Frans, I was going to suggest that the air maintenance device might be faulty but David beat me. Not only is he smarter than I am but he's quicker. I had a similar problem on a giant system with four exhausters once. (This was a SeaLand warehouse and I seem to remember there was a horizon between one end and the other :-}). Apart from the exhausters being a maintenance nightmare they were operating as Ed described even when working. Similar pressures were also at play. The system was large but with a lot of small pipes with screwed ends layed out in a similar fashion to a pipe schedule with diminishing sizes towards the end. The problem was a stone in the branch line several joints back from the IT where a transition in size had occurred. Bon Chance.
On Sat, May 2, 2009 at 10:25 PM, David de Vries <[email protected]> wrote: > Yes, that 50 second trip time with the new accelerator still appears too > long. Is the air maintenace device working properly? Perhaps left in fill > mode rather than switched to operating mode? Or the orifice is missing from > the operating side of the AMD? > > Dave > > David A. de Vries, P.E., CSP > Firetech Engineering Incorporated > > > --- On Sat, 5/2/09, Ed Vining <[email protected]> wrote: > > > From: Ed Vining <[email protected]> > Subject: Re: Slow responding dry pipe valves > To: [email protected] > Date: Saturday, May 2, 2009, 10:08 PM > > > You point out that the valve now trips in 50 seconds, where before it was > 80. This indicates the accelerator is working, but not fast enough. > Possibly because of the accelerator itself. A restriction in the IT > discharge line could cause it too. If the pipe to the ITV is very long, > trip time could be reduced by upping the size. Even if the accelerator > tripped much faster, it seems the delivery time would be too long > > An exhauster would certainly help, particularly if it is way out on the > system. One has to be careful, though, when both an exhauster and > accelerator are used. The exhauster must trip first. > > A manufacturer could tell you if the 19 psi is outside the working range of > his exhauster. Spec sheets usually list only the maximum rated pressure. > The speed of operation of an exhauster can be adjusted, but it must be done > carefully. If it is too sensitive, the system could trip on normal > variations in pressure. > > Ed > > -- > Ed Vining > 4819 John Muir Rd > Martinez CA 94553 > 925-228-8792 > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)