Re: Conducted Emissions for PS output

1999-11-17 Thread Ken Javor
Re this: If the power supply is for a single unit utilizing a common power bus for the power supply input, then the output ripple of the supply might need to be controlled more stringently, perhaps on the order of tens of millivolts. Huh? Maybe I've been in Alabama too long, but I don't

RE: Conducted Emissions for PS output

1999-11-17 Thread Brumbaugh, David
Maybe I've been working on space systems too long...you can draw your own conclusions about that. At any rate, even though it isn't likely to be what Derek was after in the first place, let me try to make my statement clearer: What I was referring to was the distinction between a power

ISDN Access Switch for LAN/WAN

1999-11-17 Thread Nezam Najafi
To All: I was wondering if there is anybody out there who is interested in buying any ISDN based access switch for Video, Data, Voice call routing and networking equipment. We do have a fine products and a variety of models for Basic Rate Access and Primary Rate Access/T1/E1 networking for video

RE: impact /probes

1999-11-17 Thread Eric Monk
Hi Ed. You would need to be a pedantic purist to project a steel ball through an arc, 'pendulum like' and strike a verticle surface with the necessary impact required in ***950 by electromagnetic trickery. There is an addition to the drop test in the standard for vertical surfaces. the

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread georgea
I should not have required my old (non CE marked) brain to recall something over one day old! It is halon, not halogen, that we use in our old (1972?) EMC chamber. I believe that halon is far less a toxic threat than halogen, which is the family of agents which includes chlorine etc. Halon is

Measuring Capacitance in HV circuits

1999-11-17 Thread Brian Kunde at LECO
Hello Group, In EN61010, section 6.3 says, If the voltage exceeds the value listed in 6.3.1 or 6.3.2, the current and capacitance shall be measured. I understand how to measure current (6.3.1.2) with the circuit in Annex A, but how do I measure Capacitance for section 6.3.1.3? It doesn't

Correction

1999-11-17 Thread Scott Douglas
I should have been referring to Halon, not Halogen. Must have been in that CE marked brain clamp too long last night. Scott s_doug...@ecrm.com ECRM Incorporated Tewksbury, MA USA - This message is coming from the emc-pstc discussion list. To cancel your subscription, send mail to

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread Lacey,Scott
Scott, I beg to disagree, ... but, Halon, along with Freon and other compounds was banned by the Montreal Protocol, ostensibly to protect the ozone layer. Interestingly, the Freon replacements must, per the treaty, be phased out in 20 years - by coincidence about the time when the international

RE: DC Power Applied to an AC Rated Switching Power Supply

1999-11-17 Thread Jim Eichner
Peter: I don't think a 250Vac fuse can be relied on at 250Vdc, let alone 370Vdc. Regards, Jim Eichner Senior Regulatory Compliance Engineer Statpower Technologies Corporation jeich...@statpower.com http://www.statpower.com phone:(604) 420-4820 ext. 2162 fax: (604) 420-1591 Any

Printed Wiring Board Design for Safety Compliance

1999-11-17 Thread Rains,Mike
Colleagues, I am curious to know how you handle PWB design for safety compliance: 1. How do you document the required spacings on the schematics? 2. Do you use tools provided by your schematic entry system (ViewLogic, Valid or whatever) to enter these requirements? 3. Does

FW: Shielded Enclosure Fire Hazard

1999-11-17 Thread Price, Ed
Posted for: lothar.schm...@cetecom.de -Original Message- From: Schmidt Lothar, Essen [SMTP:lothar.schm...@cetecom.de] Sent: Wednesday, November 17, 1999 7:33 AM To: 'ken.ja...@emccompliance.com' Cc: 'emc-p...@ieee.org' Subject: AW: Shielded Enclosure Fire Hazard

RE: internet information

1999-11-17 Thread Laura Leyba-Newton
We are trying to determine the proper fusing for the UK power cord. The products we will be using the cord set on will never exceed 3amps in normal operating conditions. For the power cord set the Manufacturer has provided us with the following information: BSI/ASTA Approved British Male to

Re: DC Power Applied to an AC Rated Switching Power Supply

1999-11-17 Thread Robert Macy
BE CAREFUL ! ! ! If this PS does not have Power Factor Correction Many switching power supplies comply with the conducted emissions limits BECAUSE of the conducting angle of the AC diodes. Simply said, the AC rectifying diodes only come on for 15--18% of the duty cycle. therefore the noise

POWER CORDS FOR SOUTH AMERICA.

