RE: IEC 60320 C14 module MOV's

2010-02-21 Thread emc-p...@ieee.org
Derek,

Not sure if there are any entry modules with MOV's; check
www.interpower.com.  You might even talk to those folks for more info.  

From my past life I remember that MOV's have a measurable leakage
current.  This current degrades the device with life and the leakage current
continues to increase.  This can result in overheating and/or fire as the
end of life event.  Many applications use a gas discharge tube in series
with the MOV to stop the leakage current and, thus, the degradation.  

GE used to have a MOV handbook with a lot of good stuff in it; not
sure if it is still available.  

Finally, undersized MOV's can explode under a very large fault
current.  This can be hazardous under some conditions.  

br, Pete

Peter E Perkins, PE
Principal Product Safety  Regulatory Consultant
Tigard, ORe  97281-3427

503/452-1201fone/fax
p.perk...@ieee.org

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@socal.rr.com
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-18 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that Arthur Michael amich...@safetylink.com wrote
(in pine.bsf.4.40.0312171050350.7927-100...@shelley.shelltown.net)
about 'CTL Decisions (was: RE: MOV's to ground)' on Wed, 17 Dec 2003:
In my experience, the CTL Decisions are not 'normative' but are a 
consensus position arrived at by the CTL (Committee of Testing Labs).

To my knowledge, the test labs are not bound to implement or observe 
these 'decisions'; The 'decisions' are documented/provided for guidance 
only.

But don't you think that the manufacturers should know about these
'decisions', whatever they are called?  Let's not argue about the exact
terminology. If you like, CTL *decides* to issue a *guide* on a certain
obscure matter or how the standard applies to a new situation.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
Brian,

Please see my comments below.

Richard Hughes

In a message dated 17/12/2003 21:41:30 GMT Standard Time,
boconn...@t-yuden.com writes:



Sir 

Most people working in the compliance field are under severe time and fiscal
constraints. Official response to these issues is seldom allowed by workers at
my level.



REH Since I'm coming up to about 1/4 century of working in the compliance
field I am fully aware of the severe time and fiscal constraints that folks in
the compliance field are under.  This is nothing new.

REH I have no idea what 'level' you are within your company, so I couldn't
comment on that point.




The typical corporate reaction will not occur until the design process has
been made intractable from conformity requirements. And then, it often takes
the form of a political and/or legal response, backed by the fever of
nationalism.



REH Sorry, but I do not understand what point you are trying to convey.




Please advise what I can do the make a difference, other than making
statements. Your advice is appreciated. 




REH That depends not only on you but on this forum as a whole.  This forum
seems to be good a good place to exchange information, however, on 16/12/2003
Richard Georgerian asked is there enough interest within the group to start
product technical committees?  I thought that this was point worthy of
further debate and so I sent out a proposal on 17/12/2003 which said, in part,
I believe that Richard Georgerian made some useful proposals on how to move
forward on the above front.  However, this community would need to grow into
either a professional organisation (and thereby be a voice for technical
concerns, but outside the province of standards making) or a voice for
industry (a kind of multinational trade association).  

Judging from the lack of replies to either Richard Georgerian or myself, it
would seem that there is no desire to extend this forum beyond exchanging
compliance information.  Therefore, in reply to your question it would seem
that there is nothing that you or anyone else can do in this forum to bring
about change.  

If you wish to make a difference then my advice would be to get your
employer to join a trade association and send you along as a representative. 
Of course this will take time and money just as it does for everyone who
attends such meetings and just as it does for those of us who are involved in
writing standards.  

Is your company willing to pay the association fees, travel costs and deal
with the fact that you will have to balance internal project work against
standards work?  Can your company make do with the compliance situation as it
is today or will it gain a sufficient competitive advantage in being able to
be at the forefront of knowledge, possibly even having the ability to effect
change?  These are the kinds of questions cum balancing act that all companies
face when they choose whether, and how actively, to participate in such
organisations. 

Before yet another Richard (Nute) steps in, I suggest that we close the
discussion at this point because it seems to have gone pretty much as far as
it is going to go.  Of course, you are free to reply to me individually if you
wish.




Respectfully, 
Brian 













RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
Sir 

Most people working in the compliance field are under severe time and fiscal
constraints. Official response to these issues is seldom allowed by workers at
my level.

The typical corporate reaction will not occur until the design process has
been made intractable from conformity requirements. And then, it often takes
the form of a political and/or legal response, backed by the fever of
nationalism.

Please advise what I can do the make a difference, other than making
statements. Your advice is appreciated. 

Respectfully, 
Brian 



-Original Message- 
From: richhug...@aol.com [ mailto:richhug...@aol.com] 
Sent: Wednesday, December 17, 2003 10:13 AM 
To: boconn...@t-yuden.com; emc-p...@majordomo.ieee.org 
Subject: Re: CTL Decisions (was: RE: MOV's to ground) 

Brian, John, 

I personally think that the question of test house interpretations has
deviated from the original point, though I do agree that any 'invisible'
requirement is a bad thing.  However, what is more important to me is what we
can do about it.  

In the above regard I have thus far seen no reaction to my earlier
contribution.  Therefore I conclude that people are satisfied with making
statements in the knowledge that no action is going to result, other than
perhaps to elicit a me to response from others.

Controversially yours, 

Richard Hughes 




Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that richhug...@aol.com wrote (in 15.1ed64bf4.2d11f
6...@aol.com) about 'CTL Decisions (was: RE: MOV's to ground)' on Wed,
17 Dec 2003:
Brian, John,

I personally think that the question of test house interpretations 
has deviated from the original point, though I do agree that any 
'invisible' requirement is a bad thing.  However, what is more 
important to me is what we can do about it.  

In the above regard I have thus far seen no reaction to my earlier 
contribution.  Therefore I conclude that people are satisfied with 
making statements in the knowledge that no action is going to 
result, other than perhaps to elicit a me to response from 
others.

Controversially yours,

I was under the impression that you were extremely averse to
controversy. It's out of season anyway. Nadolig llawen!

Anyway, I replied to Richard by e-mail, because UK national committee
business is involved.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

Hello John et al,

In my experience, the CTL Decisions are not 'normative' but are a
consensus position arrived at by the CTL (Committee of Testing Labs).

To my knowledge, the test labs are not bound to implement or observe these
'decisions'; The 'decisions' are documented/provided for guidance only.

Best regards; Happy Holidays, Art Michael


  -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --
 | Thinking of joining the Product Safety Engineering Society?? |
 |We REBATE PSES Dues to new subscribers to IPSN|
 |  |
 |Int'l Product Safety News |
 |   P.O.Box 1561-PSES  |
 |  Middletown CT 06457-8061 U.S.A. |
 |   Phone: (860) 344-1651 Fax: (860) 346-9066  |
 |  |
 | See Details at:http://www.safetylink.com/pses/psesoffr.txt |
  -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- -- --

On Wed, 17 Dec 2003, John Woodgate wrote:


 I read in !emc-pstc that krobin...@metlabs.com wrote (in D0A7A5548389C
 14e848a6fd28629251201045...@balte.metlabs-int.com) about 'CTL Decisions
 (was: RE: MOV's to ground)' on Wed, 17 Dec 2003:

  The bulletins are available for purchase in PDF Format from the IECEE
 Web Store to organizations that are not designated as NCB's or CBTL's
 (NCB's and CBTL's can obtain them from the Restricted Site as part of
 their Accredidation dues.):www.cbscheme.org IEC Standardssearch for
 Bulletins leads you to the following link:https://domino.iec.ch/websto
 re/webstore.nsf/artnum/030702 The posted cost is 312 CHF (approx 250 US
 Dollars or 200 EURO)


 I think this discussion has deviated from the original point.

