Here's another consideration: automatic ball drip. If outside you'll need a pit 
for checking it. Plus the check valve will need to have access. 
The easiest solution is to just have a meter pit with a backflow inside the 
pit.  
Forest 
Cherokee Fire 
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Timothy W Goins" <[EMAIL PROTECTED]>

Date: Thu, 13 Nov 2008 23:04:37 
To: <[email protected]>
Subject: RE: Fire line FDC and Inside controls


This arrangement would defeat the very purpose of a backflow device.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, November 13, 2008 4:23 PM
To: [email protected]
Subject: RE: Fire line FDC and Inside controls


I think 13 allows the FDC to be connected to the fire line, regardless of
what devices are located inside the building.  Section 8.17.2.4.4 infers it
is acceptable, but you'll still need to install a check valve and the
control valve upstream of the FDC connection point (to satisfy 8.17.2.4.1
and 8.16.1.1.4).

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum- 
> [EMAIL PROTECTED] On Behalf Of Jamie Seidl
> Sent: Thursday, November 13, 2008 1:49 PM
> To: [email protected]
> Subject: Fire line FDC and Inside controls
> 
> Forum,
> I have a situation where the fire department is requiring a post 
> indicator valve and free standing FDC outside the building.  We will 
> also need a backflow preventer installed inside in the sprinkler 
> control room.  Is it permissible to install the FDC so it ties into 
> the fire line prior to the backflow control valves, or would we need 
> to install a separate FDC line into the building? I know 8.16.1.1.1.3 
> does not allow a shutoff valve in the line, but it seems contradictory 
> with Figure A.8.16.1.1 2007 NFPA 13. Thanks,
> Jamie Seidl
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> 
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to