630's, IRF740's, IRF840's, and RFP50N06's, but the list goes
on and on.  If you are using power FET's in power electronics, chances are
they have changed or will soon.  The main manufacturers that come to mind
are IR, Fairchild/Harris, Philips, and STM-Thomson.  Not all have forced
changes to the shrunk-die version - some have agreed to keep the old style
available - and all have at least added a suffix to their markings on the
devices so you can tell if it's the new revision die or old.  In one case,
however, we received modified parts with no markings differentiating them
from the old rev parts, for almost a year with no communication from the mfr
telling us about the change.  We found out through other channels and then
contacted them.  They seem to be behaving as if fundamental changes to the
performance and specifications of the part are none of our business.

I am re-doing radiated and conducted emissions, some thermal testing, and a
bunch of functional testing and looking at waveforms on 4 different products
affected by this change.  Those are only the products I am responsible for -
as a company we're doing functional testing and possibly compliance
re-testing on many more products.

This is not a simple component substitution exercise, if your products are
or use power electronics!  I would advise everyone potentially affected to
have your procurement department look into this.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



-Original Message-
From: Michael Mertinooke [mailto:mertino...@skyskan.com]
Sent: Wednesday, October 24, 2001 6:45 AM
To: 'Jim Eichner'
Subject: RE: Shrunk-die power MOSFET's and compliance


Jim;

I suspect that a lot of us just don't have time to investigate the latest
subtleties involved in producing a new chip design sold under an
old component part number. We order by manufacturer part number
and when the order comes in we count the pieces and throw it in
the stockroom. 

If there are reliability problems, most companies take a month or
so for the news to get back from Field Service. Then the issue goes
to Manufacturing because we know the design worked perfectly for
X years, so Manufacturing must have built 'em wrong, or the PC
house had a bad batch of boards or somebody screwed up the
wave solder machine again or the stockroom was sweeping parts
off the floor and dumping them back in the bins ... or a hundred
other cockups that happen every day. By the time somebody 
finally figures out that the FETs are not performing as they should,
it could be a year after the parts first hit the receiving dock.

Instead of a general reference, perhaps you can provide a few 
part numbers? If I see such a list and my FETs are on it, then 
I sure as hell am going to look into it immediately! 

Thanks.
Mike Mertinooke

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



RE: Insulated Electrolytic Capacitors

2001-10-24 Thread Jim Eichner

I asked a similar question a couple of years ago, and was told that the
bodies of plastic encapsulated Y1 capacitors are considered by CENELEC to be
reinforced insulation, except in the vicinity of the leads.  I don't know if
this extends to types of  X and Y caps other than Y1.

Hope this is some help,

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really
exists.  I know because he talks to me.  Honest.



-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Wednesday, October 24, 2001 6:38 AM
To: EMC-PSTC (E-mail) 
Subject: Insulated Electrolytic Capacitors



Dear All,

I have submitted an ac input to dc output switching power supply for NRTL
approval. One deviation is that the primary ac insulated capacitor is too
close to the earthed chassis and that the insulation cannot be relied to
provide the required basic insulation. 

1. What is the group's opinion regarding this point? I have personally seen
many Listed/Recognized units with clearance distance less than 2.0 mm to the
earthed chassis without any additional insulation to provide the required
insulation. In fact, I am holding a switching power supply by a reputable
manufacturer with only approx. 0.7 mm between the primary and earthed
chassis. This power supply is  UL Recognized and TUV approved.

2. There is a UL Pag 156002 regarding this issue, but it seems that some
NRTL engineers are using their own judgement and approving units at their
own discretion.





This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.




PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



  1   2   >