 Manufacturers are required to make products that conform to standards.
 OK, they can buy the standards and work to them. But in the background,
 the CTL and, in Europe, the OSM, make decisions, known as
 'interpretations', on what certain words in those standard mean, either
 in general or in special circumstances, **and the manufacturers have no
 way of even knowing that these decisions have been made, let alone what
 they are**. The national standards bodies either don't know or won't
 say.

 So, the manufacturer is required to work to the standard, but lurking
 behind it is a hidden text that he does not even know exists. This is a
 situation worthy of Kafka.  But it is NOT about whether CTL and OSM
 decisions should be available free of charge, it's whether it's in any
 way justifiable for them to be SECRET. One former IEC Committee
 certainly decided that it was not justifiable and published its own list
 of interpretations. It remains to be seen whether its successor
 committee continues that policy.
 --
 Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk
 Interested in professional sound reinforcement and distribution? Then go to
 http://www.isce.org.uk
 PLEASE do NOT copy news posts to me by E-MAIL!

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ieee-pses.org/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   emc_p...@symbol.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
Brian, John,

I personally think that the question of test house interpretations has
deviated from the original point, though I do agree that any 'invisible'
requirement is a bad thing.  However, what is more important to me is what we
can do about it.  

In the above regard I have thus far seen no reaction to my earlier
contribution.  Therefore I conclude that people are satisfied with making
statements in the knowledge that no action is going to result, other than
perhaps to elicit a me to response from others.

Controversially yours,

Richard Hughes




RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
Well said, Mr. Woodgate; and it NEEDS to be said... 

In these United States, this can (technically) be considered illegal, and may
also be considered restraint of free trade. On the civil side (but, thank god,
I am not a lawyer, so my opinion is worthless) I have heard colleagues suggest
that this could be remedied by a tort based on the Freedom of Information Act.

luck, 
Brian 

-Original Message- 
From: John Woodgate [ mailto:j...@jmwa.demon.co.uk] 
Sent: Wednesday, December 17, 2003 5:58 AM 
To: emc-p...@majordomo.ieee.org 
Subject: Re: CTL Decisions (was: RE: MOV's to ground) 

I read in !emc-pstc that krobin...@metlabs.com wrote (in D0A7A5548389C 
14e848a6fd28629251201045...@balte.metlabs-int.com) about 'CTL Decisions 
(was: RE: MOV's to ground)' on Wed, 17 Dec 2003: 

 The bulletins are available for purchase in PDF Format from the IECEE 
Web Store to organizations that are not designated as NCB's or CBTL's 
(NCB's and CBTL's can obtain them from the Restricted Site as part of 
their Accredidation dues.):www.cbscheme.org IEC Standardssearch for 
Bulletins leads you to the following link: https://domino.iec.ch/websto 
re/webstore.nsf/artnum/030702 The posted cost is 312 CHF (approx 250 US 
Dollars or 200 EURO) 


I think this discussion has deviated from the original point. 

Manufacturers are required to make products that conform to standards. 
OK, they can buy the standards and work to them. But in the background, 
the CTL and, in Europe, the OSM, make decisions, known as 
'interpretations', on what certain words in those standard mean, either 
in general or in special circumstances, **and the manufacturers have no 
way of even knowing that these decisions have been made, let alone what 
they are**. The national standards bodies either don't know or won't 
say. 

So, the manufacturer is required to work to the standard, but lurking 
behind it is a hidden text that he does not even know exists. This is a 
situation worthy of Kafka.  But it is NOT about whether CTL and OSM 
decisions should be available free of charge, it's whether it's in any 
way justifiable for them to be SECRET. One former IEC Committee 
certainly decided that it was not justifiable and published its own list 
of interpretations. It remains to be seen whether its successor 
committee continues that policy. 
-- 




Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that krobin...@metlabs.com wrote (in D0A7A5548389C
14e848a6fd28629251201045...@balte.metlabs-int.com) about 'CTL Decisions
(was: RE: MOV's to ground)' on Wed, 17 Dec 2003:

 The bulletins are available for purchase in PDF Format from the IECEE 
Web Store to organizations that are not designated as NCB's or CBTL's 
(NCB's and CBTL's can obtain them from the Restricted Site as part of 
their Accredidation dues.):www.cbscheme.org IEC Standardssearch for 
Bulletins leads you to the following link:https://domino.iec.ch/websto
re/webstore.nsf/artnum/030702 The posted cost is 312 CHF (approx 250 US 
Dollars or 200 EURO) 


I think this discussion has deviated from the original point. 

Manufacturers are required to make products that conform to standards.
OK, they can buy the standards and work to them. But in the background,
the CTL and, in Europe, the OSM, make decisions, known as
'interpretations', on what certain words in those standard mean, either
in general or in special circumstances, **and the manufacturers have no
way of even knowing that these decisions have been made, let alone what
they are**. The national standards bodies either don't know or won't
say. 

So, the manufacturer is required to work to the standard, but lurking
behind it is a hidden text that he does not even know exists. This is a
situation worthy of Kafka.  But it is NOT about whether CTL and OSM
decisions should be available free of charge, it's whether it's in any
way justifiable for them to be SECRET. One former IEC Committee
certainly decided that it was not justifiable and published its own list
of interpretations. It remains to be seen whether its successor
committee continues that policy.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

 The bulletins are available for purchase in PDF Format from the IECEE Web
Store to organizations that are not designated as NCB's or CBTL's (NCB's and
CBTL's can obtain them from the Restricted Site as part of their
Accredidation dues.):
www.cbscheme.org IEC Standardssearch for Bulletins leads you to the
following link:
https://domino.iec.ch/webstore/webstore.nsf/artnum/030702 
The posted cost is 312 CHF (approx 250 US Dollars or 200 EURO)

Kevin Robinson
MET Laboratories


From: richhug...@aol.com
To: john.al...@era.co.uk; emc-p...@majordomo.ieee.org
Sent: 12/17/2003 6:00 AM
Subject: Re: CTL Decisions (was: RE: MOV's to ground)

John,

I understand from a UK NCB that the information is now published
quarterly in electronic format (on the IECEE web site?).  I am not an
NCB and so cannot comment on this first-hand.

Has anyone who is not an NCB approached the IECEE and been refused
access to this information?

Regards,

Richard Hughes


In a message dated 17/12/2003 10:43:49 GMT Standard Time,
john.al...@era.co.uk writes:



The CB Bulletin certainly did not used to be a private document and
you
used to be able subscribe to the CB Bulletin through your national
standards
sales organisation/outlet (e.g. from BSI in the UK, but I could'nt see
any
reference to it on the current IECEE site.

It used to cost several hundred pounds/dollars a year, but could be well
worth it even if you don't use the CB certification scheme - but it
could
also be somewhat out of date in paper form (do they yet do an electronic
form).

Regards

John Allen






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
John,

I understand from a UK NCB that the information is now published quarterly in
electronic format (on the IECEE web site?).  I am not an NCB and so cannot
comment on this first-hand.

