Didn't look, Bob- 2007 isn't adopted yet, and we use galv on our dry systems unless the owner is penniless or aware of the shortened life. The insurance requirements I refer to are NOT limited to LD's, FM, IRI, Lumbermans if memory works on Monday, all had requirements for dry systems to be galv for years. Fittings didn't need to be unless there were external considerations.
glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Monday, May 19, 2008 9:27 AM To: [email protected] Subject: Missing George and Craig, Isn't this section that you referred to just for large drops? Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church Sent: Monday, May 19, 2008 6:41 AM To: [email protected] Subject: RE: Missing And what Todd said about previous requirements by some insurance AHJs to use it preceded the 2007 #13 requirement. glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Monday, May 19, 2008 8:27 AM To: [email protected] Subject: RE: Missing 8.4.7.2 of the 2007 NFPA 13 states: 8.4.7.2* Galvanized Pipe. 8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems, piping materials shall be limited to internally galvanized steel. 8.4.7.2.2 Nongalvanized fittings shall be permitted. *A.8.4.7.2 The purpose of this requirement is to avoid scale accumulation. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Coastal Sent: Sunday, May 18, 2008 8:40 PM To: [email protected] Subject: Missing Hello sprinklerforum, I think I am missing something. IF my old brain remembers it was a requirement for dry pipe systems to use Galvanized Pipe, But were allowed to use black iron fittings. I am unable to find that in the 2007 edition of 13, Am I dreaming, or was it deleted, or where is it now? -- Best regards, Charles Thurston CET Coastal Fire Protection mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)