1999-11-17 Thread George Waters
I need help on power cords for South America. We are supplying our US customer with product that he mostly uses in the US. He will however be shipping a few hundred to various South American countries. The power cord which we have packed with the units, has an IEC connector on one end, and a

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread Scott Douglas
George, I once worked in a laboratory that developed the Doppler weather radar we all see on TV today. In our just built (in 1979) control room, they put a halogen extinguisher system. Halogen works by displacing the oxygen and thus the fuel for the fire. No fuel, no fire. The system could fill

INFO REQUESTED ON TABLE OF COMPLIANCE REQUIREMENTS BY COUNTRY

1999-11-17 Thread George Waters
All, Some time back, one the contributors to this forum had a one page table listing countries and what compliances were mandatory for these countries. I seem to remember it was an attachment to an email rather than a web link. I have not been able to find it in rcic.com. Can someone help me

RE: DC Power Applied to an AC Rated Switching Power Supply

1999-11-17 Thread Andrews, Kurt
Peter, Is the DC Input shown on the power supply ratings label along with the AC Input? If this is the case then both inputs would have been tested when the supply was tested by UL and TUV for Recognition. No additional testing would be required. We have used supplies that are rated for both an

Re: Conducted Emissions for PS output

1999-11-17 Thread Ralph Cameron
Derek The most common method I've found effective - even after sale- is the use of a toroidal ferrite core , large enough to take 8-9 turns of the power cord, mounted as close to the supply as possible. There is 15-20 dB decoupling to common mode noise provided by this method and I've used it

Re: Grounding Questions

1999-11-17 Thread Robert Macy
Probably the wrong words to use. I should have said design in a highly reliable GFI function to detect when an installation has been done improperly. That, coupled with incredibly clear installation instructions should cover legal liability (and moral liability - after all what more can one do,

RE: internet information

1999-11-17 Thread John Allen
Raymond I think you have asked a very big question - and unfortunately I do not have time to go into it! However, I also think that it has been discussed before in EMC-PSTC, and so I suggest that you ask Ed Price or Rich Nute if they can identify the previous threads for you to examine on

RE: impact /probes

1999-11-17 Thread Aschenberg, Mat
Hi, I just bought a 2 ball bearing from Whistler Bearing Company in Denver for $15.00. Thats fifteen, not one hundred and fifty. However, I will be happy to charge you a mere $75, to purchase it for any of you and mail it to you. :) Mat Aschenberg -Original Message- From: Dwight

RE: impact /probes

1999-11-17 Thread Price, Ed
I don't normally go around dropping steel balls on things, but if I wanted to be a purist about it, I would hold the ball by an electromagnet, so I wouldn't have to alter the shape and mass of the ball by drilling or affixing an eyelet. It also sounds like more fun. Ed

RE: Conducted Emissions for PS output

1999-11-17 Thread Brumbaugh, David
Derek In my experience in the aerospace industry, the output voltage ripple is typically specified. However, the amount of acceptable ripple and the frequency range of concern depends on the application. An example is the ripple level specified by MIL-STD-1541A which calls for a ripple limit

British plugs

1999-11-17 Thread John Radomski
Laura, Also I am interested to know if a detachable UK power Cord is required to be fused. J.R.: YES. The fuse must conform to BS 1362. Products using this line cord have integral fuses in both AC lines. J.R.: Just one fuse. It is located in the BS 1363 style power plug and wired to the

IEC 61000-6-* series standards

1999-11-17 Thread cnewton
I've been told by a source in France that EN 50082-1 and EN 50082-2 Industrial level generic standards are going to be combined into this IEC 61000-6 series of standards. I'm also told that this series will become EN, replace the generic industrial standards, and become effective January 1,

RE: internet info

1999-11-17 Thread ron_wellman
Laura, For UK power cord sets, BS 1363 and 1362 are the two standards you want to look at for plugs and fusing, respectively. You have to fuse the plug regardless if your product is double fused. Regards, Ron Wellman ron_well...@agilent.com -Original Message- From: Non-HP-LNewton

RE: PTCs for Transformer Overload/Short Circuit Protection

1999-11-17 Thread WOODS
We use them in the secondary to provide limited power outputs per IEC 950. We have obtained UL and TUV certifications without a problem. Richard Woods -- From: pmerguer...@itl.co.il [SMTP:pmerguer...@itl.co.il] Sent: Wednesday, November 17, 1999 8:43 AM

RE: internet information

1999-11-17 Thread Raymond . Li
John, I am very insterested in your explaination on fused plug requirement between the ring main supply system and branch or spur systems. Could you please shed more light on to me about the fused plug requirement on the ring main supply and a simply way to identify the said main supplies.