Has anyone who is not an NCB approached the IECEE and been refused access to
this information?

Regards,

Richard Hughes


In a message dated 17/12/2003 10:43:49 GMT Standard Time, john.al...@era.co.uk
writes:



The CB Bulletin certainly did not used to be a private document and you
used to be able subscribe to the CB Bulletin through your national standards
sales organisation/outlet (e.g. from BSI in the UK, but I could'nt see any
reference to it on the current IECEE site.

It used to cost several hundred pounds/dollars a year, but could be well
worth it even if you don't use the CB certification scheme - but it could
also be somewhat out of date in paper form (do they yet do an electronic
form).

Regards

John Allen







RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

Hello all,

I am a member of the Australian committee responsible for managing
Australia's participation in IECEE, including managing how Australia
participates in the CB Scheme and the IECex scheme etc.

I believe the reason the IECEE CB Bulletins are restricted is economic (as
always).  It is more pressure from the standards writing bodies in each
country than an IECEE thing I believe.  Of course the IECEE need to recoup
some money for producing the CB Bulletin etc but also the various national
standards writing bodies are not keen on a differences list between their
standard and the IEC standard being available free of charge.  If they were,
not many people would end up buying the national standard now would they.

So the answer is yes, it is very much a copyright issue and if any CB labs
were discovered making their genuinely obtained CB Bulletins available to
others then that would be considered a very serious matter by the IECEE and
the continued CB accreditation of such a lab I believe would be in serious
jeopardy.


Best regards,
Kevin Richardson

Stanimore Pty Limited
Compliance Solutions for Technology
(Legislation/Regulations/Standards/Australian Agent Services)

Ph:   02-4329-4070   (Int'l: +61-2-4329-4070)
Fax:  02-4328-5639   (Int'l: +61-2-4328-5639)
Mobile:  04-1224-1620   (Int'l: +61-4-1224-1620)
Email:kevin.richard...@stanimore.com
URL:  www.stanimore.com

This material (this message and the information contained in all attachments
to this message) is confidential and/or privileged information and is
intended only for the addressee/s named above. Any unauthorised
dissemination, copying, use of or reliance upon this material by persons or
entities other than the addressee/s named above is prohibited. If you
receive this material in error, please notify Stanimore Pty Limited and
destroy all copies (electronic and hardcopy) of this message and all
attachments immediately.




From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Robert Johnson
Sent: Wednesday, 17 December 2003 7:03 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: CTL Decisions (was: RE: MOV's to ground)


Whether copyright violations are involved depends on the conditions of the
copyright. Sometimes copyrights are used to guarantee free public access to
a document, for example to guarantee attribution or assure completeness.

In this case it depends on the conditions issued by IECEE. They may be
providing these to labs doing certification for use with their client,
allowing it to be distributed to those involved. On the other hand, they may
be selling them at a price per copy. Maybe they are considered secret and
can't be provided to anyone but the certifying lab.

Can someone at a lab or IECEE provide information regarding the conditions
of the copyright?

Bob Johnson
ITE Safety



From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Colgan Christopher
[Soundcraft UK]
Sent: Tuesday, December 16, 2003 12:51 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: CTL Decisions (was: RE: MOV's to ground)


CB bulletins are available from the IEC http://www.iec.ch/ but you'll have
to pay.

I've had copies given to me by certain test labs but it was completely
unofficial and probably broke copyright laws.

This is a good time of year to meet up with your test lab engineers and
bribe them with a couple of drinks :)

Regards

Chris Colgan


From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 16 December 2003 16:16
To: emc-p...@majordomo.ieee.org
Subject: CTL Decisions (was: RE: MOV's to ground)




 From: John Woodgate

 Why are they not in the public domain?


And as much to the point, is the listing complete?  More
than once I've been referred to a CTL Decision that wasn't
on the CB Scheme web site that was provided to someone via
their CBTL or NCB.

Another item of great interest is the CB Bulletin.  There
may be items not for public consumption, but it's referred
to often enough, even in CB Scheme test reports, that it not
being public is unreasonable secrecy.  I've asked three
different CBTLs on more than one occasion for a copy and
been turned down every time, on the basis of copyright
protection.  Yet, I've read it on this list that it was
given for the asking.

Maybe I need to disguise my request in a lovely pastry or a
few pints.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher

RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org

The CB Bulletin certainly did not used to be a private document and you
used to be able subscribe to the CB Bulletin through your national standards
sales organisation/outlet (e.g. from BSI in the UK, but I could'nt see any
reference to it on the current IECEE site.

It used to cost several hundred pounds/dollars a year, but could be well
worth it even if you don't use the CB certification scheme - but it could
also be somewhat out of date in paper form (do they yet do an electronic
form).

Regards

John Allen
ERA Technology Ltd



From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 16 December 2003 16:16
To: emc-p...@majordomo.ieee.org
Subject: CTL Decisions (was: RE: MOV's to ground)




 From: John Woodgate

 Why are they not in the public domain?


And as much to the point, is the listing complete?  More
than once I've been referred to a CTL Decision that wasn't
on the CB Scheme web site that was provided to someone via
their CBTL or NCB.

Another item of great interest is the CB Bulletin.  There
may be items not for public consumption, but it's referred
to often enough, even in CB Scheme test reports, that it not
being public is unreasonable secrecy.  I've asked three
different CBTLs on more than one occasion for a copy and
been turned down every time, on the basis of copyright
protection.  Yet, I've read it on this list that it was
given for the asking.

Maybe I need to disguise my request in a lovely pastry or a
few pints.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


**
Copyright ERA Technology Ltd. 2003. (www.era.co.uk). All rights reserved. The
information supplied in this Commercial Communication should be treated in
confidence. 
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.
**


_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-17 Thread owner-emc-p...@majordomo.ieee.org
This is a multi-part message in MIME format.
Whether copyright violations are involved depends on the conditions of the
copyright. Sometimes copyrights are used to guarantee free public access to
a document, for example to guarantee attribution or assure completeness.

In this case it depends on the conditions issued by IECEE. They may be
providing these to labs doing certification for use with their client,
allowing it to be distributed to those involved. On the other hand, they may
be selling them at a price per copy. Maybe they are considered secret and
can't be provided to anyone but the certifying lab.

Can someone at a lab or IECEE provide information regarding the conditions
of the copyright?

Bob Johnson
ITE Safety
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Colgan Christopher
[Soundcraft UK]
Sent: Tuesday, December 16, 2003 12:51 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: CTL Decisions (was: RE: MOV's to ground)


CB bulletins are available from the IEC http://www.iec.ch/ but you'll have
to pay.

I've had copies given to me by certain test labs but it was completely
unofficial and probably broke copyright laws.

This is a good time of year to meet up with your test lab engineers and
bribe them with a couple of drinks :)

Regards

Chris Colgan


From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 16 December 2003 16:16
To: emc-p...@majordomo.ieee.org
Subject: CTL Decisions (was: RE: MOV's to ground)




 From: John Woodgate

 Why are they not in the public domain?


And as much to the point, is the listing complete?  More
than once I've been referred to a CTL Decision that wasn't
on the CB Scheme web site that was provided to someone via
their CBTL or NCB.

