Read the FAQ information in the Handbook edition of the 2007 NFPA-13
8.4.7.2 this issue is addressed directly.  "The use of internally
galvanized steel piping materials applies only where large drop
sprinklers are used.  Dry pipe systems using other types of sprinklers
are not limited to particular piping material but must comply with the
requirements of section 6.3 and 6.4."

Mark E. Eckard S.E.T.
Phone: (336) 658-4359
Fax: (336) 658-3257
Cell: (336) 467-0194
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, May 19, 2008 9:27 AM
To: [email protected]
Subject: Missing

George and Craig,
Isn't this section that you referred to just for large drops?

Bob Knight


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, May 19, 2008 6:41 AM
To: [email protected]
Subject: RE: Missing

And what Todd said about previous requirements by some insurance AHJs to
use
it preceded the 2007 #13 requirement.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, May 19, 2008 8:27 AM
To: [email protected]
Subject: RE: Missing

8.4.7.2 of the 2007 NFPA 13 states:

8.4.7.2* Galvanized Pipe.
8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems,
piping
materials shall be limited to internally galvanized steel.
8.4.7.2.2 Nongalvanized fittings shall be permitted.

*A.8.4.7.2 The purpose of this requirement is to avoid scale
accumulation.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Sunday, May 18, 2008 8:40 PM
To: [email protected]
Subject: Missing

Hello sprinklerforum,

  I think I am missing something. IF my old brain remembers it was a
requirement for dry pipe systems to use Galvanized Pipe, But were
allowed to
use black iron fittings. I am unable to find that in the 2007 edition of
13,
Am I dreaming, or was it deleted, or where is it now?

--
Best regards,
Charles Thurston CET
Coastal Fire Protection
mailto:[EMAIL PROTECTED]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to