DC Power Applied to an AC Rated Switching Power Supply

1999-11-17 Thread Peter Merguerian
Dear Folks, I have a product with an UL/TUV UL1950/EN 60 950 Approved 100-240 Vac rated switching power supply. Manufacturer has means for 110-370 Vdc connection to this power supply. My question is can this be done without additional tests? If tests are necessary, what kind of tests are

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread georgea
Between a hard place and a rock It is hard to argue that EMC chambers should not have fire protection. The newer tiled facilities may have little combustible content other than the DUT. However, most factory insurance carriers will insist on an adequate prevention and extinguishing

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread Ned Devine
Hello, Put the sprinklers in. Also, make sure they are 360 deg (i.e. spray up and down) heads!!. At a previous employer, we had a fire in a cone lined, shield room. We had sprinklers, but they were only 180 deg. (i.e. down). The fire started when some cones on the ceiling came loose and

PTCs for Transformer Overload/Short Circuit Protection

1999-11-17 Thread Peter Merguerian
Hello Group, Anyone had problems with Test Houses regarding the use of PTCs in Transformer Primary and/or Secondary Windings to Protect Against Overload/Short Circuit Conditions? Regards, +++ RTTE Directive Seminar Renaissance Hotel, Tel-Aviv 12th January 2000.

RE: Definition of Residential location

1999-11-17 Thread georgea
Another slant on this issue is the price of the product. The FCC looks at the function, price and marketing of an ITE product. The maker can claim it is intended for commercial enterprises, and should be Class A. However, if it is affordable for the typical consumer PC workstation, OR is

RE: internet information

1999-11-17 Thread Colgan, Chris
Hi John When I typed that last statement I didn't believe it to be naive but obviously it was. I was surprised to find that quite a lot of countries use UK type plugs (see web sites below). Amongst them is Hong Kong although I believe that Hong Kong requires plugs to conform to BS1363.

RE: Shielded Enclosure Fire Hazard

1999-11-17 Thread WOODS
We also had to install sprinklers. Richard Woods -- From: Ken Javor [SMTP:ken.ja...@emccompliance.com] Sent: Wednesday, November 17, 1999 1:37 AM To: Price, Ed; 'emc-p...@ieee.org' Subject: Re: Shielded Enclosure Fire Hazard This

RE: Temperature Ratings:

1999-11-17 Thread WOODS
I don't know where you got the information for commercial applications. 0-70C are the specs for commercial grade ICs. There is no standard for commercial equipment. However, generally, ITE intended for indoor use is rated 0-35C. For non-air conditioned space the upper limit goes to 55C.

RE: internet information

1999-11-17 Thread John Allen
Laura With respect to the last line of Chris Colgan's email: Be careful! In the UK we have seen a number of bogus power cords with 13A plugs which have no provision for fuses. Additionally, they are much narrower than BS1363-compliant plugs and have no insulating sleeving on the Line

RE: Definition of Residential location

1999-11-17 Thread roger . viles
There is a further issue because the generic emissions standard EN 50081-1 covers the Residential, Commercial and Light Industrial environment, i.e. the only one it does not cover is the real industrial (EN 50081-2). This means that all normal commercial applications require EN 50081-1 which

RE: EN61000-4-6 versus EN55103-2

1999-11-17 Thread Colgan, Chris
Hi Mike Don't panic! The test level is not as high as it seems. For a start, the test level of 3V is the open circuit generator output. Next, I guess that you could reasonably expect high interference levels in the 150kHz - 80MHz range after all, amongst other things, CB radio, taxi comms and

RE: internet information

1999-11-17 Thread Colgan, Chris
Laura Re. the power cord. SI No.1768 requires UK consumer products to be fitted with a plug conforming to BS1363. Both BS1363 and SI 1768 require the plug to be fused. The fuse value is determined by the cross sectional area of the power cord conductors. I doubt that you could find an

RE: Underfloor Radiant Heating Panels for Europe

1999-11-17 Thread Crabb, John
In the BSI catalogue I have found : - BS EN 1264 Floor Heating. Systems and Components comprises : BS EN 1264-1:1998 Definitions and symbols BS EN 1264-2:1998 Determination of the thermal output BS EN 1264-3: 1998 Dimensioning All the above BS are identical to the EN. There is also a BSI CP 1018