Another item of great interest is the CB Bulletin.  There
may be items not for public consumption, but it's referred
to often enough, even in CB Scheme test reports, that it not
being public is unreasonable secrecy.  I've asked three
different CBTLs on more than one occasion for a copy and
been turned down every time, on the basis of copyright
protection.  Yet, I've read it on this list that it was
given for the asking.

Maybe I need to disguise my request in a lovely pastry or a
few pints.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc

Title: RE: CTL Decisions (was: RE: MOV's to ground)






Whether copyright violations are involved depends on the conditions of the

copyright. Sometimes copyrights are used to guarantee free public access to

a document, for example to guarantee attribution or assure completeness.


In this case it depends on the conditions issued by IECEE. They may be

providing these to labs doing certification for use with their client,

allowing it to be distributed to those involved. On the other hand, they may

be selling them at a price per copy. Maybe they are considered secret and

can't be provided to anyone but the certifying lab.


Can someone at a lab or IECEE provide information regarding the conditions

of the copyright?


Bob Johnson

ITE Safety




-Original Message-

From: owner-emc-p...@majordomo.ieee.org

[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Colgan Christopher

[Soundcraft UK]

Sent: Tuesday, December 16, 2003 12:51 PM

To: emc-p...@majordomo.ieee.org

Subject: RE: CTL Decisions (was: RE: MOV's to ground)



CB bulletins are available from the IEC http://www.iec.ch/ but you'll have

to pay.


I've had copies given to me by certain test labs but it was completely

unofficial and probably broke copyright laws.


This is a good time of year to meet up with your test lab engineers and

bribe them

Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-16 Thread owner-emc-p...@majordomo.ieee.org

Hmmm... THat approach would get just about every salesman and marketing person
fired too...

Nothing wrong with having a working meeting in a pub, gets around all the red
tape...

Cheers ( literally :-) )

Derek.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: CTL Decisions (was: RE: MOV's to ground)

2003-12-16 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that Colgan Christopher [Soundcraft UK] Christopher
.col...@soundcraft.com wrote (in 31F4BED1E7C6814C99079DB01681234E1B015
D@HPROUKX3) about 'CTL Decisions (was: RE: MOV's to ground)' on Tue, 16
Dec 2003:
CB bulletins are available from the IEC http://www.iec.ch/ but you'll 
have to pay.

I've had copies given to me by certain test labs but it was completely 
unofficial and probably broke copyright laws.

This is a good time of year to meet up with your test lab engineers and 
bribe them with a couple of drinks :) 

But that is not the way to run a respectable conformity system. It is
clearly open to serious abuse. Those people accepting 'drinks' are
theoretically subject to instant dismissal.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: CTL Decisions (was: RE: MOV's to ground)

2003-12-16 Thread owner-emc-p...@majordomo.ieee.org

CB bulletins are available from the IEC http://www.iec.ch/ but you'll have
to pay.

I've had copies given to me by certain test labs but it was completely
unofficial and probably broke copyright laws.

This is a good time of year to meet up with your test lab engineers and
bribe them with a couple of drinks :)

Regards

Chris Colgan


From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 16 December 2003 16:16
To: emc-p...@majordomo.ieee.org
Subject: CTL Decisions (was: RE: MOV's to ground)




 From: John Woodgate

 Why are they not in the public domain?


And as much to the point, is the listing complete?  More
than once I've been referred to a CTL Decision that wasn't
on the CB Scheme web site that was provided to someone via
their CBTL or NCB.

Another item of great interest is the CB Bulletin.  There
may be items not for public consumption, but it's referred
to often enough, even in CB Scheme test reports, that it not
being public is unreasonable secrecy.  I've asked three
different CBTLs on more than one occasion for a copy and
been turned down every time, on the basis of copyright
protection.  Yet, I've read it on this list that it was
given for the asking.

Maybe I need to disguise my request in a lovely pastry or a
few pints.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



CTL Decisions (was: RE: MOV's to ground)

2003-12-16 Thread owner-emc-p...@majordomo.ieee.org


 From: John Woodgate

 Why are they not in the public domain?


And as much to the point, is the listing complete?  More
than once I've been referred to a CTL Decision that wasn't
on the CB Scheme web site that was provided to someone via
their CBTL or NCB.

Another item of great interest is the CB Bulletin.  There
may be items not for public consumption, but it's referred
to often enough, even in CB Scheme test reports, that it not
being public is unreasonable secrecy.  I've asked three
different CBTLs on more than one occasion for a copy and
been turned down every time, on the basis of copyright
protection.  Yet, I've read it on this list that it was
given for the asking.

Maybe I need to disguise my request in a lovely pastry or a
few pints.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: MOV's to ground

2003-12-15 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that ari.honk...@nokia.com wrote (in 7B9AF58829C5D
b4e869271eca2de58ea018ae...@esebe017.ntc.nokia.com) about 'MOV's to
ground' on Mon, 15 Dec 2003:
Fortunately, this secrecy is not complete, 
see 
http://www.iecee.org/ctl/decisions.htm

Interesting. Why are they not on, or linked from, the IEC web site?
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MOV's to ground

2003-12-15 Thread owner-emc-p...@majordomo.ieee.org

Fortunately, this secrecy is not complete, 
see 
http://www.iecee.org/ctl/decisions.htm

Regards,
Ari Honkala
 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of ext 
 John Woodgate
 Sent: 12 December, 2003 23:03
 To: emc-p...@majordomo.ieee.org
 Subject: Re: MOV's to ground
 
 
 
 I read in !emc-pstc that richhug...@aol.com wrote (in 
 1d5.16592759.2d0b
 3...@aol.com) about 'MOV's to ground' on Fri, 12 Dec 2003:
 Perhaps someone with access to the decisions of the Committee of 
 Test Laboratories (CTL) may be able to help find a 
 document you can 
 refer to. 
 
 Why are they not in the public domain? Manufacturers are required to
 conform to standards that are 'interpreted' by these bodies but the
 interpretations are kept secret. That can't be right, surely? 
 
 The IEC is trying to do something about it, by publishing
 interpretations, but the secrecy persists.
 -- 
 Regards, John Woodgate, OOO - Own Opinions Only. 
http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

This issue was beaten to death recently; and one solution is to put the
line to ground MOV in series with a gas discharge tube.  A properly
approved and rated gas discharge tube will practically eliminate the
leakage current to ground; and provide a safeguard against the MOV
failing short. 

Chris Maxwell
Design Engineer
Nettest 
(Currently figuring out how to get my autosignature back on my upgraded
version of outlook :-)




From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Tyra, John
Sent: Friday, December 12, 2003 9:55 AM
To: 'brian_ku...@leco.com'; jim.eich...@xantrex.com;
emc-p...@majordomo.ieee.org
Cc: Eszlari, Edward; Espinal, Mario; Tsitsopoulos, George
Subject: RE: MOV's to ground


Hello Jim

You can find CTL and OSM decisions which will have information about the
use
of MOV's at the following link

http://www.iecee.org/ctl/OSM_decisions.htm

The OSM decisions are the result of meetings held by participating
European
Agencies where clarification is offered for standards interpretations.
These
are not legally binding but I have found them a big help in
understanding
how the Agencies interpret the standardsYou can also find CTL
decisions
which are very helpful. 

I did not see 50178 listed but I know EN60950 and EN60065 have concerns
with
MOV's line to earth so you may want to use this as guidance.

