George and Craig,
Isn't this section that you referred to just for large drops?

Bob Knight


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, May 19, 2008 6:41 AM
To: [email protected]
Subject: RE: Missing

And what Todd said about previous requirements by some insurance AHJs to use
it preceded the 2007 #13 requirement.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, May 19, 2008 8:27 AM
To: [email protected]
Subject: RE: Missing

8.4.7.2 of the 2007 NFPA 13 states:

8.4.7.2* Galvanized Pipe.
8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems, piping
materials shall be limited to internally galvanized steel.
8.4.7.2.2 Nongalvanized fittings shall be permitted.

*A.8.4.7.2 The purpose of this requirement is to avoid scale accumulation.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Sunday, May 18, 2008 8:40 PM
To: [email protected]
Subject: Missing

Hello sprinklerforum,

  I think I am missing something. IF my old brain remembers it was a
requirement for dry pipe systems to use Galvanized Pipe, But were allowed to
use black iron fittings. I am unable to find that in the 2007 edition of 13,
Am I dreaming, or was it deleted, or where is it now?

--
Best regards,
Charles Thurston CET
Coastal Fire Protection
mailto:[EMAIL PROTECTED]