Yes that section with that wording is just under the heading of Large
Drops.  But does the same concern not apply for any other type heads on
dry sprinkler systems?

So if you take it to it's literal extreme, dry sprinkler systems that
utilize Large Drop sprinklers are the only systems subject to scale
accumulation.  Scale accumulation doesn't occur or is of no importance
for standard 5.6K or 8.0K or X.XK sprinklers so no galvanized piping is
necessary per the Standard?  Really?  Could someone explain the logic
behind this?

If you use regular black pipe and the supervisory air supply uses
ambient air with no drier you can pretty much bet that over a period of
time the interior of that pipe will rust and scale.  The moisture in the
supervisory air will contribute to that.  

So then would you would have compliance issues with 8.16.4.2.

Your rust or corrosion isn't always from an external source, it could be
from inside as well.  

Trying to save a few bucks at the front end could be costly down the
road.  Unfortunately many will be forced to save those few bucks up
front if the code or standard doesn't particularly say it's required.





Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Eckard,
Mark - Mark E
Sent: Monday, May 19, 2008 9:53 AM
To: [email protected]
Subject: RE: Missing

Read the FAQ information in the Handbook edition of the 2007 NFPA-13
8.4.7.2 this issue is addressed directly.  "The use of internally
galvanized steel piping materials applies only where large drop
sprinklers are used.  Dry pipe systems using other types of sprinklers
are not limited to particular piping material but must comply with the
requirements of section 6.3 and 6.4."

Mark E. Eckard S.E.T.
Phone: (336) 658-4359
Fax: (336) 658-3257
Cell: (336) 467-0194
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, May 19, 2008 9:27 AM
To: [email protected]
Subject: Missing

George and Craig,
Isn't this section that you referred to just for large drops?

Bob Knight


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, May 19, 2008 6:41 AM
To: [email protected]
Subject: RE: Missing

And what Todd said about previous requirements by some insurance AHJs to
use it preceded the 2007 #13 requirement.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, May 19, 2008 8:27 AM
To: [email protected]
Subject: RE: Missing

8.4.7.2 of the 2007 NFPA 13 states:

8.4.7.2* Galvanized Pipe.
8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems,
piping materials shall be limited to internally galvanized steel.
8.4.7.2.2 Nongalvanized fittings shall be permitted.

*A.8.4.7.2 The purpose of this requirement is to avoid scale
accumulation.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Sunday, May 18, 2008 8:40 PM
To: [email protected]
Subject: Missing

Hello sprinklerforum,

  I think I am missing something. IF my old brain remembers it was a
requirement for dry pipe systems to use Galvanized Pipe, But were
allowed to use black iron fittings. I am unable to find that in the 2007
edition of 13, Am I dreaming, or was it deleted, or where is it now?

--
Best regards,
Charles Thurston CET
Coastal Fire Protection
mailto:[EMAIL PROTECTED]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)