Hope everyone finds this useful.

Regards,

John




From: brian_ku...@leco.com [mailto:brian_ku...@leco.com] 
Sent: Friday, December 12, 2003 8:29 AM
To: jim.eich...@xantrex.com; emc-p...@majordomo.ieee.org
Subject: Re:MOV's to ground


Jim,

You want to look at the EN60950 CCA document (not sure where to get the
latest copy). Attached is a WORD file that has a section of an older CCA
document that addresses this issue. I got it from a TUV office.

Brian



Reply Separator
Subject:MOV's to ground
Author: jim.eich...@xantrex.com
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date:   12/11/03 6:27 PM


Sorry - I know this has been flogged to death, but can someone please
point
me to something in writing that says you can't have MOV's to ground in a
product destined for Germany?  Or has that gone away?  Any other
countries
with the same or similar rules?

We are not in EN60950 - this is an EN50178 question, but really it's a
general question.

Thanks,

Jim Eichner, P.Eng. Compliance Engineering Manager
Xantrex Technology Inc. e-mail: jim.eich...@xantrex.com web:
www.xantrex.com
Any opinions expressed are purely accidental. Confidentiality Notice:
This
email message, including any attachments, is for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the
sender
by reply e-mail and destroy all copies of the original message.



This message is from the IEEE EMC Society Product Safety Technical
Committee
emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http

Re: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

I read in !emc-pstc that richhug...@aol.com wrote (in 1d5.16592759.2d0b
3...@aol.com) about 'MOV's to ground' on Fri, 12 Dec 2003:
Perhaps someone with access to the decisions of the Committee of 
Test Laboratories (CTL) may be able to help find a document you can 
refer to. 

Why are they not in the public domain? Manufacturers are required to
conform to standards that are 'interpreted' by these bodies but the
interpretations are kept secret. That can't be right, surely? 

The IEC is trying to do something about it, by publishing
interpretations, but the secrecy persists.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

Thanks to everyone who replied.  I was not aware that the answer was
dependent on the power system (TN-s vs. others) having been under the
impression that the issue was about increasing leakage current throughout
the life of the product.

As always the forum is vastly useful!

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are purely accidental.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: Jim Eichner [mailto:jim.eich...@xantrex.com] 
Sent: Thursday, December 11, 2003 3:10 PM
To: 'EMC-PSTC - forum'
Subject: MOV's to ground



Sorry - I know this has been flogged to death, but can someone please point
me to something in writing that says you can't have MOV's to ground in a
product destined for Germany?  Or has that gone away?  Any other countries
with the same or similar rules?  

We are not in EN60950 - this is an EN50178 question, but really it's a
general question.

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are purely accidental.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



This message is from the IEEE EMC Society Product Safety Technical Committee
emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org
Jim,

Perhaps someone with access to the decisions of the Committee of Test
Laboratories (CTL) may be able to help find a document you can refer to.  

Ken has explained one of the problems associated with MOVs, whether from line
to line or line to earth.  My understanding is that the failure mechanism is
not to go straight from an open circuit to a dead-short, but rather a
continued reduction in resistance with each hit.  Hence, when used from line
to ground, your equipment would probably fail to meet the protective conductor
(leakage) current before you see thermal problems with the MOVs.

You may also be unlucky in finding a generic answer applicable to all
standards.  I have been involved in discussing this topic as regards IEC/EN
60950-1, but not with EN 50178.

My recollection is that for Pluggable Type A equipment (e.g. regular domestic
plugs) Germany permit the use of MOVs in series with gas tubes from line to
ground.  Other countries accept this with the proviso that the gas tube meets
the requirements for Basic Insulation.  

There is an IEC standard (IEC 61051-2) covering MOVs and it is of course
recommended that you use such components.  Of course, it is also possible to
purchase MOVs with a built-in thermal fuse - great for ensuring that your
equipment doesn't catch on fire, but perhaps of limited use for continued
protection against transient voltages! 

Not exactly what you were looking for, but hopefully a few pointers for you to
follow-up with...

Regards,

Richard Hughes

Safety Answers Limited
www.safetyanswers.ltd.uk





RE: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

Hello Jim

You can find CTL and OSM decisions which will have information about the use
of MOV's at the following link

http://www.iecee.org/ctl/OSM_decisions.htm

The OSM decisions are the result of meetings held by participating European
Agencies where clarification is offered for standards interpretations. These
are not legally binding but I have found them a big help in understanding
how the Agencies interpret the standardsYou can also find CTL decisions
which are very helpful. 

I did not see 50178 listed but I know EN60950 and EN60065 have concerns with
MOV's line to earth so you may want to use this as guidance.

Hope everyone finds this useful.

Regards,

John




From: brian_ku...@leco.com [mailto:brian_ku...@leco.com] 
Sent: Friday, December 12, 2003 8:29 AM
To: jim.eich...@xantrex.com; emc-p...@majordomo.ieee.org
Subject: Re:MOV's to ground


Jim,

You want to look at the EN60950 CCA document (not sure where to get the
latest copy). Attached is a WORD file that has a section of an older CCA
document that addresses this issue. I got it from a TUV office.

Brian



Reply Separator
Subject:MOV's to ground
Author: jim.eich...@xantrex.com
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date:   12/11/03 6:27 PM


Sorry - I know this has been flogged to death, but can someone please point
me to something in writing that says you can't have MOV's to ground in a
product destined for Germany?  Or has that gone away?  Any other countries
with the same or similar rules?

We are not in EN60950 - this is an EN50178 question, but really it's a
general question.

Thanks,

Jim Eichner, P.Eng. Compliance Engineering Manager
Xantrex Technology Inc. e-mail: jim.eich...@xantrex.com web: www.xantrex.com
Any opinions expressed are purely accidental. Confidentiality Notice: This
email message, including any attachments, is for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the sender
by reply e-mail and destroy all copies of the original message.



This message is from the IEEE EMC Society Product Safety Technical Committee
emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

Jim, Ken, is correct in that when MOV's fail, they fail short. That is why
you see a circuit breaker or fuse in front of the MOV's. If your safety
ground is defective or does not return to the neutral side of the power
source, then your safety ground raises to line potential when the MOV's
short line to safety ground, with significant current available. In a case
like this the failure does not trip the circuit breakers or fuses in the
electrical panel. 

We had a such a failure here (multiple failures were to blame) and the only
thing damaged were 26 MOVs (in 26 electrical strips) that were line to
safety ground. None of the computers plugged into the strips were damaged,
even though fuses blew to protect the MOVs (after letting the smoke out of
the MOVs), but left the computers powered up. None of the computers had MOVs
line to safety ground. In our case the cubical area is three phase (115VAC
60Hz). One cubical was miss wired, which put the neutral to safety ground
MOV in the none fused part of the electrical strip, in to the line side of
the circuit. The main electrical box for the area was not properly grounded,
nor was the safety ground tied to the neutrals. So when the MOV failed it
raised the safety ground to the line potential of phase A, which put 230VAC
across all the MOV's on Phase B and Phase C. As Murphy would have it the MOV
that failed had a unintentional heatsink and survived longer than it should
have.  All the other MOV's did not have heatsinks.

The reality is you should never really need a MOV from line to safety ground
(or neutral to safety ground). It is the difference in potential that
destroys semiconductors. In most designs the semiconductors are line to
neutral not line to ground. So as long as you have one across line to
neutral you should be OK (not to mention the filters that assist).