RE: internet information

1999-11-17 Thread John Allen
Laura All UK standard power cords require to be fused - regardless of the fusing in appliance to which they are connected - because we use a totally different building ring main supply system to most other countries which use branch or spur systems ! The main reason is that the power cord

Re: Shielded Enclosure Fire Hazard

1999-11-17 Thread roger . viles
Not a recommendation - I just saw the ad in Compliance Engineering - but non-combustible pyramid absorbers are offered by the German company Frankonia. See: www.frankonia-emc.com Roger - This message is coming from the emc-pstc discussion list. To cancel your subscription, send mail

Re: Grounding Questions

1999-11-17 Thread Matthew Meehan
Robert, I don't think GFIs are failsafe. Don't they all come with test buttons? Matt Why has no one mentioned using a GFI detector as a failsafe way to make certain the installation is done per spec? After all, in the US the manufacturer still comes out liable for any damages.

Re: Conducted Emissions for PS output

1999-11-17 Thread Ken Javor
I'm not sure if the question is technical or spec-ese. I don't know the spec-ese answer, but technically the answer is straight-forward. If the anticipated loads are not antenna-connected receivers, then the only CE concern is that the output wires not radiate sufficiently to cause rfi. You

Re: Shielded Enclosure Fire Hazard

1999-11-17 Thread Ken Javor
This happened to me at a previous employer. There is some sense to it in that foam absorber is quite flammable, even with modern precautions and flammability requirements. We had to install sprinklers. The system was set up so that the sprinklers are dry until a smoke alarm signal allows

Re: Shielded Enclosure Fire Hazard

1999-11-17 Thread Matthew Meehan
My lab just had an annual inspection visit by our friendly fire hazard inspector. Seems that after 4 successive years of inspections, I suddenly failed this year. Hi Ed, Don't shoot the bearer. Go find the guy who passed you the last 3 years - shoot him. If it's the same guy - well it's

Re: internet information

1999-11-17 Thread Rich Nute
Hi Laura: Could someone please tell me where previous EMC and safety discussions are posted on the internet. emc-pstc messages are archived at: http://www.rcic.com/ Click on Virual Conference Hall. The archives can be searched by topic. Also I am interested to know if a

Re: impact /probes

1999-11-17 Thread Rich Nute
BTW, you may find a 50mm diameter ball bearing, but will it weigh 500g +/-25g? And then you'l have to drill and tap it for an eyelet for the string. The impact ball spec was written around a 2-inch diameter ball bearing. Drilling and tapping the ball bearing requires some sort of

Conducted Emissions for PS output

1999-11-17 Thread Derek Walton
HI, would anyone like to suggest a specification for controlling conducted emissions from the output of a power supply or battery charger. The market place is either the USA or Europe. Thanks, Derek. -- Derek Walton Owner L. F. Research EMC Design and Test Facility 12790 Route 76, Poplar

Shielded Enclosure Fire Hazard

1999-11-17 Thread Price, Ed
Hi Listmembers! My lab just had an annual inspection visit by our friendly fire hazard inspector. Seems that after 4 successive years of inspections, I suddenly failed this year. The reason is that my 24' x 35' x 10' modular shielded enclosure doesn't have internal water sprinklers. Now I'm all

FW: EN61000-4-6 versus EN55103-2

1999-11-17 Thread Price, Ed
Posted for: mmur...@alesis1.corpusa.com :-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-) Ed Price ed.pr...@cubic.com Electromagnetic Compatibility Lab Cubic Defense Systems San Diego, CA. USA 619-505-2780 (Voice) 619-505-1502 (Fax) Military Avionics EMC

RE: IEC 61010-1 2nd Edition

1999-11-17 Thread ron_wellman
Joe, The 2nd Edition of IEC 61010-1 is brand new. The amendments you speak of were for the 1st Edition. The big question is whether CENELEC will adopt the 2nd Edition without modifications. Regards, +=+ |Ronald R. Wellman

Re: Biohazard Symbol per ISO 7000

1999-11-17 Thread Ron Pickard/Hypercom/US
Hi Joe, According to ISO7000, symbol 0659's description is Biological risks. I hope this helps. Best regards, Ron Pickard rpick...@hypercom.com MartinJP@pebi

internet info

1999-11-17 Thread Laura Leyba-Newton
Could someone please tell me where previous EMC and safety discussions are posted on the internet. Also I am interested to know if a detachable UK power Cord is required to be fused. Products using this line cord have integral fuses in both AC lines. You help would be greatly appreciated. -Laura