Thank you all for your responses!

Forest:
It is not about the annual trip test. It is the acceptance test for a 
new system.
The exhauster is a good idea. However, the Victaulic dry pipe valves 
use a lower air pressure (1.3 bar = 19 psi) than other brands.
Victaulic themselves don't have an exhauster in their product range. 
And I don't know if exhausters of other brands are suited to operate 
with such a low air pressure.

Ron:
The elapsed time is 3 minutes from opening the IT to water delivery.
Almost 80 seconds to trip and 100 seconds from trip to waterdelivery.
Water pressure: static 9.3 bar (135 psi),
         dynamic during filling pipe system 7 bar (100 psi) roughly 
2700 dm3/min (713 GPM),
         dynamic during water delivery by the IT 8 bar (116 psi).
Air pressure before opening the IT: 1.3 bar (19 psi).
The high volume is caused by the size of the protected area and the 
distance between the area and the heated valve room.

Ed:
Good idea, we will check the accelerator and if it appears to be 
connected correctly I will propose tripping with the accelerator on and off.
Draining the system after each test is a complication: it takes 2 man 
half a day each time!

Allen:
I don't think it is an obstruction in this case: the flow test 
downstream the pump performs OK.

Mike:
A too high air pressure, due to a defective pressure gauge could be 
the cause of a delayed trip time. I will propose to check the actual 
pressure and the pressure gauge. The air supply is coming from a tank 
mounted compressor by way of an air maintenance device.

Craig:
The water supply is existing. The static and dynamic pressures 
readings are the same as before.
The dry pipe system is a new system, added to an existing sprinkler 
system with several wet and dry pipe systems.

Gregg:
There is no past; this is acceptance testing of a new system.
For trip time, water pressure and air pressure see the answers to Ron above.

Again, thank you all for your suggestions.
Meanwhile Victaulic has replaced the accelerator and the trip time 
has been reduced to 50 seconds.
The total time between IT open and water delivery is 2.5 minutes now. 
Still too slow.
Could any undrained water in the distribution piping slow down the 
filling time?

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112  

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to