The past discussions on this subject can be found in our archive on :
https://www.ieeecommunities.org/emc-pstc?go=t907166

Jim

Jim Bacher,  Senior Engineer
Paxar Americas, Inc.
e-mail: j.bac...@ieee.org
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Ken Javor
Sent: Thursday, December 11, 2003 11:08 PM
To: Jim Eichner; 'EMC-PSTC - forum'
Subject: Re: MOV's to ground



Not a legal answer, but I have seen a failure mode for MOVs where they
partially conduct line current.  This was in power strips.  My house
electrical system took a lightning hit.  Nothing was damaged but the MOVs,
including all the stuff in the house not connected to MOV protected power
strips.  The power strips with bad MOVs were quite hot (thermally) due to
the fault current (high impedance short to ground).  The MOVs were tiny, I
think larger ones might have fared better.  No doubt there is a spec
covering how many Joules/Watts an MOV must be able to absorb without damage.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: MOV's to ground

2003-12-12 Thread owner-emc-p...@majordomo.ieee.org

Not a legal answer, but I have seen a failure mode for MOVs where they
partially conduct line current.  This was in power strips.  My house
electrical system took a lightning hit.  Nothing was damaged but the MOVs,
including all the stuff in the house not connected to MOV protected power
strips.  The power strips with bad MOVs were quite hot (thermally) due to
the fault current (high impedance short to ground).  The MOVs were tiny, I
think larger ones might have fared better.  No doubt there is a spec
covering how many Joules/Watts an MOV must be able to absorb without damage.

 From: Jim Eichner jim.eich...@xantrex.com
 Reply-To: Jim Eichner jim.eich...@xantrex.com
 Date: Thu, 11 Dec 2003 15:10:21 -0800
 To: 'EMC-PSTC - forum' emc-p...@majordomo.ieee.org
 Subject: MOV's to ground
 
 
 Sorry - I know this has been flogged to death, but can someone please point
 me to something in writing that says you can't have MOV's to ground in a
 product destined for Germany?  Or has that gone away?  Any other countries
 with the same or similar rules?
 
 We are not in EN60950 - this is an EN50178 question, but really it's a
 general question.
 
 Thanks,
 
 Jim Eichner, P.Eng.
 Compliance Engineering Manager
 Xantrex Technology Inc.
 e-mail: jim.eich...@xantrex.com
 web: www.xantrex.com
 Any opinions expressed are purely accidental.
 Confidentiality Notice: This email message, including any attachments, is
 for the sole use of the intended recipient(s) and may contain confidential
 and privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender by reply e-mail and destroy all copies of the original
 message.
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ieee-pses.org/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



MOV's to ground

2003-12-11 Thread owner-emc-p...@majordomo.ieee.org

Sorry - I know this has been flogged to death, but can someone please point
me to something in writing that says you can't have MOV's to ground in a
product destined for Germany?  Or has that gone away?  Any other countries
with the same or similar rules?  

We are not in EN60950 - this is an EN50178 question, but really it's a
general question.

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are purely accidental.
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MOV's (Varistor to Earth)

2003-09-10 Thread POWELL, DOUG

Spencer,

It is possible to get UL 1449 approved MOVs up to 16 Amps, I think.  
See http://ulstandardsinfonet.ul.com/scopes/1449.html

I find that because of the added capacitance of the MOV, the leakage current
can go up unacceptably.  I will typically couple the MOV with a gas tube
that is rated higher than the line voltage. You now have to think about the
voltages of the two keeping in mind the trip points and the fact that the
gas tube clamps to ground while the MOV clamps to a voltage.

-doug


end


Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80535 USA 




From: Spencer, David H [mailto:david.spen...@usa.xerox.com]
Sent: Wednesday, September 10, 2003 9:49 AM
To: 'emc-p...@ieee.org'
Subject: MOV's (Varistors to Earth)



Howdy All,

I was curious if anyone out there has place a separately certified MOV
from Line (or Neutral) to Earth as a solution for Surge and placement in the
EU.
  
The specific application is a pluggable Type B.

The OSM/EE Note 1.5.1 98/2  indicates that for Pluggable Type B (and
permanently connected) equipment that provided the MOV is separately
certified it is an acceptable option.
See:  http://www.lyons.demon.co.uk/cenlec01.pdf

For my part this is a check to insure there are no other superceding
requirements  that would not allow a MOV from Line to Earth in the EU.
Also, are most MOV's separately certified?

Any additional  information would be appreciated.

Best Regards
David Spencer


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc

___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



MOV's (Varistors to Earth)

2003-09-10 Thread Spencer, David H

Howdy All,

I was curious if anyone out there has place a separately certified MOV
from Line (or Neutral) to Earth as a solution for Surge and placement in the
EU.
  
The specific application is a pluggable Type B.

The OSM/EE Note 1.5.1 98/2  indicates that for Pluggable Type B (and
permanently connected) equipment that provided the MOV is separately
certified it is an acceptable option.
See:  http://www.lyons.demon.co.uk/cenlec01.pdf

For my part this is a check to insure there are no other superceding
requirements  that would not allow a MOV from Line to Earth in the EU.
Also, are most MOV's separately certified?

Any additional  information would be appreciated.

Best Regards
David Spencer


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Line-ground MOV's

2002-06-20 Thread Chuck Mullett

Joachim:

I believe you're right on!  MOVs degrade with repeated hits.  Perhaps the
answer is the silicon TVS products from ON Semi and others.

Chuck



jl...@astex.mksinst.com wrote:

 Greetings,

 To meet  immunity requirements I will get a line filter which will include
 three line-ground MOV's,  (275V).
 To my opinion this may be a safety issue due to the danger to increase the
 leakage current especially after an overload of the MOV's.

 Am I in the right or is this not an issue regarding the Low Voltage
 Directive?

 Joachim Lohr
 ASTeX GmbH
 Tel.: ++49 30 464 003 19
 jl...@astex.mksinst.com

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Line-ground MOV's

2002-06-19 Thread jlohr

Greetings,

To meet  immunity requirements I will get a line filter which will include
three line-ground MOV's,  (275V).
To my opinion this may be a safety issue due to the danger to increase the
leakage current especially after an overload of the MOV's.

Am I in the right or is this not an issue regarding the Low Voltage
Directive?

Joachim Lohr
ASTeX GmbH
Tel.: ++49 30 464 003 19
jl...@astex.mksinst.com





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


[Fwd: Re:Oh those maddening MOV's!!]

2001-04-03 Thread Dave Heald

Forwarded for Jim Bacher

 Original Message 
Subject: Re:Oh those maddening MOV's!!
List-Post: emc-pstc@listserv.ieee.org
Date: Mon, 2 Apr 2001 16:34:21 -0500
From: jim_bac...@mail.monarch.com (Jim Bacher)
To: McCoy; Paul
pmc...@systemationusa.com,'emc-p...@majordomo.ieee.org'
emc-p...@majordomo.ieee.org

Popcorn and Smoke, this is not an answer to your question, just an
interesting
failure of MOV's that relates to your question.  About  five years ago,
first
thing in the morning, as everybody came into the wing I was in, they
would turn
on the electrical strips that their PC's were plugged into.  And most of
the
strips contained MOV's.  A few minutes later there would be a POP and
smoke
would pour out (flames in a few cases) of the electrical strip.  In the
matter
of a few minutes we lost over 25 electrical strips.  It was the same
morning and
the same time they were scrolling messages on who had just bought our
company.  

