I believe that the reason that you would need the K factor is that modeling
has shown that in very high ceilings like arena's and such the droplet size
is very important if you want the water to reach the floor in a fire, and
not just be steam 30' AFF.

I agree it should be the PE, not the AHJ deciding this, without further
guidance in the standards. The important thing for the AHJ is to recognize
the potential for failure if you simply "Provide coverage per the code".

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Autry, David
Sent: Wednesday, September 10, 2008 7:23 AM
To: [email protected]
Subject: RE: Help!! Sprinkler in Planetarium

"Start with checking with the AHJ & see what k-factor they require"

Why in the hell would an AHJ be giving a k-factor????? Does this even make
sense?
I would tell you to provide coverage per the code, and if it is not in black
and white in the code, then have an engineer tell me what/how you are going
to protect it.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Sent: Wednesday, September 10, 2008 7:20 AM
To: [email protected]
Subject: Re: Help!! Sprinkler in Planetrium

George, I did an omni max dome a few years back so I know what you are up
against. Start with checking with the AHJ & see what k-factor they require
for a 60' high ceiling, thats the first problem. One way or another you have
to cover all the floor area, if that can be done with heads only above the
screen then you're in business.

Ron Dusky
----- Original Message -----
From: "George Lau" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, September 09, 2008 7:24 PM
Subject: Help!! Sprinkler in Planetrium


> Dear Sprinkler Experts,
>
> I am new to the forum. Besides a "Hi" to yall, I am desperately 
> seeking suggestion or reference regarding the "Sprinkler installation 
> in a PLANETARIUM" which possesses a (60ft dia) semi-spherical dome 
> screen (made of white paint coated matellic plate with small holes). 
> Our current plan is to keep all those sprinker heads above the dome 
> screen. Is it a workable design?
>
> Since we are lack of local technical reference, can anyone throw me 
> some light regarding the normal practice, if the sprinkler heads 
> should be above the dome screen. If yes, what other concerns/attention 
> should be paid?
>
> Thank you so much,
> George Lau
> Macau S.A.R.
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [EMAIL PROTECTED]
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> __________ Information from ESET Smart Security, version of virus 
> signature database 3431 (20080910) __________
>
> The message was checked by ESET Smart Security.
>
> http://www.eset.com
>
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to