George,
Don't' look at what?  The text in 13?  2007 is adopted in many areas
including the area that I live in.  So, the bottom line is 13 is the
document of reference, then galvanized is not required with the exception of
large drop systems.  If there is another document referenced in the bid
documentation because of insurance concerns or other concerns then and only
then is the text of 13 trumped.  As far as being penniless, it seems to me
that almost every building owner I have dealt with is penniless.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, May 19, 2008 9:55 AM
To: [email protected]
Subject: RE: Missing

Didn't look, Bob- 2007 isn't adopted yet, and we use galv on our dry systems
unless the owner is penniless or aware of the shortened life. The insurance
requirements I refer to are NOT limited to LD's, FM, IRI, Lumbermans if
memory works on Monday, all had requirements for dry systems to be galv for
years. Fittings didn't need to be unless there were external considerations.

glc