It seems that one of our cubes had been miss wired. It seems that line
and
neutral had been reversed.  As a result the fuse / circuit breaker of
the
electrical strip was in the neutral leg rather than the line side.  As
MOV's do
once in a while, the MOV that was line to ground failed as a short
circuit (the
MOV without the protection).  The MOV happened to be wedged against the
metal of
the strip so it could dissipate a little more power than normal.  Once
it
shorted to ground some even more interesting things happened.  Our wing
is run
on three phases.  It turns out that the ground was not installed
correctly and a
main ground wire to the wing had failed.  So when the MOV shorted, it
basically
lifted the ground of our wing to phase A's potential.  All of the MOV's
on phase
B and C then had twice their nominal voltage applied and without having
the
extra heat sinking that the first MOV had, they were popping like
popcorn.  None
of the computers were damaged, only the electrical strips were damaged.

Jim

Jim Bacher,  Senior Engineer
Paxar - Monarch
e-mail: jim_bac...@monarch.com
voice: 1-937-865-2020
fax: 1-937-865-2048


Reply Separator
Subject:Oh those maddening MOV's!!
Author: McCoy; Paul pmc...@systemationusa.com
List-Post: emc-pstc@listserv.ieee.org
Date:   4/2/01 3:30 PM


Group,
I know in conversations and threads past there has been
discussion
on the use of MOV's and gas arrestors for the main power input.
Specifically
at which times and under what conditions an MOV can be placed between
LINE
and PE. Could some one please tell me what standard (standards?) these
requirements come from?

Thank you,
Paul McCoy

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Oh those maddening MOV's!!

2001-04-02 Thread McCoy, Paul

Group,
I know in conversations and threads past there has been discussion
on the use of MOV's and gas arrestors for the main power input. Specifically
at which times and under what conditions an MOV can be placed between LINE
and PE. Could some one please tell me what standard (standards?) these
requirements come from?

Thank you,
Paul McCoy

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: MOV's

2000-10-13 Thread Patrick Lawler

On Thu, 12 Oct 2000 13:22:30 EDT, lfresea...@aol.com wrote:
does anyone have a SPICE model for an MOV?

Thanks,
Derek.

Take a look at the models offered by Intusoft
http://www.intusoft.com/Models.htm , and look for the 'Varistors' link.

Also try Littelfuse.  They now own the Harris/GE varistor product line:
http://www.littelfuse.com/
Do a search for the LA product series.  There's a link at the bottom of the
page for the SPICE models.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



MOV's

2000-10-12 Thread Lfresearch

Hi,

does anyone have a SPICE model for an MOV?

Thanks,

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Requirements For MOV's

2000-05-22 Thread Spencer, David H
I know this is a rehash of a topic from six months ago.. Sorry.

I would like to find a break down of the requirements for MOV's ( this is
only in AC mains applications)

1) By country  (EU countries primarily..  But Globally is good info too.)
2) What  safety markings ( on the device) are required?
3) What application limitations there are ; i.e. is  Line-to-Line, vs.
Line-to-Ground?
4) Are there national deviations regarding  the application specifics?
5)  What are the installation requirements?

Any comments or direction on this would be appreciated.

Regards

David Spencer
Xerox Corporation





attachment: Spencer,_David_H.vcf


RE: MOV's Vs Unipolar Suppressors

1999-08-05 Thread Jacowleff, Bill

Darrell:

Is Transorb a brand name?  On a prototype level I recently tried AVX
Transguard with success against positive and negative ESD Pulses up to 8KV
air discharge.  These parts according to the mfg. are MLVs, Multilayer
Varistors and act in a bipolar manner.
Best Regards,

Bill Jacowleff
VDO Control Systems
Airpax Instruments
150 Knotter Drive
Cheshire, CT 06410
Phone: 203 271-6394
FAX:203 271-6200
bjacowl...@vdo.com


-Original Message-
From: Darrell Locke (MSMail) [mailto:dlo...@advanced-input.com]
Sent: Wednesday, August 04, 1999 12:48 PM
To: 'emc-p...@majordomo.ieee.org'
Subject: MOV's vs Unipolar Suppressors



Compliance Collegues,

I have a question on MOV's (bi-polar) vs Transorbs (unipolar) devices for
board level transient protection, specifically ESD pulses that are very fast
rising.  The MOV type devices are inexpensive and come in arrays, so theyr'e
pretty easy to use.  I have heard  arguments against these type of devices
because a negative going pulse can drive an IC pin below ground (greater
than a diode drop) and cause the IC to be damaged by sourcing a large
current.  Some engineers prefer a unipolar device for this purpose.  I have
not however, seen this to occur in the test lab.  Has anyone experimented or
have opinions on this?

Thanks
Darrell Locke

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



MOV's vs Unipolar Suppressors

1999-08-04 Thread Darrell Locke (MSMail)

Compliance Collegues,

I have a question on MOV's (bi-polar) vs Transorbs (unipolar) devices for
board level transient protection, specifically ESD pulses that are very fast
rising.  The MOV type devices are inexpensive and come in arrays, so theyr'e
pretty easy to use.  I have heard  arguments against these type of devices
because a negative going pulse can drive an IC pin below ground (greater
than a diode drop) and cause the IC to be damaged by sourcing a large
current.  Some engineers prefer a unipolar device for this purpose.  I have
not however, seen this to occur in the test lab.  Has anyone experimented or
have opinions on this?

Thanks
Darrell Locke

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Re(2): Insulation on MOV's

1999-01-11 Thread rbusche
The other reason for putting tubing on MOV's is to direct (or contain) the
resulting explosion. Tubing helps direct the discharge away from other
circuits which may compromise spacings.

-Original Message-
From:   s_doug...@ecrm.com [mailto:s_doug...@ecrm.com]
Sent:   Monday, January 11, 1999 2:16 PM
To: jrbar...@lexmark.com
Cc: emc-p...@majordomo.ieee.org
Subject:Re(2): Insulation on MOV's

jrbar...@lexmark.com writes:

The vendor
 
who designed and built the power supply for us put
thick-wall heat-shrink
tubing
 
over the MOV to provide a safety barrier, since the dipped
epoxy coating
was
 
considered to be only operational insulation.

This reminds me of a product we made about 10 years ago. We
put MOV's on a
terminal block in the primary circuit to solve a problem.
Had no trouble
with that but I recall one of the agencies (UL, CSA, TUV)
made us put
heatshrink over the body of each MOV. Now I find out why.

Regards,
Scott
s_doug...@ecrm.com


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Use of MOV's ???

1998-04-21 Thread Ing. Gert Gremmen
That's right,  if any MOV fails, it fails by leaking more and more and more
and more
and then somebody is going to say aauauauauaua:(((


No kidding, you may use MOV's for surge suppressing between phases, but not
connect it to ground for the reasons above.

You may use MOV's for surge suppressing between phases, but not
connect it to ground for every MOV that fails slowly start leaking and
leaking
and finishes as a short circuit.

In the philosophy of LVD a double protection of a Class 1 apparatus consists
of:

- Isolation + earth bounding   ( 2 levels of protection agains electric
shock)

That would invalid one of the protection layers, as the MOV is no isolation
, and not
equivalent to an isolation layer.


BTW  Double Isolated apparatus Class II have two protection layers too,

Isolation +  extra isolation.  (  2 levels of protection agains electric
shock)


In both classes a single failure would not lead to catastrophy.


I suppose the guys at UL started to learn something from their TUV german
collegues ?!


Regards

Gert Gremmen , Ing.

== Ce-test, Qualified testing ==
Consultants in EMC, Electrical safety and Telecommunication
Compliance tests for European standards and ce-marking
Member of NEC/IEC voting committee for EMC.
Our Web presence: http://www.cetest.nl
List of current harmonized standards http://www.cetest.nl/emc-harm.htm
15 great tips for the EMC-designer http://www.cetest.nl/features01.htm




-Oorspronkelijk bericht-
Van: colli...@perkin-elmer.com colli...@perkin-elmer.com
Aan: emc-p...@ieee.org emc-p...@ieee.org
Datum: dinsdag 21 april 1998 16:46
Onderwerp: Re: Use of MOV's ???



 I recently received an e-mail from a colleague on the east coast
 stating that UL has joined TUV Rheinland in NOT accepting the use
 of MOV's in primary circuitry.

 The reasoning behind this is due to the unpredictable dielectric
 break down of these components which can increase leakage current
 beyond acceptable levels.


 Has anyone heard any truth to these statements ?
 If so, what other methods are being used to solve problems
 without these devices?

 Your comments are appreciated,

 Jeff Collins EMC/Product Safety Engineer
 Perkin-Elmer Applied Biosystems
 colli...@perkin-elmer.com








RE: Use of MOV's ???

1998-04-21 Thread Peter Tarver
Jeff -

This rumor doesn't make much sense as an across-the-board requirement,
especially considering UL has a component product category for MOVs and
other transient voltage surge suppressors, along with some product standards
that allow reductions of over-surface and through-air electrical spacings
when transients are known and/or controlled.  Presumably, your friend means
one specific product category or standard, but even then it makes little
sense for US application.

Could it be that this rumor is based on certain EU countries not wanting
MOVs in primary circuits, based on the nature of their power systems and UL
is enforcing this requirement for CB Scheme evaluations where specific
national deviations come into play?

I've seen no official mailing from UL on this topic.  Such a drastic
measure, after accepting MOVs in primary circuits for a long time, would
require a formal Industry Review (File Review), with announced schedules for
product compliance.

If your friend has more information on this, please convince them to pass it
along.


Regards,

Peter L. Tarver
Homologation Engineering
Dept. 4D02-4
MPK
MS:  D-2120
V:  ESN 655-2453
F:  ESN 655-2575

 --
 From: colli...@perkin-elmer.com[SMTP:colli...@perkin-elmer.com]
 Sent: Monday, April 20, 1998 11:31 AM
 
 
  I recently received an e-mail from a colleague on the east coast 
  stating that UL has joined TUV Rheinland in NOT accepting the use
  of MOV's in primary circuitry.
  
  The reasoning behind this is due to the unpredictable dielectric
  break down of these components which can increase leakage current
  beyond acceptable levels.
  
  
  Has anyone heard any truth to these statements ?
  If so, what other methods are being used to solve problems
  without these devices?
  
  Your comments are appreciated,
  
  Jeff Collins EMC/Product Safety Engineer
  Perkin-Elmer Applied Biosystems
  colli...@perkin-elmer.com
 
 


Re: Use of MOV's ???

1998-04-21 Thread collinjj

 I recently received an e-mail from a colleague on the east coast 
 stating that UL has joined TUV Rheinland in NOT accepting the use
 of MOV's in primary circuitry.
 
 The reasoning behind this is due to the unpredictable dielectric
 break down of these components which can increase leakage current
 beyond acceptable levels.
 
 
 Has anyone heard any truth to these statements ?
 If so, what other methods are being used to solve problems
 without these devices?
 
 Your comments are appreciated,
 
 Jeff Collins EMC/Product Safety Engineer
 Perkin-Elmer Applied Biosystems
 colli...@perkin-elmer.com



RE: MOV's

1998-02-22 Thread Farnsworth, Heber
One possibility is a MOV in series with a fuse (or spark gap in some
cases.) The MOV limits overvoltage current, the fuse or spark gap
provides required voltage standoff.

___
Heber Farnsworth, P.E.
Physio-Control Corp, Seattle, USA

 -Original Message-
 From: Stewart, Judd [SMTP:stewart.jud...@sd.littondsd.com]
 Sent: Thursday, February 19, 1998 2:00 PM
 To:   'EMC-PST'
 Subject:  MOV's
 
 Hello from San Diego,
 
 Does anyone know of components that will meet the requirements of
 EN60950 and also function as a MOV. The component will bridge basic
 insulation in a primary circuit. 
 
 Thanks
 
 Judd Stewart
 Litton Data Systems
 619.623.6639


RE: MOV's

1998-02-20 Thread Ing. Gert Gremmen
Hello Jim,


I do not think it is wise to use any component between phase and ground having 
a CM voltage limiting function. No component fits the requirements of EN 60950 
RELIABLE for sufficient amount of time.

I want re refer here to the requirements for solid state switches in EN 60730 
which are severe, and just for differential mode.

Especially MOV resistors tend to short circuit after a number of limiting 
actions, after a period of increasing leakage current.  

Regards,

Ing. Gert Gremmen


==
CE-test, qualified testing, 
Consultancy, Compliance tests for EMC and Electrical Safety
15 Great EMC-design tips available !
Visit our site  :  http://www.cetest.nl 
The Dutch Electronics Directory http://www.cetest.nl/electronics.htm
==


-Oorspronkelijk bericht-
Van:Stewart, Judd [SMTP:stewart.jud...@sd.littondsd.com]
Verzonden:  donderdag 19 februari 1998 23:00
Aan:'EMC-PST'
Onderwerp:  MOV's

Hello from San Diego,

Does anyone know of components that will meet the requirements of
EN60950 and also function as a MOV. The component will bridge basic
insulation in a primary circuit. 

Thanks

Judd Stewart
Litton Data Systems
619.623.6639


MOV's

1998-02-19 Thread Stewart, Judd
Hello from San Diego,

Does anyone know of components that will meet the requirements of
EN60950 and also function as a MOV. The component will bridge basic
insulation in a primary circuit. 

Thanks

Judd Stewart
Litton Data Systems
619.623.6639


Spark-gaps, MOV's and other breakover devices---

1997-04-25 Thread DenBleyker, R. (919-543-7251 TL 441)
In my opinion, any device that shifts from a high impedance to a low
impedance to protect an attached, parallel load, needs another part.

The additional part is a series energy limiter, examples a PTC device, an
inductor, a resistor, a fuse, etc.  The resulting circuit is nothing more
than a shunt regulator with the load and breakover device at the same
voltage, the remainder across the series limiter and the mains impedance.
The mains impedance tends towards 1/2% per unita very small number.

This point was made several years ago when an ambitious marketer brought a
voltage suppressor comprised of several MOV's in parallel across the mains,
and nothing else.  We gave it single simulated lightning disturbance---when
the smoke cleared all that remained of the suppressor was a dark stain on the
test bench.